Water doesn't appear to be circulating into the house
« on: October 26, 2014, 06:54:24 PM »

I just tried to fire up the mf5000 for the season, but it appears I have a problem.

The wood stove reached temp of 180.  But inside the house the temp readings are only 145 on the one pipe, and 80 on the other.  I checked all the valves multiple times, and everything was open.

First picture shows the circulator that I think is not working properly. The pipe coming into the top is hot, but pipe coming out is cold...the feed to the furnace.  Would I be correct in thinking I should replace it?

Second picture is of the model number.  Should I do a direct replacement with another Taco? Or is there a better choice?

Logged
Climb High Tree Service
Lebanon PA

Certified Arborist

"Kiss My Axe"

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: Water doesn't appear to be circulating into the house
« Reply #1 on: October 26, 2014, 06:59:40 PM »

You probaly have an  air bubble can you bleed it?
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

Tree_Killer

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 38
  • OWF Brand: Heatmaster
  • OWF Model: MF5000SS
    • View Profile
Re: Water doesn't appear to be circulating into the house
« Reply #2 on: October 26, 2014, 07:07:32 PM »

I guess I can disconnect the bottom flange and check there for air.  I will try that tomorrow
Logged
Climb High Tree Service
Lebanon PA

Certified Arborist

"Kiss My Axe"

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Water doesn't appear to be circulating into the house
« Reply #3 on: October 26, 2014, 07:39:29 PM »

take a wrench and whack the housing a couple of times, it more than likely is simply seized up and about 90% of the time that will free up the impeller, the motor and impeller can be removed from the housing by removing the 4 7/16th's bolts and that gives you access to the impeller, simply turn it with your hand until it frees up then re install.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

Tree_Killer

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 38
  • OWF Brand: Heatmaster
  • OWF Model: MF5000SS
    • View Profile
Re: Water doesn't appear to be circulating into the house
« Reply #4 on: October 27, 2014, 05:42:59 PM »

The circulator is toast...propeller was messed up and deteriorated.

So replace with the same Taco pump? Or go with another/better brand?
Logged
Climb High Tree Service
Lebanon PA

Certified Arborist

"Kiss My Axe"

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Water doesn't appear to be circulating into the house
« Reply #5 on: October 27, 2014, 06:39:48 PM »

A Taco 009 will get you a bit more flow
Logged
Wood boiler sales, service and installation for the Northeastern USA.

Tree_Killer

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 38
  • OWF Brand: Heatmaster
  • OWF Model: MF5000SS
    • View Profile
Re: Water doesn't appear to be circulating into the house
« Reply #6 on: October 27, 2014, 06:47:39 PM »

it is a taco 009-f5. Just wasnt sure if it was the best product out there
Logged
Climb High Tree Service
Lebanon PA

Certified Arborist

"Kiss My Axe"

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Water doesn't appear to be circulating into the house
« Reply #7 on: October 27, 2014, 06:54:25 PM »

Not a bad circ but I would rip out that darn Flo check entirely on the wood boiler loop
Logged