Author Topic: FIGUREING PUMP HEAD  (Read 5303 times)

GUSWHIT

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 91
    • View Profile
FIGUREING PUMP HEAD
« on: May 04, 2017, 11:07:28 AM »

I am too dumb to understand these head charts apparently and I have asked 2 of my plumber friends to help get my main flow pumps set up and they both come up with answers different than I can decipher from the literature I have been reading.  HELP, please from someone knowledgeable!
Here is what I have:  OWB, 20' from house then a run to the basement for 52', so the 1 1/4" Logstar comes in approximately 4' below the level of the stove.  I am placing my infloor heat manifolds on this wall for the tie ins.  The main line will then run another 31' to the plentumn on the forced air unit before returning another 31' to the water heater heat exchanger then the 72' back to the stove(103' all together each way).  I will have 2 separate infloor heat manifolds which one will have 9 runs of 275' of 1/2" pex in the basement floor and the other has 6 runs od the 1/2" pex for the garage floor.  Planning on using grundfos-alpha 15-55's for the manifolds, but trying to figure out the best, most efficient for the main line is really confusing me.  Any help would be appreciated.
Logged

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: FIGUREING PUMP HEAD
« Reply #1 on: May 04, 2017, 11:59:52 AM »

What heat exchanger are you using for your domestic water, what size coil in the duct and cfm of the air handler, and what temp are you putting into the infloor loops might be helpful to know.
« Last Edit: May 04, 2017, 12:02:57 PM by E Yoder »
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

GUSWHIT

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 91
    • View Profile
Re: FIGUREING PUMP HEAD
« Reply #2 on: May 04, 2017, 12:52:21 PM »

30  plate with 1 1/4" inlet/outlets, 139,000 btu exchanger with 1" ports, 2100cfm max on the furnace.  Going to hit 110 on the floor water.
Logged

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: FIGUREING PUMP HEAD
« Reply #3 on: May 04, 2017, 05:33:32 PM »

What kind of forced air furnace is it? And what air temps does it currently put out, and what percent of the time does it run on the coldest day of the year?
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: FIGUREING PUMP HEAD
« Reply #4 on: May 04, 2017, 08:39:58 PM »

Some rambles here. .
Another Alpha might squeak by, but run a really big delta t when everything kicks in. Would have to be plumbed dhw>air handler>infloor to work. That's a pretty big load when that air handler kicks in. Would knock out the dhw.  Counter flowing through the coil can gain some air temp.
Something like a 26-99 Grundfos 3 speed would be a much safer and flexible option I would think... ? Dial your speed according to the delta t you can tolerate.
But I'd like to hear other opinions. Are there any bigger ecm pumps out there that are halfway affordable?
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

GUSWHIT

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 91
    • View Profile
Re: FIGUREING PUMP HEAD
« Reply #5 on: May 05, 2017, 10:10:21 AM »

What kind of forced air furnace is it? And what air temps does it currently put out, and what percent of the time does it run on the coldest day of the year?

Its a York- 96% efficient.  Don't know the air temps and since the last winter was not that normal/cold here it's hard to say.  Not really worth it to burn wood as I haven't even burned 900 gallons of L.P. in 16 months-January through april of 2016 house was being heated to 65 while finishing construction.  This includes the furnace, DHW and the oven/stove.  If I wasn't already in the firewood business, didn't have the stove and didn't want the floors in the basement and garage heated, I wouldn't be doing it.  The house is extremely well insulated.  Realistically, I'm sure I could have put in a small gas boiler and would be ahead if I wasn't able to use culls from firewooding. Just want to get the flow right the first time.
Logged

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: FIGUREING PUMP HEAD
« Reply #6 on: May 06, 2017, 05:47:51 PM »

The hard part about this is we don't know yet if the air handler is oversized or not with the air temps that you will get off of the coil. If the outdoor furnace that you're getting can tolerate low return water temps then low-flow with a smaller circulator won't be nearly as much of an issue. I would guess the 26 - 99 would have plenty of flow on high speed even if everything ran non-stop which it probably won't. There's where having a three speed is nice so you can adjust it back to save electricity.
But again I want to emphasize that if the domestic water is after any of the heat loads the required flow rate will have to be a lot higher because the water will not be hot enough to make a flat plate operate properly.
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: FIGUREING PUMP HEAD
« Reply #7 on: May 06, 2017, 07:01:05 PM »

The difference between the heat load the house will pull and what the emitters (coil, pipe in the slab) are capable of putting out might be quite a bit different. Sizing by the second may or may not be overkill, I have no way of knowing. So I'm guessing with the info we have to work with so far.
On my house I'd do another alpha, but I don't mind turning down the radiant til I could swap pumps if the radiant ran a little low on a bitter night.
I would not tee off for the radiant first in line on the main loop or when you kick it in the first day or two your forced air heat could suffer.
But putting a bigger pump would be the "safe" route if you don't want to worry about it, I just don't like burning extra electricity.
Ask three guys and you'll get three answers on flow rate needed based on what order the loads are pulled off the loop. I ways aim for the most efficient use of water temps and use a large delta t if possible. But a Heatmaster furnace return water is dispersed in the tank well enough and with recirc pump flow really low return water temps aren't an issue. On some the return water hits the firebox and can create a wet spot and rust it out. So my advise is for the brand I've worked with.
Is that too long-winded? :)
« Last Edit: May 06, 2017, 08:13:28 PM by E Yoder »
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

GUSWHIT

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 91
    • View Profile
Re: FIGUREING PUMP HEAD
« Reply #8 on: May 08, 2017, 08:50:31 AM »

Not too long winded at all.  I appreciate the input.  You are very correct about asking 3 people and getting 3 different answers on this one.  I have my results from the furnace inspection guy when he was out setting it for the final time, but its all greek to me.  If that would help, I could post that info for reference.  I have the rest of the summer to decide.  I am finishing hooking up the manifolds and soldering all of the piping in the basement, so I could just leave the pumps out for now.   
Logged

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: FIGUREING PUMP HEAD
« Reply #9 on: May 09, 2017, 08:02:39 AM »

Any info about the gas furnace would help, also what order you are piping the flow on the main loop (this can change flow needed dramatically), what model of outdoor furnace you are installing.
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

GUSWHIT

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 91
    • View Profile
Re: FIGUREING PUMP HEAD
« Reply #10 on: May 09, 2017, 01:02:40 PM »

It's a York furnace, 96% effiencey rating, 100,000 btuh.  Putting a Portage and Main BL3444 OWB in.  Flow to appliances has not been established.  Main line is into house-72' from stove, from here I need to hook up to furnace plentumn, DHW and to the infloor heat manifolds.  I can go any direction I want to first.  Was planning to go through 30 plate exchanger for DHW first, then 31' to the furnace and then pull out secondary piping, close spaced tee's for the infloor heat.  What other info would you like for the furnace?
Logged

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: FIGUREING PUMP HEAD
« Reply #11 on: May 09, 2017, 01:26:04 PM »

  Setup looks good to me, I'd be surprised you would need a 26-99, but a 3spd would let you slow it down if needed. That 1 1/4 main line is going to cut down on the friction and therefore need less head. Think you could use something a little cheaper.  I'll let E Yoder coach you through it as it looks your getting it right.
Logged
Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: FIGUREING PUMP HEAD
« Reply #12 on: May 10, 2017, 09:41:36 AM »

The BTU rating helps. So I'm assuming the coil in the duct is slightly oversized but that's great for airflow.  Probably could run a 30 degree delta t and still put out 100,000 btu's to match (assumption being it was sized correctly). That would need 6.66 gpm. Since domestic water load is first in line and very intermittent that really doesn't affect gpm needed.
Looking at the Alpha pump curve I think it would work especially if you really try to minimize 90's. I'm assuming 1 1/4" all the way through except the coil.
That would give you 166,500 btu's (if we started at 170, 30 Dt across the coil, = 140) to dump into the floor at a 20 Dt on the 110 ℉ floor loop. 50℉  Dt on the main loop before and after the floor heat tees.  Will that heat your basement and other building? I don't know. I don't know what heat loss they have.
I would check with P&M as to what they think about potential for occasional 90℉ return water temps. I do it on what I install but I'm not familiar with how the BL return water is dumped into the tank. You wouldn't want to cause continuous sweating on mild steel.
So I'm still thinking another alpha but I'd like to hear some other opinions. Actually I'be used quite a few B&G NRF-25's as it has a slightly higher gpm but still fairly low cost. Would gain you several gpm but use more electric as it isn't ecm.
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

GUSWHIT

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 91
    • View Profile
Re: FIGUREING PUMP HEAD
« Reply #13 on: May 10, 2017, 10:06:03 AM »

The BTU rating helps. So I'm assuming the coil in the duct is slightly oversized but that's great for airflow.  Probably could run a 30 degree delta t and still put out 100,000 btu's to match (assumption being it was sized correctly). That would need 6.66 gpm. Since domestic water load is first in line and very intermittent that really doesn't affect gpm needed.
Looking at the Alpha pump curve I think it would work especially if you really try to minimize 90's. I'm assuming 1 1/4" all the way through except the coil.
That would give you 166,500 btu's (if we started at 170, 30 Dt across the coil, = 140) to dump into the floor at a 20 Dt on the 110 ℉ floor loop. 50℉  Dt on the main loop before and after the floor heat tees.  Will that heat your basement and other building? I don't know. I don't know what heat loss they have.
I would check with P&M as to what they think about potential for occasional 90℉ return water temps. I do it on what I install but I'm not familiar with how the BL return water is dumped into the tank. You wouldn't want to cause continuous sweating on mild steel.
So I'm still thinking another alpha but I'd like to hear some other opinions. Actually I'be used quite a few B&G NRF-25's as it has a slightly higher gpm but still fairly low cost. Would gain you several gpm but use more electric as it isn't ecm.
I would like to think the furnace/air are sized correctly since I sent the house plans into the supplier and they designed the layout and made me move my location for the unit.
I have 1 1/4" run the entire way from the OWB to the furnace.  The ports on the DHW plate exchanger are 1 1/4" as well.  The way I have run the lines, I only have 3-90 degree elbows before reaching the furnace(total of 6 counting the return run).  I have the capability to run the floor manifolds off a separate pump from the furnace if you think that would help.  I actually put 2 main runs in from the furnace to the basement where the manifolds are so I could do it this way if it would end up being more economical.  It may well be better to do this and run the ECM pumps to save the electrical costs.  What do you think?   
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: FIGUREING PUMP HEAD
« Reply #14 on: May 10, 2017, 04:59:57 PM »

What is the actual ID of the Logstor? (they use metric pex so if it was sold as 1-1/4 it is hard to say what you actually have)
What size is the plate heat exchanger and how many plates?