Author Topic: Boilover on a regular basis  (Read 594 times)

MarineRecon

  • Newbie
  • *
  • Offline Offline
  • Posts: 3
  • OWF Brand: WoodMaster
  • OWF Model: 4400
    • View Profile
Boilover on a regular basis
« on: October 31, 2013, 04:55:08 PM »

We have a couple year old 4400. No problems until this year….The set point is 170 and the stove regularly goes way past to boil over.

Pump works fine and fan works fine…

Where should I start looking?
Logged

slimjim

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2553
  • OWF Brand: portage and main
  • OWF Model: Enviro 500 wood chip boiler
    • View Profile
    • www.mainlycustom.com
Re: Boilover on a regular basis
« Reply #1 on: October 31, 2013, 05:10:01 PM »

Door Gaskets
Logged
Portage and Main dealer
trouble shooting rep in northeastern US and Canada

pintopaul

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 89
  • OWF Brand: wood master
  • OWF Model: model 434
    • View Profile
Re: Boilover on a regular basis
« Reply #2 on: October 31, 2013, 05:53:42 PM »

does this model have the fan and damper on the door? if so make sure the fan damper is closing ,just cause the fan is working doesnt mean the damper is closing.
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3719
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Boilover on a regular basis
« Reply #3 on: October 31, 2013, 07:24:26 PM »

Solenoid could be a bit rusty or door gaskets...  Spray solenoid with some oil and manually work it up no down
Logged
Dealer for:  Heatmaster, Empyre, Natures Comfort, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

Goat Herder

  • Newbie
  • *
  • Offline Offline
  • Posts: 7
  • OWF Brand: WOODMASTER
  • OWF Model: HEAVY DUTY 4400
    • View Profile
Re: Boilover on a regular basis
« Reply #4 on: November 19, 2013, 08:45:26 PM »

Noob, with same problem, purchased a house with a Woodmaster 4400 installed, boiling over.  What does a good door gasket look like and where is the selinoid that might need spraying?  Thanks in advance. 
Logged

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 560
  • OWF Brand: Hardy
  • OWF Model: H4
    • View Profile
Re: Boilover on a regular basis
« Reply #5 on: November 20, 2013, 04:22:06 PM »

Check your loading door gasket where you load your wood into, check your ash cleanout door if your model has one. Your solenoid is under that cover on the front door. What it does is lift a small flapper door that covers the intake for the fan so that it doesn't pull air through the opening for the fan when the aquastat is not calling for heat. Make sure that this door is also sealing over the fan opening.
Logged

Goat Herder

  • Newbie
  • *
  • Offline Offline
  • Posts: 7
  • OWF Brand: WOODMASTER
  • OWF Model: HEAVY DUTY 4400
    • View Profile
Re: Boilover on a regular basis
« Reply #6 on: November 21, 2013, 05:05:22 AM »

Honda racer, thanks for the input, you are 100% on the money.  I looked at this last night, the door seal is not tight was creosoted up and the little rubber flapper had dry rotted a 1/4" crack in the bend.   I replaced the door seal with a 5/8" seal which was too small but got me going and ordered a one inch door seal online last night along with a new flapper.  The stove is currently working properly with no runaway temps.  I also found a manual online which always helps. 

The stove is a Woodmaster 4400 Heavy Duty model.  The more I use this the more I like it.

To help pull the door tight for now, I slid some lock washers over the door bar for a spacer that rubs or contacts with the inner wall.  In an emergency with a leaking seal, this might be something a person could do until there parts arrived.
Logged

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 560
  • OWF Brand: Hardy
  • OWF Model: H4
    • View Profile
Re: Boilover on a regular basis
« Reply #7 on: November 21, 2013, 06:32:23 AM »

Glad you got it figured out. Most don't think to check the seals each year but it is common for them to only last a season or two before needing replacement. I have a buddy with a Shaver(yeah I know :bash:) who had runaway issues constantly. We put the fan damper mod on it along with replacing the awful silicone door seals. No more boiling!