Re: 5036 cenral boiler
« Reply #15 on: November 28, 2009, 11:41:01 AM »

Hy , im looking at bying a central boiler cl 5036 next spring .I live in northern New Brunswick Canada (north of main ) im looking at some winter temperature of - 30 in the peak winter months . the only thing i noticed is the way the fuel box is built . very good for heat transfer but  i m affaide the smoke is going to comme out the door all the time i will be loading it . and the fact that ther is no force draft fan on it bothers me a little . any coment from any body will be appreciated .
I wouln't worry about the smoke coming out the door while loading.  You'll get some but not enough to care.  I have a bag of marshmallows out by my stove and my kids and I roast them sometimes standing in front of the door.  Don't get me wrong.... You're gonna smell like smoke for a while, but that's a small price to pay for the savings you'll see.

The forced draft fan is best in my opinion for burning wet or green wood.  If your wood is dry, you won't need it.  Although you can get one from the factory and it might be nice for starting fires during the warmer months.  Once it gets cold out and you need the heat in the house all the time.  You'll only have to light it once and it'll burn all season long.
Logged
Hudson, WI

jon d

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
    • View Profile
Re: 5036 cenral boiler
« Reply #16 on: November 28, 2009, 05:09:11 PM »

I've had a 5036 for 2yrs. I like the fact it has no blower. Less heat being forced out the chimney--they recover/cycle just fine for me. The draft door opens 10degrees below water temp. setpoint not allowing water temp. to drop too low. If you fill your owb just before it starts it's heating cycle the smoke is not bad.. 
Logged
jon d
Hawesville, Kentucky
Central boiler 5036

RMRranche

  • Newbie
  • *
  • Offline Offline
  • Posts: 2
    • View Profile
Re: 5036 cenral boiler
« Reply #17 on: November 29, 2009, 04:47:01 AM »

Thanks for the advice . any of you looked at the water drum . meanig if you look at the boiler side view drawing the ripple on the top are water pocket . i just want to make sure that there is a countinuous flow in those ripple . whont the debris tend to remaine there . and finaly what test do you perform on that water ex PH , alcalinity etc . becase i am a boiler operater by profession and the water quality is the life of your boiler . thanks again .by the way this forum is grate.
Logged

Alan

  • Newbie
  • *
  • Offline Offline
  • Posts: 17
    • View Profile
Re: 5036 cenral boiler
« Reply #18 on: November 29, 2009, 07:21:51 AM »

Testing Supply Water
Before filling the furnace with water, test a sample of
the supply water that will be used to fill it (softened
water is best, if possible).
1. Collect a small sample of the water to be used to fill
the furnace in a clean container.
2. Dip the pH indicator tape from the test kit in the
water. Shake excess water off the paper. Compare
the color of the tape to the chart provided with the
test paper to determine pH level. .
3. If the pH level is between 6.5 and 8 and there are no
other known water quality problems, then the
furnace may be filled with this water.
4. If the water to be used to fill the furnace has a pH
level of less than 6.5 or greater than 8, a sample of
the water should be sent to a water quality test lab
for recommended treatment, the water should be
conditioned, or water should be supplied from a
different source.
Corrosion Inhibitor Plus and Initial Treatment
Central Boiler Corrosion Inhibitor Plus (pin 1650) gives
optimum protection when the water is initially treated to
a nitrite level of 20 drops of permanganate reagent.
The recommended initial treatment rate for the furnace
is specified by units. One unit of the Corrosion Inhibitor
Plus is a l-gallon container. The normal rate for the initial
treatment is dependent on the model: CL 4030, CL
5036 and SCL 5036 - 1 unit; CL 6048 and SCL 6048-
2 units.
NOTE: If the system has a larger than normal
water capacity, more Corrosion Inhibitor Plus
should be added at a recommended rate of one
unit per 180 gallons of water.
Section 3 - Maintenance Instructions
I. Add the recommended amount of Corrosion
Inhibitor Plus through the vent pipe at the top of the
furnace.
2. Immediately fill the furnace to the FULL level mark
on the sight gauge.
3. Start the pump(s) and circulate water for 24 hours.
4. See Obtaining System Water Sample for
instructions on collecting a test sample.
5. Use Test Kit (pin 405) when no antifreeze is present
in the water. Use Test Kit (pin 597) when antifreeze
has been added to the water.
6. Remove and dip one strip of pH paper into the water
sample. Shake excess water off the paper. Compare
the paper color to the color chart in the kit. The pH
of the water should now be between 8.0 and 9.5.
7. Rinse and fill the sample tube to the 25 mL mark
with treated water from the furnace.
8. Add 25 drops of Sulfuric Acid (pin 404) to the water
sample and swirl to mix.
CAUTION
Sulfuric Acid is a corrosive acid. Handle
carefully.
9. Using the dropper, add Permanganate Reagent (pin
403) one drop at a time, swirling the water and
counting each drop, until the color changes from
colorless to a faint pink that persists for at least one
minute.
NOTE: Always hold the dropper in a vertical
position to ensure proper droplet size.
10. If the nitrite level is not at least 20 drops by nitrite
test, add 112 unit of Corrosion Inhibitor Plus (pin
1650); then circulate water for 24 hours and repeat
procedure, as needed, to achieve a nitrite level of at
least 20 drops by nitrite test.
11. Do not exceed treatment of higher than 30 drops by
the nitrite test. If the test requires more than 30
drops, dilute the water by draining water from the
system until the water level just reaches the bottom
of the sight gauge and then perform steps 2-12.
CAUTION
Before draining water from the system, make
sure the firebox is not hot.
12. After the proper nitrite level has been obtained,
check pH to make sure it is between 8 and 9.5.
After the initial treatment, maintain the nitrite level
between 15-20 drops by the nitrite test. One drop of permanganate
reagent equals approximately 100 ppm.
31
Logged
Alan  Marydale ky

critter

  • Newbie
  • *
  • Offline Offline
  • Posts: 1
    • View Profile
Re: 5036 cenral boiler
« Reply #19 on: December 29, 2009, 03:03:18 PM »

We have owned a Central Boiler for six years.  Everything was great til this year. Corrosion on the side panels were discoved in Mid October.  We have had to send the stove back to factory for repairs.  Costing us alot.  It is now the end of December - we still do not have the stove back!  Minnesota is cold! Not at all happy.  Shouldn't such an investment last longer?
Logged

jon d

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
    • View Profile
Re: 5036 cenral boiler
« Reply #20 on: December 29, 2009, 05:02:27 PM »

Critter, sorry your having problems. Wondering if u took any pics u could post. What yearly post season maintaince did u do? I've had the same unit now for 3-years. Not good news for CB. Good luck & keep us informed of your experience involving problems with CB.....
Logged
jon d
Hawesville, Kentucky
Central boiler 5036

cooch

  • Newbie
  • *
  • Offline Offline
  • Posts: 49
  • central NH C.B. 5036
    • View Profile
Re: 5036 cenral boiler
« Reply #21 on: January 07, 2010, 09:11:08 PM »

critter, sorry to hear about corrosion problems. Has c.b. taken care of the problems yet? Those of us who are only a few years into the owb experience with a c.b.5036 will be very interested in the final outcome of warranty response.
An investment with this kind should last many years. I hope they take good care of you.
Logged

woodywoodchucker

  • Newbie
  • *
  • Offline Offline
  • Posts: 48
  • central boiler 5036
    • View Profile
Re: 5036 cenral boiler
« Reply #22 on: June 01, 2010, 06:19:42 AM »

We have owned a Central Boiler for six years.  Everything was great til this year. Corrosion on the side panels were discoved in Mid October.  We have had to send the stove back to factory for repairs.  Costing us alot.  It is now the end of December - we still do not have the stove back!  Minnesota is cold! Not at all happy.  Shouldn't such an investment last longer?
Have you got anything from CB yet?
Logged

jon d

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 80
    • View Profile
Re: 5036 cenral boiler
« Reply #23 on: June 16, 2010, 08:22:31 PM »

Any news on this would be great,,,,thanks
Logged