I am not at all familiar with the grundfoss pumps. But this is what I have and it works well and I know I have room to spare. My boiler is 60 feet from the house and has a taco 011 mounted on it. The 011 pushes through 60 feet, to the house through 1" pex lines, through 40 feet in the house to the air exchanger that has a 18"x18" coil, also has a parallel loop of 3/4" pex lines about 50' long total that go to a water to water exchanger and side arm heater in series. I split off in parallel at the fan coil. I get sufficient flow from the pump and know this because when the heat is on and the bathtub (largest water demand in our home in terms of gpm) I see a water return temp that is about 30 degrees less than feed temp at the boiler. My fan coil and water heat sit about 10 feet lower than the boiler.
This is all just for comparison though. What you really need to do is calculate your required gpm flow rate (10,000 btu per 1gpm at 20 degree Fahrenheit temp drop) and calculate your head loss and then study a flow chart for the pumps your considering. Grundfos should have one available that shows all their pumps. Follow the head in ft lines and the gpm line and pick the one nearest the point they intersect. Slightly larger is good if you didn't calculate all your fittings individually as these add to head loss. Every tube and pipe and pex manufacturer, along with fitting manufactureres, along with heat exchanger manufactures all offer flow and head ratings, charts, and calculations for their products. Add up the total feet of tubing you will use, calculate the pump head in feet. Add up all the fittings values for head loss in feet. Add in the head loss value of your heat exchanger to the above two, and you have your total pump head.
Here is a good read on how to go about this all and has examples. They also use the standard 10,000 btu per 1 gpm figure in their examples.
http://www.pexuniverse.com/content/how-size-circulator-pump