Overheating problem
« on: October 08, 2016, 08:37:13 AM »

Well, I fired up my CB 5036 this week and have an overheating problem.  The temp goes up to 185, but when I go back out an check it, it's up as high as 194.  I noticed this at the end of the season this past May, but it was windy here at the time and just thought it might be over drafting.  I've check the door and damper and both seem to be sealing good.  Any ideas?
Logged
"a man is no fool to give up what he can not keep to gain what he can not lose"

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: Overheating problem
« Reply #1 on: October 08, 2016, 12:47:55 PM »

Check again it's got to be getting air from somewhere I was told to put a piece of paper and close the door and try to slide it out  and check the damper the same way  just a thought!
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Overheating problem
« Reply #2 on: October 09, 2016, 04:38:04 AM »

Probably a bit of gasket leak but more likely that you have a good fire and when it hits temp with no more demand, the coal bed inside overshoots the temp, see if it continues now that you are up to temp.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

Pointblank

  • Full Member
  • ***
  • Offline Offline
  • Posts: 177
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550
    • View Profile
Re: Overheating problem
« Reply #3 on: October 09, 2016, 06:42:52 AM »

If youve checked over the door seal and damper, Id look at the solenoid. Spray it down good with some wd40 and work it back and forth by hand. Sometimes they get a little sticky. Otherwise, Id look back over the door and damper. If your door gasket is more than a few years old, it might need a new one, they get hard and brittle over time. You also could try adjusting the cam lock on the door so it shuts tighter.  Clean and scrape any creosote from where the damper shuts against the door, also check the damper for pitting or deterioration.
Logged
Central Boiler Classic Edge 550
Previous- Central Boiler 5648- 13 years

Minnesota

adamant

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 67
    • View Profile
    • my pic site
Re: Overheating problem
« Reply #4 on: December 07, 2016, 06:59:41 PM »

What did u find out?
Logged
gas forced hot air/gas hot water
buck supreme insert 2/14/1991 to 2/21 2007 (rip)
LOPI freedom bay insert. (present)
central boiler classic 6048

NEW JERSEY


what we do on the weekends
http://community.webshots.com/user/adamant117


http://adamant.pictiger.com/

MTJAG

  • Full Member
  • ***
  • Offline Offline
  • Posts: 186
  • OWF Brand: Central Boiler
  • OWF Model: CL5036
  • CB 5036, Husky 450, Montana 2740 4WD,100% off grid
    • View Profile
Re: Overheating problem
« Reply #5 on: December 31, 2016, 07:18:03 PM »

I checked everything and everything is good.  It seems this is only happening when we have strong winds.  If the wind is not blowing, everything works as it should.   When the wind is blowing, I see temps overshoot the 185 set point up to 190.  Again, this only occurs when the wind is over 25mph.  In the mountains, 25 is low wind.
Logged
"a man is no fool to give up what he can not keep to gain what he can not lose"

Roger2561

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1780
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550 HD
    • View Profile
Re: Overheating problem
« Reply #6 on: January 01, 2017, 03:33:35 AM »

I checked everything and everything is good.  It seems this is only happening when we have strong winds.  If the wind is not blowing, everything works as it should.   When the wind is blowing, I see temps overshoot the 185 set point up to 190.  Again, this only occurs when the wind is over 25mph.  In the mountains, 25 is low wind.

For the past 4 years my E-Classic 1400 has gone over the high set point by 5 degrees.  No matter what I tried, it always goes over the high set point by 5 degrees.  As long as it doesn't go any higher than that, I'm not too worries about it.  I it find fascinating that your unit only exceeds the high set point with high winds.  Roger   
Logged
CB Classic Edge 550 HD
JD Tractor 4500 4X4 with front-end loader
JD LX277AWS
Stihl 021
Stihl MS 311
Cud Cadet 27 Ton Wood splitter
2012 Honda Goldwing GL1800
New Hampshire

duramax

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 87
  • OWF Brand: central boiler
  • OWF Model: 1450
    • View Profile
Re: Overheating problem
« Reply #7 on: January 25, 2017, 02:45:09 PM »

Mine was going over. I just scraped the door seal better and that did it for now.
Logged
Central Boiler E 1450 Homemade 13 hp wood splitter, Kubota L 3800 tractor

clydem

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 57
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Re: Overheating problem
« Reply #8 on: March 27, 2017, 08:39:36 PM »

My neighbor had a similar over temp problem in high winds, he did not have a chimney cap on a 3 section chimney.  He added a chimney cap and has not had the problem since.  he also replaced the door gasket before the heating season.
Logged
CB5036    inst: 11/20/11
Stihl MS280C  WOODPECKER 24T Log Splitter
JD 4600,  G27 IWB
Michigan's Thumb north of Port Huron

'When someone shares something of value with you and you benefit from it, you have a moral obligation to share it with others.'

Member: MGO, USCCA, MCRGO, GOA, GSSF, NRA,

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: Overheating problem
« Reply #9 on: March 29, 2017, 05:09:51 AM »

I would guess:
that overheating caused by high winds would only occur in a few very specific situations where the terrain creates an updraft during high winds. Maybe 1 out of 10 furnaces. Maybe that's why it is difficult to diagnose. You could probably see the turbulence better during a snowstorm.
For example I have leaves just spinning in a vertical circle on the downwind side if my house when it really blows . The house causes a tumble like a ledge in a river.
If you ever have been in a hydraulic in a river you won't forget it. Surprisingly powerful.

Overheating caused by leaky gaskets or air dampers is much more common.
« Last Edit: March 29, 2017, 05:58:09 AM by E Yoder »
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com