Author Topic: Shorter burn times per load question  (Read 5313 times)

clydem

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 57
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Shorter burn times per load question
« on: January 05, 2018, 10:49:38 PM »

Is anyone in Michigan experiencing short burn times per load?

 For the last 2-1/2 weeks overnight temps average +5 to -22  daytime ave +15* to +20*
This is the first time in 8 winters I have went from 12hr burn times to 8 hours between loads. I have my CB5036 temp set @185* and my monitor system emails me if the water temp hits 168*.   
Is it just the low temps & the higher home heat load causing the 30% drop in burn times?  :bash:   What do you think?


Water level ok
door gasket new in Oct 17
well seasoned ash, oak & maple
damper clean & working fine

Logged
CB5036    inst: 11/20/11
Stihl MS280C  WOODPECKER 24T Log Splitter
JD 4600,  G27 IWB
Michigan's Thumb north of Port Huron

'When someone shares something of value with you and you benefit from it, you have a moral obligation to share it with others.'

Member: MGO, USCCA, MCRGO, GOA, GSSF, NRA,

schoppy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 377
  • OWF Brand: Heatmaster
  • OWF Model: G200
    • View Profile
Re: Shorter burn times per load question
« Reply #1 on: January 06, 2018, 12:28:20 AM »

These last 2 weeks are the hardest my G200 has run since I installed it. I am very pleased with its performance and I can still get 12 hour burn times at night, 14 if I push it but that is filling it almost full. About half loads during the day.

My temps cycle from 180 to 160 (factory preset) and been working good for me.
Logged
Husqvarna 562XP
Echo CS-361P
Echo CS-310
31 ton splitter

heat550

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 401
  • OWF Brand: Heatmor
  • OWF Model: 1994 200ss 2015 400dcss
    • View Profile
Re: Shorter burn times per load question
« Reply #2 on: January 06, 2018, 03:29:02 AM »

I have a guess ready stoves needs a good clean out .or test your trench lines at boiler and in house should be same temp  maybe loosing 1-2 degrees depending on line length . Sounds basic but that's first things to think about .
at below 0f it can be alot of factors . wind , wood moisture  house pulling more heat.

Heat550

I don't see a draft fan on your model . So clean stove would be more of a issue .



Is anyone in Michigan experiencing short burn times per load?

 For the last 2-1/2 weeks overnight temps average +5 to -22  daytime ave +15* to +20*
This is the first time in 8 winters I have went from 12hr burn times to 8 hours between loads. I have my CB5036 temp set @185* and my monitor system emails me if the water temp hits 168*.   
Is it just the low temps & the higher home heat load causing the 30% drop in burn times?  :bash:   What do you think?


Water level ok
door gasket new in Oct 17
well seasoned ash, oak & maple
damper clean & working fine
Logged

U.P. Doug

  • Full Member
  • ***
  • Offline Offline
  • Posts: 125
  • OWF Brand: Ridgewood
  • OWF Model: 7500
  • Rudyard, Michigan Upper Penninsula
    • View Profile
Re: Shorter burn times per load question
« Reply #3 on: January 06, 2018, 06:49:16 AM »

I live in the upper Penninsula and it has been -5 for a high and -30 at night, with some windy days. I have been coming home from work to hot coals and a boiler at 155 or so, after a 11 hour burn time. I would say a 8 hour burn time is probably what I am getting in this cold snap as well. Worst it has been in the last 4 years for me.
Logged

Walleye

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 35
  • OWF Brand: Central Boiler
  • OWF Model: 6048
    • View Profile
Re: Shorter burn times per load question
« Reply #4 on: January 06, 2018, 07:34:26 AM »

I'm seeing the same thing here in SE Ohio with my 6048. I've monitored and recorded temperatures on mine for the past 5 years and have noticed my delta t has increased some this year for some unknown reason. I'm seeing the return temperatures from two baseboard heaters 20 to 30 degrees hotter this year than in the past. cleaned the dust out of them and it didn't change anything. I'm thinking I need to look in the attic and see if the insulation is gone!   
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Shorter burn times per load question
« Reply #5 on: January 06, 2018, 07:53:55 AM »

Unless all your structures are very well insulated extreme cold with any amount of wind will raise the heat load which will shorten burn times.

I got called out awhile back, installed a used Woodmaster 434 for a young couple, wasn’t running continuously but couldn’t get the house over 62, up until then it did fine, but set records that night, low turned out to be -14 with a windchill of -30, turned the cutout up to 192 and tightened the differential up, had the house up to 69 by morning, I can guarantee that killed his burn times.

« Last Edit: January 06, 2018, 08:06:03 AM by mlappin »
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: Shorter burn times per load question
« Reply #6 on: January 06, 2018, 08:05:02 AM »

If you need to warm your house from 25 degrees to 70 degrees that means you need to raise it 45 degrees. If you need to raise it from -15 to 70 that is 85 degrees. Double the heat, double the wood. It is simple math.
Logged

wreckit87

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 659
  • OWF Brand: Heatmaster
  • OWF Model: C375
    • View Profile
Re: Shorter burn times per load question
« Reply #7 on: January 06, 2018, 08:31:17 AM »

I used to run a Cozeburn MS250 that was similar in design to a 5036, with a draft fan in the door. I don't recall having one of these 3 week below zero spells like we're having now when I had it, but I do know any single day below zero would flatten that poor thing in 6-8 hours. I could fill it full enough that I'd have to hammer another toothpick in it and still only 6-8 hours. It was undersized for me of course, but subzero temps are going to cause an excessive hunger problem with any boiler
Logged

Pointblank

  • Full Member
  • ***
  • Offline Offline
  • Posts: 177
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550
    • View Profile
Re: Shorter burn times per load question
« Reply #8 on: January 06, 2018, 08:35:20 AM »

Ya, its probably just be the cold. Subzero temps always seem to do a number on the wood pile. I did some heat loss calculations on my home and shop a few years back and IIRC, -25 required like 2 1\2 times more BTU's then 20 above to maintain the same indoor temperature. That means 2 1\2 times more wood.

Once temps moderate next week things should get back to normal.
Logged
Central Boiler Classic Edge 550
Previous- Central Boiler 5648- 13 years

Minnesota

Range91

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 34
  • OWF Brand: Portage and Main
  • OWF Model: ultimizer 34-44 shaker
    • View Profile
Re: Shorter burn times per load question
« Reply #9 on: January 06, 2018, 08:37:13 AM »

If you need to warm your house from 25 degrees to 70 degrees that means you need to raise it 45 degrees. If you need to raise it from -15 to 70 that is 85 degrees. Double the heat, double the wood. It is simple math.
I see what your trying to say but I'll have to disagree on the double the wood. My stove actually burns better and same or a smidge less wood when it starts to get around 0 compared to 25-35 unless it is real windy. I relate this to the short on off cycles and being able to burn more efficient. This has been my experience with my portage and Maine and was not the case with my ridgewood 6000 I had.
Logged

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: Shorter burn times per load question
« Reply #10 on: January 06, 2018, 09:53:38 AM »

Some models seem to run better with a heavy load, others not so much.
We've gotten more calls about record wood consumption in the last couple of weeks than I can remember for a long time.
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: Shorter burn times per load question
« Reply #11 on: January 06, 2018, 11:20:03 AM »

yes with these fridge cold temps I'm definitely getting a shorter burn time..I got plenty of wood though!
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

heat550

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 401
  • OWF Brand: Heatmor
  • OWF Model: 1994 200ss 2015 400dcss
    • View Profile
Re: Shorter burn times per load question
« Reply #12 on: January 06, 2018, 04:09:41 PM »

One other thing your daft is drawing twice as much also
Cold heavy air . At below 0f my slabs  startburning just when
They get inside the boiler door it's like below 0f makes it draw dang hard. There's no flames but it's so hot slabs ignite instantly air so hot. I have 300 cfm blowers.

Heat550
Logged

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: Shorter burn times per load question
« Reply #13 on: January 06, 2018, 06:03:58 PM »

all things mentioned above are valid factors, however at the amount your referring too.  Wet wood can effect burn times that much that dramatically.  I would look for a major problem in the system, or use the moisture meter to truly find out wood conditions..    Even good seasoned wood can absorb water depending on storage conditions.

well covered and aged wood, off the ground....
Logged
Michigan Thumber

clydem

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 57
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Re: Shorter burn times per load question
« Reply #14 on: January 06, 2018, 10:09:20 PM »

First of all thanks for all who have replied...   Having worked in a power plant  I understand how having pre-heated combustion air would raise the  efficiency of the boiler,  I just haven't figured how to capture wast heat from the chimney & pipe it to the draft intake.  Any ideas?

One of these days I'll have to quit overthinking this stuff.

thanks again  & Keep Warm
Clyde
Logged
CB5036    inst: 11/20/11
Stihl MS280C  WOODPECKER 24T Log Splitter
JD 4600,  G27 IWB
Michigan's Thumb north of Port Huron