Need advice on t-stat wiring.
« on: November 24, 2014, 10:39:45 PM »

Hi all,

I've had my boiler up and running for a little over a week now.  The system is functioning beautifully with only 1 minor set back.  The first time my secondary thermostat called for heat, it also turned my A/C on.  Any quick ideas on how to rectify?

I have the basic double thermostat set-up for an existing forced air unit using the guide CentralBoiler has on their website.  I've been working 12 hours since the install and haven't had much time to troubleshoot... any advice would be appreciated so I can get it done sooner rather than later.  Currently, I have the breaker disconnected for the A/C unit - that was my quick-fix.
Logged
Husqvarna - Rancher 460, 18"
28 Ton Splitter

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Need advice on t-stat wiring.
« Reply #1 on: November 25, 2014, 03:27:12 AM »

I'd love to help but I use a single TT and add an Aqua stat to kill all but the blower on the backup system, I think RSI has your solution!
Logged
Wood boiler sales, service and installation for the Northeastern USA.

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Need advice on t-stat wiring.
« Reply #2 on: November 25, 2014, 10:18:51 PM »

The quick fix is to remove the wire off the G terminal on the original thermostat and only run it to the W in the second thermostat. This is assuming you have a gas furnace. If you have a heatpump you may need to add a relay.

Another possible thing that might work but I haven't gotten around to trying out yet, use the original thermostat for the OWB and the 2nd for the backup heat. To do this, take the wire off the W terminal and run it to the W in the new thermostat. Then add a jumper from the G to the W on the original thermostat. You will still need the RH and c jumpers between the two thermostats.

Not sure if the 2nd way will work but I think it should.
Logged

Corngrinder

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 33
  • OWF Brand: Central Boiler
  • OWF Model: 5036
    • View Profile
Re: Need advice on t-stat wiring.
« Reply #3 on: November 25, 2014, 10:49:33 PM »

Thanks, RSI.

I have a gas furnace as back-up.  When I remove the 'g' terminal from the original thermostat, will I have to reconnect it during the summer months when I want the A/C to run?  Or, is this a permanent fix?
Logged
Husqvarna - Rancher 460, 18"
28 Ton Splitter

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Need advice on t-stat wiring.
« Reply #4 on: November 25, 2014, 10:50:42 PM »

You probably won't have to connect it again. I always just leave them off.