Heat draw from a plate exchanger
« on: February 26, 2012, 06:37:46 AM »

Hi all -

Quick question; how much heat loss do you see across a 30 plate heat exchanger?  I have a 30 plate stainless with 1" supply and returns, 1" copper for my boiler and well water supply loops and I see 25 -30 degree drop when filling the big tub in the house. My boiler uper limit is 180 degrees lower is 170ish. I have digital temp gauge with leads zip tied and metal taped to my copper lines right after the thermopex enters the crawl so my readings are right on the money. Normal or what?  I have a constant supply of really hot water, not complaining, just want to see what others are experiencing..

Thnaks,

Jamie
Logged

gmviso

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 79
  • OWF Brand: Central Boiler
  • OWF Model: CL5036
  • Northeast Indiana
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #1 on: February 26, 2012, 08:16:30 AM »

Well, I have  5 x 12 - 20 plate exchanger with 1" supply and returns and see a drop of about 22 degrees across it when running my tub spout full open. But, note what my brazed plate exchanger dealer states that Any brazed plate heat exchanger can have higher or lower performance data based on temperatures, flow rates, and other variables.

That being said yours is probably about right.
Logged
Central Boiler CL5036

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Heat draw from a plate exchanger
« Reply #2 on: February 26, 2012, 08:28:28 AM »

It depends on how big your pump is and how much pipe you have. If you want less temperature drop you would need a larger pump.
Logged

donahuej

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 56
  • OWF Brand: American Royal
  • OWF Model: 7300
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #3 on: February 26, 2012, 08:35:41 AM »

B&G PL36 about 400 feet of 1" copper suppling DHW and two water to air exchangers.
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #4 on: February 26, 2012, 08:37:27 AM »

B&G PL36 about 400 feet of 1" copper suppling DHW and two water to air exchangers.

What's the deal on 400 feet of copper?  Is it underground?
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

donahuej

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 56
  • OWF Brand: American Royal
  • OWF Model: 7300
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #5 on: February 26, 2012, 09:15:14 AM »

Sorry 140 feet (round trip) of therompex in that number.  The coper is in the crawl...
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Heat draw from a plate exchanger
« Reply #6 on: February 26, 2012, 11:36:51 AM »

So you have 400' of copper and 140' of pex in the loop?
For every elbow in the copper you need to add 5.2 feet to the length when figuring restriction.

With the length of pipe you have and a big heat load like that you should be fine with that temperature drop.
Logged

donahuej

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 56
  • OWF Brand: American Royal
  • OWF Model: 7300
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #7 on: February 26, 2012, 05:50:35 PM »

240' copper - 140' pex total 400' did not add the 90's...thanks for the help.  No problems just was wondering what y'all were seeing.

Thanks again,

Jamie
Logged

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #8 on: February 26, 2012, 06:10:15 PM »

scott, what side of the ex should the bigger pump be on ? I have taco 007 on both sides of my ex, i have a 011 sitting in a box on the floor not shore witch side to put it on to get the most out  of the ex.
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #9 on: February 26, 2012, 07:51:42 PM »

scott, what side of the ex should the bigger pump be on ? I have taco 007 on both sides of my ex, i have a 011 sitting in a box on the floor not shore witch side to put it on to get the most out  of the ex.

Not sure which side would be best.  RSI knows a lot more about pumps than I do
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Heat draw from a plate exchanger
« Reply #10 on: February 26, 2012, 09:49:38 PM »

What is each side pumping through?
Logged

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #11 on: February 27, 2012, 04:52:59 AM »

one side comes from the wood furnace 14' away, pump is at wb. the other one just goes to the oil burner and back to ex 2' round trip the ex is at the oil burner both pumps run continously. I have a third pump that pushes it up stairs!
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Heat draw from a plate exchanger
« Reply #12 on: February 27, 2012, 06:48:13 AM »

It would probably be best to put the 0011 on the outdoor boiler side of the plate. It you only have 2' of pipe on the indoor side the 007 should be moving a lot of water. (assuming it is at least 1" and not all elbows)

How much temperature drop are you getting between the supply and return lines on the outdoor loop?
Logged

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: Heat draw from a plate exchanger
« Reply #13 on: February 27, 2012, 07:27:33 PM »

not sure how accurate  but the wb set @ 195  and it returns @180 I only have a gauge on the return side of wb!
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Heat draw from a plate exchanger
« Reply #14 on: February 27, 2012, 07:53:35 PM »

Can you move the gauge easily? If so put it on the supply side and see how it compares to the boiler gauge.