Duct blower speed different using heat pump vs. boiler
« on: December 22, 2016, 03:33:31 PM »

What can I do to get my blower speed to blow as hard as it does when the central air is on. I'm only using the green wire on my thermostat. My ducts are in the ceiling and my ceiling is 11 ft causing a lot of heat to stay up high away from floor. If the duct was putting out more air it would blow it down to floor. When the central heat pump is running you can hear the air coming out and feel it. Using boiler thermostat it's much slower.
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #1 on: December 22, 2016, 04:07:18 PM »

Do you have a variable speed blower on a heat pump or is it a gas or oil furnace with air on it? Two t-stats or one? This is a good question and it can be done but I'd like to hear others comments.
Logged
Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #2 on: December 22, 2016, 05:58:16 PM »

Yes it is a variable speed blower. I use 2 thermostats 1 for heat pump and the other for the boiler.
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Duct blower speed different using heat pump vs. boiler
« Reply #3 on: December 22, 2016, 06:04:05 PM »

Okay, when the term variable speed is used are we referring to an infinitely variable speed blower or a three speed?

If its a three speed, get a 1 into 2 spade adapter, and a short jumper, then the high speed wire on the blower can be plugged into both the heat and cool terminal on the control board.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #4 on: December 22, 2016, 06:17:26 PM »

Sounds to me like he has a DC variable.  But sometimes they still have  double bank speed increments at the blower. Do you have a single or dual compressor in your outside unit? If dual the outside unit can send the signal back to the board when the second compressor cuts in and ramps the blower. But you may have only one compressor and the board decides the speed.
Logged
Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #5 on: December 23, 2016, 07:42:36 AM »

Do you guys feel that will be a help to me? You could feel the air being pushed down. Would the extra air flow cool the coils too fast? Would it be a way to keep our house warmer with same amount of firewood use. If there not a benefit I will leave it like it is. When the ac is on the air speed changes up and down when it's calling for cool air. It blows much harder when heat pump kicks on calling for heat than it does if the boiler kicks on the fans.
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #6 on: December 23, 2016, 08:13:21 AM »

Anytime you draw more heat you use more wood. Can you keep your house warm with the fan on low speed? If you can, just leave it. But if you need more heat there is a way to speed up your fan. But then you get more heat transfer and you use more wood. The objective is to get your house warm. Right now you are using manual fan on port speed to move air, so whatever your air handler is set for on manual fan on that's what air flow you are getting.Variable speed units generally have dip switches to control air flow and that can be changed however manual fan on port can generally be only turned op to 60% max. So you need to power the board to thinking something else is on when the wood boiler is on when really it isn't. How to do that depends how your system is set up.
Logged
Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #7 on: December 23, 2016, 08:52:13 AM »

My boiler keeps my house warm. However with 11 ft ceilings in every room it's 6-7 degrees warmer up next to ceiling than at eye level where the thermostat is. I'd like to figure out how to push that air on down without a bunch of ceiling fans. My boiler is capable of heating 8000 sq ft, my house is 5400 sq ft, so the boiler is not struggling at all. All my duct work is in attic. My house sits on a solid concrete slab about 4 ft thick so no crawl space for ducts under floor. I don't mind the overhead registers, just wish it would blow a little harder than what it us. There's a big difference in when the heat pump kicks on and when the boiler heat kicks on in the speed of the moving air. You may be right in that I just need to leave well enough along. Thanks for your help. I was hoping some one might of had exact same situation and what thier solution is.
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #8 on: December 23, 2016, 09:04:47 AM »

Ceiling fan? But if you want to speed it up we will try to walk you through it , or shoot me a pm with a phone # and I'll explain how to do it. But we will need info from in your air handler, how it is set up.
Logged
Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #9 on: December 23, 2016, 09:13:50 AM »

The change you have for me would be at the thermostat or in my air handler? I'm just afraid that even with your expertise I might mess something up. My son in laws father is an hvac man and he would be better to let you walk him thru it. Will these changes affect the heat pump with air conditioning and backup as far as how it works? If you think it's simple enough I'm willing to try
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #10 on: December 23, 2016, 09:29:02 AM »

Hey shepherd boy, this may sound a little dumb but what is pm? You said shoot you a pm.😆
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #11 on: December 23, 2016, 09:40:31 AM »

I figured out as answer  to last questionabout PM. You should have gotten one by now from me? The older I get the funnier I get on things like this. That's what my wife kids and grand kids tell me.
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #12 on: December 25, 2016, 02:06:30 PM »

Just an update here. Bluegrass has a Trane variable speed air handler. Infinitely variable that is. He is running a standard Trane stat (nothing fancy) and has a Honeywell 5000 as a second t-stat for the boiler. He has it turning on the blower using the g terminal. This uses the manual fan on route to turn on the blower. Manual fan on will only give a max of about 60% air flow. How can he get 100% and still leave his existing stat intact to back up the boiler? He is to send me a pic of the circuit board how it is wired now but if someone is familiar with this unit you may want to give your advise.

Bluegrass if you read this your father in law is a heating and air man I would hire him. He owes you a favor anyway for giving his son a good wife. The change will be in the airhandler.
Logged
Let the youngin's have it
 Gettin' old and lazy
 Lookin' for the next good fishing hole

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Duct blower speed different using heat pump vs. boiler
« Reply #13 on: December 25, 2016, 05:31:57 PM »

Just an update here. Bluegrass has a Trane variable speed air handler. Infinitely variable that is. He is running a standard Trane stat (nothing fancy) and has a Honeywell 5000 as a second t-stat for the boiler. He has it turning on the blower using the g terminal. This uses the manual fan on route to turn on the blower. Manual fan on will only give a max of about 60% air flow. How can he get 100% and still leave his existing stat intact to back up the boiler? He is to send me a pic of the circuit board how it is wired now but if someone is familiar with this unit you may want to give your advise.

Bluegrass if you read this your father in law is a heating and air man I would hire him. He owes you a favor anyway for giving his son a good wife. The change will be in the airhandler.

First thing that comes to mind, cheap and simple, use the second thermostat to activate the Y wire, use a aqua stat to open the signal to the compressor or just turn the breaker off to it, on call for heat Y wire is activated which I would think should run the fan on high speed, with the aqua stat the compressor won’t start.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

shepherd boy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 365
  • OWF Brand: HeatMaster
  • OWF Model: C375
    • View Profile
Re: Duct blower speed different using heat pump vs. boiler
« Reply #14 on: December 25, 2016, 07:23:22 PM »

I think you are on track. You need to energize the y and it will go to high. Aqua stat on the compressor would give backup when temp drops on boiler. However some of these units are programed so you need both the G and the Y energized at the same time for them  the fan to come on and then go to high. You need to be careful not to link the G to the Y with the same wire or the original stat will turn on the compressor any time it energizes the G even in the manual fan on situation.
Logged