Plate heat exchanger.
«
on:
September 19, 2011, 06:44:31 AM »
I'm in the process of hooking up my new Portage and Main Optimizer 250 and have a question. I have a 20 plate heat exchanger for my domestic hw. Does it matter if you install the the exchanger in the upright position or can you lay in on its side with the outlets sticking toward you?(long ways horizontal). Also does it matter which port if inlet and outlet? It would plumb in a lot easier to lay it on it's side. Thanks for any feedback.
Logged
Portage & Main 250 - Gasser
yoderheating
Hero Member
Offline
Posts: 833
Re: Plate heat exchanger.
«
Reply #1 on:
September 19, 2011, 06:51:31 AM »
It doesn't matter so long as you do not hang it with the outlets down, in that position it has a higher chance of getting air locked in the top. Make sure you install with the water from the boiler running the opposite way from the domestic water, it will make your domestic water hotter.
Logged
Southwest Virginia
WF4000 Heat Master
Bull
Hero Member
Offline
Posts: 662
OWF Brand: Hardy
OWF Model: Rebuilt H2
Re: Plate heat exchanger.
«
Reply #2 on:
September 19, 2011, 07:05:12 AM »
Welcome to the site Skyking
Logged
Southern Indiana
Just outside of the "Small Town"
skyking
Training Wheels
Offline
Posts: 31
OWF Brand: Portage & Main
OWF Model: 250 Optimizer - Gasser
Re: Plate heat exchanger.
«
Reply #3 on:
September 19, 2011, 09:29:36 AM »
Thanks for the replies and the good information. Will get a picture or two on here when I get it completed. Should get it fired up in a week or two.
Logged
Portage & Main 250 - Gasser
RSI
Hero Member
Offline
Posts: 3100
OWF Brand: HeatMaster
OWF Model: G200 and B250
Re: Plate heat exchanger.
«
Reply #4 on:
September 19, 2011, 03:36:31 PM »
If at all possible, I would put it vertical. It is a lot easier to get the air out.
Do you get much air in your pipes from the well? If you do, you will want to make sure you put the boiler fittings on the bottom. Otherwise air will get trapped in it and cut the efficiency way down.
Logged
yoderheating
Hero Member
Offline
Posts: 833
Re: Plate heat exchanger.
«
Reply #5 on:
September 19, 2011, 06:41:22 PM »
RSI is correct, the biggest problems with plate heat exchangers is air lock. Anything you can do to avoid this is good.
Logged
Southwest Virginia
WF4000 Heat Master
donahuej
Jr. Member
Offline
Posts: 56
OWF Brand: American Royal
OWF Model: 7300
Re: Plate heat exchanger.
«
Reply #6 on:
November 07, 2011, 12:41:12 PM »
Might be a dumb question but; how do you clear an air lock from a plate exchanger?