Author Topic: 2017 G200 stack questions  (Read 4547 times)

tinfoilhat2020

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 634
  • OWF Brand: POS
    • View Profile
2017 G200 stack questions
« on: August 25, 2017, 05:42:41 AM »

Can a 3ft section of 6inch double wall SS pipe twist right on tp the new G200??? I'm getting a new unit installed here next month and I just want to be prepared from the pictures it looks like they change something over the course of the last year or two when the chimney extensions on the units themselves.

Thanks
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 2017 G200 stack questions
« Reply #1 on: August 25, 2017, 06:39:58 AM »

The new ones are supposed to be universal so you can use either standard single wall pipe or double walled.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: 2017 G200 stack questions
« Reply #2 on: August 25, 2017, 07:28:29 AM »

You need to buy an adapter for the double wall. You can use any brand now instead of having to use the selkirk ultra temp like before.
Logged

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: 2017 G200 stack questions
« Reply #3 on: August 25, 2017, 07:22:15 PM »

Yes, a single to double wall adapter.
It comes with a pretty heavy gauge 18" long single wall 6" pipe to extend it.
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

aarmga

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 423
  • OWF Brand: Nature's Comfort
  • OWF Model: NCB-250
  • Central Wisconsin
    • View Profile
Re: 2017 G200 stack questions
« Reply #4 on: August 26, 2017, 03:41:04 PM »

Can I ask why they use double wall when the stack temps are so low?  Is this something for the UL tag?
Logged
Stihl 211 - 16"
Remington Rodeo Pro - 20"
Stihl 661r magnum - 36"
SpeeCo 22 Ton Honda splitter
JD 1025r with FEL
Natures Comfort NCB 250 custom added overhead air injection

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 2017 G200 stack questions
« Reply #5 on: August 26, 2017, 03:43:56 PM »

Can I ask why they use double wall when the stack temps are so low?  Is this something for the UL tag?

Wit the already low stack temps too much single wall would cause the temp to drop even more leading to condensation.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

aarmga

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 423
  • OWF Brand: Nature's Comfort
  • OWF Model: NCB-250
  • Central Wisconsin
    • View Profile
Re: 2017 G200 stack questions
« Reply #6 on: August 26, 2017, 03:48:03 PM »

Makes sense. Thanks!
Logged
Stihl 211 - 16"
Remington Rodeo Pro - 20"
Stihl 661r magnum - 36"
SpeeCo 22 Ton Honda splitter
JD 1025r with FEL
Natures Comfort NCB 250 custom added overhead air injection

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: 2017 G200 stack questions
« Reply #7 on: August 26, 2017, 04:43:02 PM »

Oh so condensation is bad even in a stainless boiler?
Logged
Wood boiler sales, service and installation for the Northeastern USA.

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 2017 G200 stack questions
« Reply #8 on: August 26, 2017, 05:48:55 PM »

Oh so condensation is bad even in a stainless boiler?





If it mixes with ash it could hypothetically form a weak acid, although I’ve seen stainless exposed to some wickedly corrosive stuff on the farm and still not hurt it.

I could see with enough single wall pipe a stack could actually freeze shut.

I could also see if somebody didn’t follow directions and used a bunch of single wall black stove pipe from a hardware store or something the stack would rot out in very short order.
« Last Edit: August 26, 2017, 05:51:52 PM by mlappin »
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: 2017 G200 stack questions
« Reply #9 on: August 26, 2017, 07:11:59 PM »

There was a thread on I think hearth.com where a guy with an indoor gasser froze his chimney shut with condensation. I'm talking like 30' chimney tho.  :)
I be more concerned about plugging the airflow than corrosion. The whole fan assembly and chimney is stainless.
« Last Edit: August 26, 2017, 07:15:25 PM by E Yoder »
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 2017 G200 stack questions
« Reply #10 on: August 26, 2017, 07:25:41 PM »

Actually got to thinking about this a bit.

I looked at the keeper I built to hold a stop pin in on the breakaway wing springs on our sprayer, used leftover 409 pipe from my waste oil boiler, the piece of 1/4” mild steel flat is rusty as can be, the 409 is still shiny.

Looked at the electric transfer pump I put together a few years ago to handle 28% and 32% UAN,  the stainless age iron frame is shiny, the mild steel bolts holding the 10hp electric motor and pump to it will either need cut or broke off, they ain’t turning.

Looked at our fertilizer spreader, this things gotta be 40 years old at least, it was used when Dad bought it and I was still too young to spread fertilizer so maybe 50+ years, the stainless box is fine, the original rear assembly rotted away years ago, we replaced that with stainless, still shiny, it’s spread thousands of tons of fertilizer over the years, replaced all the roller chains with stainless as mild steel ones would last at best two years before rusting solid. Have replaced all the leaf springs a couple of times, fertilizer even eats spring steel, have replaced the axles once as well. Have replaced all the bearings with stainless ones as well as regular steel bearings would last at best two years.

This is hypothetical at best, but if a person had enough single wall pipe on it like say if they had to meet one of those arcane minimum height requirements, you could get a lot of condensation, that could mix with the flyash and literally make mud inside the pipe or even gum up the exhaust fan.

But when it comes down to it, doesn’t natter if your buying a car or a boiler, by buying it your basically agreeing to follow the manufacturers policy on best practices to maintain your warranty. If they say an oil change every 5000 miles at a certified dealer, then thats where you get your oil changed, if they say X kind of pipe and the wood should be under a certain percentage, then so be it. Ditto on keeping it dry and avoiding having ash and moisture mix.
« Last Edit: August 26, 2017, 09:04:19 PM by mlappin »
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: 2017 G200 stack questions
« Reply #11 on: August 27, 2017, 04:26:12 AM »

 Agree, it's more about making a mess inside the boiler than any corrosion issue in a 409 boiler.

  Had a call yesterday from a person looking into buying a furnace. Said the CB dealer told him next load of CB's will have stainless fireboxes. Was told he needs to buy one he has in stock now with mild steel because the new ones will spider crack when you throw wood in them. I bet that line will change if he gets his current stock sold.
 
  If your selling stainless it's hard to be honest about mild steel and vise versa. Tendency is to look for anything to promote your product right or wrong.
Logged
Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: 2017 G200 stack questions
« Reply #12 on: August 27, 2017, 04:59:16 AM »

Cracking, hmmm, remember that photo I posted of the Magic Liberty bus on Prince Edward Island a couple of years back, I know I still have it somewhere, well anyway why do you think I was there, yup you guessed it, his 3 month old boiler had cracked on the right side rail and was leaking, that and several more doing the same are part of the reason they had me do all those upgrades. Now don't get me wrong, at that time they took care of the issue 100%. They admitted that they had made a mistake by putting a solid rail into the fire box and that the fan motors were overheating with the new door on the back, I sure wish that they had kept up the philosophy.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 2017 G200 stack questions
« Reply #13 on: August 27, 2017, 07:23:08 AM »

Yep, my distributor came out with a template, cut the hole in the door then installed the fresh air intake for the fans, easy enough to do and I could have done it myself, but they did have a template and all. Also recall they slit the rails to prevent that cracking.

Some stainless is a lot worse about spider cracking than others. Whatever the material in our fertilizer box is cracks horribly at certain welds if you keep rewelding with stainless rod, I’ve taken to welding those with 7018, stopped the cracking and just enough stainless mixed with the 7018 that the welds didn’t rust either. I’m guessing 316 maybe? I usually watch the sparks from cutting or grinding then grab a rod or roll of wire that I know works with those sparks. Real hi tech out here after all.
« Last Edit: August 27, 2017, 07:27:26 AM by mlappin »
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: 2017 G200 stack questions
« Reply #14 on: August 30, 2017, 06:18:16 PM »

I seem to remember a guy on here a few years back with a stainless boiler that rotted out in only a few months from a salt water filter on his pool and a stainless heat exchanger, I think it as well was 409, Marty, you always comment on your exhaust on your truck being 409, how do you think it would hold up if 3 years in you were to put it in a pressure test?
Logged