leak on pri air intack e 2400
« on: December 22, 2017, 07:23:38 AM »

Hi all   I changed out my primary air intake elbow and while cleaning found a little water in with soft creosote.  Boiler is 6 years old and have watched my water condition very carefully.   Question, can you use boiler seal or is that a no no?  My water level is staying on the mark, however all leaks get bigger not smaller, thoughts.    Thanks to all
Logged
Trailmaster  Plymouth NH

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: leak on pri air intack e 2400
« Reply #1 on: December 22, 2017, 07:44:39 AM »

Probably best to have this moved to the central boiler topic but are you sure thst this is water jacket water and not just condensation? You should see that leak continue to leak a lot of water out and if the water jacket isn’t dropping then I would guess this is condensation.
Logged

the trailmaster

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 70
  • OWF Brand: CENTRAL BOILER
  • OWF Model: 2400
    • View Profile
Re: leak on pri air intack e 2400
« Reply #2 on: December 22, 2017, 08:01:37 AM »

Thanks  First, I'm not sure how to transfer to central boiler. Second, I hope you are correct on the condensation, that wood make my Christmas.   Thanks again for your thoughts I will keep an eye on the water level.
Logged
Trailmaster  Plymouth NH

Roger2561

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1780
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550 HD
    • View Profile
Re: leak on pri air intack e 2400
« Reply #3 on: December 22, 2017, 09:19:23 AM »

Trailmaster - I have the E-Classic 1400 and the design basically the same.  Every time I remove the primary air elbow on my 1400 I always see moisture, but it's condensation not from a water leak.  The first time I experienced it, it scared the bugger out of me thinking it was a leak.  This is my 7th season with my 1400.  Good luck and Merry Christmas!  Roger
Logged
CB Classic Edge 550 HD
JD Tractor 4500 4X4 with front-end loader
JD LX277AWS
Stihl 021
Stihl MS 311
Cud Cadet 27 Ton Wood splitter
2012 Honda Goldwing GL1800
New Hampshire

the trailmaster

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 70
  • OWF Brand: CENTRAL BOILER
  • OWF Model: 2400
    • View Profile
Re: leak on pri air intack e 2400
« Reply #4 on: December 22, 2017, 09:54:16 AM »

Thanks Roger, first time I've really noticed it.  I hope you guys are correct  Best to you all  Merry Christmas 
Logged
Trailmaster  Plymouth NH

Roger2561

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1780
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550 HD
    • View Profile
Re: leak on pri air intack e 2400
« Reply #5 on: December 22, 2017, 01:39:09 PM »

If you're not losing water, I'd be 90% confident that it's not a leak unless it's a super duper tiny one.  Keep an eye on the water level for the next few days/weeks to see if it drops any, that should be a telling sign.  Roger 
Logged
CB Classic Edge 550 HD
JD Tractor 4500 4X4 with front-end loader
JD LX277AWS
Stihl 021
Stihl MS 311
Cud Cadet 27 Ton Wood splitter
2012 Honda Goldwing GL1800
New Hampshire

Pointblank

  • Full Member
  • ***
  • Offline Offline
  • Posts: 177
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550
    • View Profile
Re: leak on pri air intack e 2400
« Reply #6 on: December 22, 2017, 06:54:39 PM »

I think Roger's right on here. If your water level isn't dropping its more than likely just condensation. Mine does the same thing. I clean it out every couple of weeks and there's often a little soft creosote and some moisture. If your using any Ashtrol in your firebox its a good idea to also  toss a scoop of it into the elbow every couple weeks. Creosote + water creates an acid that can erode the steel over time. Ashtrol is a pH modifier that neutralizes the acid. Any Central Boiler dealer should carry it.
Logged
Central Boiler Classic Edge 550
Previous- Central Boiler 5648- 13 years

Minnesota

duramax

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 87
  • OWF Brand: central boiler
  • OWF Model: 1450
    • View Profile
Re: leak on pri air intack e 2400
« Reply #7 on: December 24, 2017, 07:36:48 AM »

I just cleaned out my E1450 last week and the tube had a good layer of creosote and some moisture. Burning soft wood and I needed to clean out my reaction chamber, it was full so it had low burn temps. I think you will be fine.
Logged
Central Boiler E 1450 Homemade 13 hp wood splitter, Kubota L 3800 tractor

Roger2561

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1780
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550 HD
    • View Profile
Re: leak on pri air intack e 2400
« Reply #8 on: December 24, 2017, 10:47:17 AM »

It'll be interesting to see how the primary air elbow is doing regarding creosote buildup.  I haven't cleaned it in a little over a month, same goes for the primary air holes in the firebox.  But with sub-zero overnight temps expected starting Tuesday night, I need to be sure everything is good clean and operating properly.  So far the 1400 has been operating flawlessly.  This is my 7th season heating my house with it and DHW.  I clean the reaction chamber weekly.  Generally there will be about 4 to 5 scoops of ash in it.  Roger
Logged
CB Classic Edge 550 HD
JD Tractor 4500 4X4 with front-end loader
JD LX277AWS
Stihl 021
Stihl MS 311
Cud Cadet 27 Ton Wood splitter
2012 Honda Goldwing GL1800
New Hampshire

the trailmaster

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 70
  • OWF Brand: CENTRAL BOILER
  • OWF Model: 2400
    • View Profile
Re: leak on pri air intack e 2400
« Reply #9 on: January 01, 2018, 02:35:24 PM »

Happy New Year to all.  I been keeping an eye on the water level and she seems to be holding.  Boiler been running hard last week and going through some wood. Seems the colder it gets the better it runs. 
For the guys with the creosote issues, I run 185 to 195, sometimes it will get to 197, but seems to run cleaner.  Thanks again for all the advice.    Trailmaster
Logged
Trailmaster  Plymouth NH

Roger2561

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1780
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550 HD
    • View Profile
Re: leak on pri air intack e 2400
« Reply #10 on: January 01, 2018, 02:52:33 PM »

Happy New Year to all.  I been keeping an eye on the water level and she seems to be holding.  Boiler been running hard last week and going through some wood. Seems the colder it gets the better it runs. 
For the guys with the creosote issues, I run 185 to 195, sometimes it will get to 197, but seems to run cleaner.  Thanks again for all the advice.    Trailmaster

Trailmaster - Happy New Year!  Glad to learn that it doesn't seem to be an leak in your OWB.  I agree with the statement that when it gets colder, the OWB seems to run cleaner.  Every Saturday morning when I go out to put wood in the 1400 I always clean the reaction chamber of ash buildup.  I think there may have been 4 shovel fulls of very fine ash in it.  Roger 
Logged
CB Classic Edge 550 HD
JD Tractor 4500 4X4 with front-end loader
JD LX277AWS
Stihl 021
Stihl MS 311
Cud Cadet 27 Ton Wood splitter
2012 Honda Goldwing GL1800
New Hampshire

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: leak on pri air intack e 2400
« Reply #11 on: January 01, 2018, 03:02:21 PM »

Good news indeed this cold week. Happy New Year to you too.
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com