Welcome, Guest. Please login or register.
Did you miss your activation email?

Username: Password:

Author Topic: Problem with wood boiler water PSI being too high  (Read 11450 times)

Ross

  • Newbie
  • *
  • Offline Offline
  • Posts: 2
    • View Profile
Problem with wood boiler water PSI being too high
« on: November 26, 2011, 08:07:12 PM »

I have an indoor wood fired boiler (New Yorker) with an expansion tank, 35 psi pressure relief valve and an automatic water regulator set at 12 - 15 psi.  The system is a closed hot water system with finned baseboard rads/ 

My problem is that the water pressure is running at 32-35 psi constantly, causing the pressure relief valve to blow off, but no water is being added to the boiler since the pressure is so high.  I have been told this is caused by air in the system somewhere.  I don't know of any way to get rid of the air except by draining the entire system and refilling system.  Due to the cold weather, this is not really an option presently.

If anyone can offer any suggestions \ advice it would be greatly appreciated, thanks.

Ross Kennedy
Nova Scotia , Canada
Logged

rhugg

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 76
  • OWF Brand: Legend
  • OWF Model: 6180
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #1 on: November 26, 2011, 08:35:40 PM »

As I remember my old oil boiler had an expansion tank but it had one or two Taco air vents that would capture and eliminate air.  Has your system been running for a long period with no problem prior to this?  Why would it be getting air in a closed system now?

Is it possible the relief valve or pressure regulator are acting up?


Logged

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #2 on: November 26, 2011, 08:48:06 PM »

As a closed loop OWB user here.. Open the relief valve and let water out it will bring down the pressure..
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Problem with wood boiler water PSI being too high
« Reply #3 on: November 26, 2011, 09:08:44 PM »

Does the pressure go up and down with the temperature? If so the problem is the expansion tank. If it is a bladder type then the bladder probably broke and if it is just a tank with air space it probably filled up all the way.

If this is the problem, the reason the pressure got so high is because when the boiler was not running the water shrunk and the pressure went below the fill valve pressure. Then when you fired it up the water expanded and had no where to go.
Logged

BoilerHouse

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 368
  • OWF Brand: Home Built
  • OWF Model: Fire Tube/Water Tube
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #4 on: November 26, 2011, 09:25:00 PM »

I don't think it should be running st such a high pressure.  The designers must have intended it to run below 10 psi.  Is there a control device which has failed?  Not trying to be alarmist but low water and over pressure is potentially an explosive combination.  If it were me i would allow it to cool to the point where the pressure is 0, make sure the water level is at normal, and than try to figure out why it is over firing.  Is there an aqastat that is supposed to turn on and off a combustion blower fan? 
Logged
Muskoka, Ont

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Problem with wood boiler water PSI being too high
« Reply #5 on: November 26, 2011, 09:31:51 PM »

I don't think it should be running st such a high pressure.  The designers must have intended it to run below 10 psi.  Is there a control device which has failed?  Not trying to be alarmist but low water and over pressure is potentially an explosive combination.  If it were me i would allow it to cool to the point where the pressure is 0, make sure the water level is at normal, and than try to figure out why it is over firing.  Is there an aqastat that is supposed to turn on and off a combustion blower fan?
If it has a properly sized and functioning expansion tank the pressure will not go down when it is cold. (unless it has been boiling and has steam in the system)
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #6 on: November 26, 2011, 09:43:03 PM »

Does the pressure go up and down with the temperature? If so the problem is the expansion tank. If it is a bladder type then the bladder probably broke and if it is just a tank with air space it probably filled up all the way.

If this is the problem, the reason the pressure got so high is because when the boiler was not running the water shrunk and the pressure went below the fill valve pressure. Then when you fired it up the water expanded and had no where to go.
:post:
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #7 on: November 26, 2011, 09:44:14 PM »

I don't think it should be running st such a high pressure.  The designers must have intended it to run below 10 psi.  Is there a control device which has failed?  Not trying to be alarmist but low water and over pressure is potentially an explosive combination.  If it were me i would allow it to cool to the point where the pressure is 0, make sure the water level is at normal, and than try to figure out why it is over firing.  Is there an aqastat that is supposed to turn on and off a combustion blower fan?
If it has a properly sized and functioning expansion tank the pressure will not go down when it is cold. (unless it has been boiling and has steam in the system)
Like I said open the relief valve..Let some water out.. It will bring the pressure down..I own a closed looped OWB..No different than my oil boiler that is a close loop boiler.. 35 psi isn't gonna blow the furnace apart...I had to change a relief valve before I fired it up for the season..I added too much water..Pressure was up..Opened the relief valve..Pressure normal 10-15 psi..
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

BoilerHouse

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 368
  • OWF Brand: Home Built
  • OWF Model: Fire Tube/Water Tube
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #8 on: November 26, 2011, 09:49:16 PM »

Good point - Regardless, the control device(s) should be double checked.  Something is not quite right.
Logged
Muskoka, Ont

Ross

  • Newbie
  • *
  • Offline Offline
  • Posts: 2
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #9 on: November 27, 2011, 01:00:19 AM »

thanks to everyone for all the helpful advice. 

1) Relief valve and pressure regulator have both been changed 2 days ago
2) Expansion tank has no bladder, just the tank, no air vents on the tank, tank has been drained
3) Pressure does not go up and down with temp, seems to stay at 32- 35 psi regardless of temp (as long as temp is above 120 degrees
4) Will try opening relief valve and taking some water out of the system (since I may have too much water in the system, as one poster indicated had happened with his system)
5) All control valves, etc were serviced by technician about a month ago and I was told everything was fine.  This was before I fired it up for the season.

Again, thank you all for your help, if opening relief valve does not work to correct problem then I will have a tech come in and diagnose the problem
Logged

beeman

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 251
  • OWF Brand: homemade
  • OWF Model: her name is HOT CHICK
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #10 on: November 27, 2011, 07:52:45 AM »

i also have a gas fired boiler cant recall what the presser would run but am trying to think of a way to hook my wood boiler to it  ie sidearm or tap into it and the hole thing would be little to no presser if i find the owners manule see what the presser is to run
Logged
work like a bee  1970 mgb stihl 029

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Problem with wood boiler water PSI being too high
« Reply #11 on: November 27, 2011, 08:28:53 AM »

If you let some out and the pressure comes back I would shut off the supply to the auto fill valve and see if that fixes it. It might not be completely shutting off.

Do you heat domestic hot water with it also? If you do, what type heat exchanger do you have?
Logged

beeman

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 251
  • OWF Brand: homemade
  • OWF Model: her name is HOT CHICK
    • View Profile
Re: Problem with wood boiler water PSI being too high
« Reply #12 on: November 27, 2011, 08:43:59 AM »

i think your right  RSI your house water from the main is about that 30 to 35 mine just hase a ball valve so if i kned water you have to turn it on  but the ato fill could be stuck open
Logged
work like a bee  1970 mgb stihl 029