heat exchanger problem
« on: February 02, 2009, 06:33:54 PM »

Gotta problem.  Here is a quick sketch of my system...


My water comes in from the stove in the middle of the pic on 1" PEX

Goes through the green pump and "will" go through the domestic water heater.  (for now it goes straight from the pump into that "Y" pipe.)

Then it splits and the left side goes into my home furnace water to air heat exchager.  it's about 10 feet of 3/4" PEX.

On the right side, it travels through my house about 95 feet one way of 3/4" PEX to the other furnace which is a small furnace designed to heat a 16'X23' area on the other side of the garage. (one person hair salon).

It goes through the water to air heat exchager in that furnace, then travels back again about 95 feet of 3/4" PEX, and meets up with the other return line from the big furnace.

They both go into a manifold to warm 3 loops of radiant heat. 
1. Basement floor,
2. 24'X24' garage floor,
3. 24'X24' floor under the garage
then it's back out to the OWB through 1" PEX.


Here's the problem.  I just finalized my small furnace water to air heat exchager yesterday and it's not heating.  When I turn the furnace fan off, the heat exchanger gets hot, and the in and out lines both get hot the entire length of the run.  Hot enough that when I touch the brass fittings and valves, anywhere along the 95 foot run on either line, it burns my hand. 
When I turn the furnace fan on, within 2 minutes, it cools down the return line a ton, and the vents blow cool air in just a couple of minutes. 

I've tried shutting the valve to the main furnace and also 2 of the floor loops thinking that maybe the pump didn't have enough pressure but it's the same result.  With the furnace fan on , it cools the heat exchanger so much that the water goes way down in temp and there's no heat from the vents.

I bought both exchangers at the same time from CB and the main furnace works great.

Any ideas...?
« Last Edit: February 02, 2009, 06:39:14 PM by Scratch »
Logged
Hudson, WI

ckbetz

  • Full Member
  • ***
  • Offline Offline
  • Posts: 124
    • View Profile
Re: heat exchanger problem
« Reply #1 on: February 02, 2009, 06:45:55 PM »

What size pump do you have?  Could it be possible that you're at the limits of the pump even without going through your first furnace?  It kinda sounds to me like you just don't have enough volume of hot water running through your second heat exchanger.  That sounds like a very complicated system that would possibly need a zone valve or multiple pumps/zones.  I can't imagine you're running everything with a standard Taco 007, or even an 011. 

If you go check out www.heatinghelp.com you can go to the wall and search for similar systems without the OWB and see what kind of flow they require. 
Logged
Pomeroy, Ohio

Dirtslinger

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Woodmaster
  • OWF Model: 4400
    • View Profile
Re: heat exchanger problem
« Reply #2 on: February 02, 2009, 06:57:46 PM »

Thats alot pulling on one zone
Did you speed up the blower on the new furnace.
Can you shut off everything but the new furnace and see whats the temp does.
« Last Edit: February 02, 2009, 07:09:08 PM by Dirtslinger »
Logged
Dirtslinger
Brockway, PA

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: heat exchanger problem
« Reply #3 on: February 02, 2009, 07:12:56 PM »

i also dont see any mixing valve or zone valves on your system

i will venture a guess as to your problem....you 3/4 line to the home furnace is short...your 1/2 line to the shop is long the "friction head loss" on the small pipe is so great that the flow is likely way less than half of the short 3/4 line
your shop furnace is starved for more GPM

as long as your furnace pump can deliver the GPM needed if you had a larger  pipe you could add a "booster pump" to the 1/2 inch line to increase GPM

if you added this pump and your furnace pump was not able to delive the GPM needed you may in fact starve the home furnace if both were running at the same time

i dont mean to be rude but your plumbing looks like it could be improved as OWB's go

most folks have two headers in the house a feed header and a return header...it takes more pipe but can come in a lot handier when needed to work on the system

you run seperate lines to each "appliance" from the feed header and seperate lines from each 'appliance" back to the return header..each and every line (both feed and return) are valved at the headers  this way you can isolate any one "appliance" at any time to work on it if needed...also you can use the valves as "chokes" to adjust the GPM flow to each "appliance"
Logged
home made OWB (2012)
Ontario Canada

Scratch

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 278
  • OWF Brand: Central Boiler
  • OWF Model: CB6048
    • View Profile
    • Edge Metalworks
Re: heat exchanger problem
« Reply #4 on: February 02, 2009, 07:27:12 PM »

I am running a standard Taco 007-F5 pump.  But it worked great before I added the second excanger.  Then to test out the small pump theory, I shut off the valves going to the first furnace and all but one floor loop, (the shortest) so the pump was pushing through the second exchanger, then through one floor loop and back to the OWB.  It still cooled down.

I do have zone valves on the 3 floor zones hooked to seperate thermostats but I shut the valves to the 2 loops when I did that test.

I didn't do anything to the furnace blower, just switched the fan on and off.

I can't shut off everything but the furnace, as you can see in the picture, I have to leave one floor loop open to circulate back to the OWB.

I do have a mixing valve right before the floor valves, and I've playes with that.  The small furnace still cools down the Xchanger.

Both lines to both furnaces are 3/4" PEX.

I'm up for either getting a stronger pump, or a "booster pump" or redoing my plumbing.
If anybody wants to attempt to sketch up a quick diagram now knowing what I have... I'd be real happy...
Logged
Hudson, WI

Dirtslinger

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Woodmaster
  • OWF Model: 4400
    • View Profile
Re: heat exchanger problem
« Reply #5 on: February 02, 2009, 07:41:47 PM »

I am running a standard Taco 007-F5 pump.  But it worked great before I added the second excanger.  Then to test out the small pump theory, I shut off the valves going to the first furnace and all but one floor loop, (the shortest) so the pump was pushing through the second exchanger, then through one floor loop and back to the OWB.  It still cooled down.

I do have zone valves on the 3 floor zones hooked to seperate thermostats but I shut the valves to the 2 loops when I did that test.

I didn't do anything to the furnace blower, just switched the fan on and off.

I can't shut off everything but the furnace, as you can see in the picture, I have to leave one floor loop open to circulate back to the OWB.

I do have a mixing valve right before the floor valves, and I've playes with that.  The small furnace still cools down the Xchanger.

Both lines to both furnaces are 3/4" PEX.

I'm up for either getting a stronger pump, or a "booster pump" or redoing my plumbing.
If anybody wants to attempt to sketch up a quick diagram now knowing what I have... I'd be real happy...

add a booster pump but I think the 3/4" line is the problem going that distance
Logged
Dirtslinger
Brockway, PA

Dirtslinger

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Woodmaster
  • OWF Model: 4400
    • View Profile
Re: heat exchanger problem
« Reply #6 on: February 02, 2009, 07:50:31 PM »

Can you slow down the blower o the new furnace
I messed around with my blower to see what worked best  I can change from low ,med,high
on high it cools it way down I have mine on medium now and it works good if you can switch to low speed it might not cool it down and allow the pump to keep up
Logged
Dirtslinger
Brockway, PA

Scratch

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 278
  • OWF Brand: Central Boiler
  • OWF Model: CB6048
    • View Profile
    • Edge Metalworks
Re: heat exchanger problem
« Reply #7 on: February 02, 2009, 08:04:20 PM »

I can try the blower speed easily enough, but you think 3/4" is too small for that distance?
Logged
Hudson, WI

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: heat exchanger problem
« Reply #8 on: February 02, 2009, 08:07:32 PM »

correct meif i am wrong (as i ahve been about your line sizes, i apologize) how does your return water get back to the furnace, it almost looks like from your diagram that the return water has to pass through your mixing valve to the radiant header?
if this is the case then you are resticting the flow rate of the return water?

i am almost sure i can't be seeing this right but i have to ask
Logged
home made OWB (2012)
Ontario Canada

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: heat exchanger problem
« Reply #9 on: February 02, 2009, 08:24:57 PM »

pardon my bad spelling in the last post but when i look at your drawing again it looks as though your mixing valve (if that is what is to the left of the top valve in your radiant drawing) may be hooked up wrong. it looks as though your return from your home furnaces must pass through this valve to get back to the OWB. if this is true this is where you are restricting your flow.

if what i am describing is true then your fix looks simple
Logged
home made OWB (2012)
Ontario Canada

MarkP

  • Full Member
  • ***
  • Offline Offline
  • Posts: 112
  • OWF Brand: Homebuilt
  • OWF Model: Hillbilly #3
    • View Profile
Re: heat exchanger problem
« Reply #10 on: February 03, 2009, 06:53:46 AM »

One thing I don't see mentioned is the elevation of the furnaces, plus the depth of the lines underground.  Is any of this run into a basement and back up to ground level or above?  The 007 ony has a head of just less than 11 feet, per the Taco spec. sheet, but even at 4 feet, the GPM is cut to about 12, from 23 at ground zero.

I am using a Taco 007 to transfer water to my house with no problems.  The lines are 38" deep, and the HX is about ground level in the ductwork under my house.  No problems.

3 weeks ago, I installed a furnace in my garage.  I purchased a second 007 for the garage, and installed a HX/blower hanging from my ceiling.  The total run to the garage is only about 15 feet total.  I turned on the pump, and the HX was hot in a matter of seconds.  I turned on the blower, and had heat for about 30 seconds.  I tried this several times, but no change.  The total height of the furnace in the garage, plus the depth of lines underground pushed the height to around 11 feet.  I either had to buy a larger pump, or lower the furnace.  I remounted the furnace under the stairway in the garage, and have had no problems since. 

The Taco website has an easy to read chart on the GPM curve at all heights.  These are calculated at no resistance.  Now, add in other appliances, smaller lines, etc.,  Do you think the 007 is capable of keeping up?
Logged
Homemade OWB  (Smokey)
Stihl 290, 2 Stihl 170s
Tractor supply 22 ton splitter
One good woman that can cut and split wood
Le Roy, WV

CL-Ohio

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 14
    • View Profile
Re: heat exchanger problem
« Reply #11 on: February 03, 2009, 06:56:03 AM »

OK my two cents, don't know if it matters but I to have two air exchangers but I didn't split off the lines fearing the water would flow unevenly because of different run lengths so it took more line but I ran everything in series so there was no doubt the water went the right direction.
Logged

MyLeakyWoodDoctor

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 72
  • MyIcyLeggedWoodDoctor
    • View Profile
Re: heat exchanger problem
« Reply #12 on: February 03, 2009, 11:53:15 AM »

Well,

Are you sure there is no blockage?  ::)

Can you test your new heat exchanger to ensure there is no flow restriction?   :bash:

Leaky :bag:
Logged

Scratch

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 278
  • OWF Brand: Central Boiler
  • OWF Model: CB6048
    • View Profile
    • Edge Metalworks
Re: heat exchanger problem
« Reply #13 on: February 03, 2009, 12:35:41 PM »

The return from both furnaces, go into the mixing valve which is wide open, then into the rad heat manifolds.  I went off from this drawing which shows the hot going into the water heater, then into the HX then into the manifold and out. 

http://www.centralboiler.com/Tech/C190.pdf

I just realized now though that it shows a note where the hot water splits and goes directly out to the OWB "and" to the rad heat manifolds.  Really?  I would think that since the rad heat lines are 1/2" and the return to the OWB is 1", the hot water would want to skip right past the rad heat manifold.

As far as height goes, my pump is about 5 feet below the ground my OWB is sitting on.  the HX's are about 2-3 feet at most above the pump but the 3/4" PEX that feeds both HX goes up to the ceiling which is about 4' above the pump.

I do remember blowing through the second HX before I hooked it up, but didn't notice any restriction... of course I was just using my mouth.

The reason I split the two lines was I figured that the longer run would cool down faster than the shorter run, so if I ran them in series, the water would be alot cooler going into the floor lines.  This way there would be a mix of hot water and really hot water going into the floor lines.


But again... I shut everything else down remember.  Here's what I have for loops, approximate lengths:

1 main furnace run, 3/4",  20 feet total
1 second furnace run, 3/4", 190 feet total
1 garage rad heat loop, 1/2", 560 feet total
1 under garage rad heat loop, 1/2" 560 feet total
1 basement bedrooms rad heat loop, 1/2", 400 feet total

And it's been working great on all but the second furnace.  The main HX stays hot, the floor lines stay hot, no problems. 
So then I shut the valves to the main furnace and 2 of the long floor loops so now, all it was going through was:

1 second furnace run, 3/4", 190 feet total
1 basement bedrooms rad heat loop, 1/2", 400 feet total

and the fan cooled it down right away.
« Last Edit: February 03, 2009, 12:38:40 PM by Scratch »
Logged
Hudson, WI

CL-Ohio

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 14
    • View Profile
Re: heat exchanger problem
« Reply #14 on: February 03, 2009, 03:36:47 PM »

So if you shut other lines down and still not enough heat recovery, you need to increase volume of heated water go 1" lines which might require bigger pump. That's what I got going with no probelms and like I mention earlier in series or you might need a back flow preventer on the longer line . I've been monitoring my line temp and losing about 10-13 deg. when blower kicks on. if that helps any
Logged