Author Topic: Pressurized vs. Non Pressurized  (Read 5908 times)

Cabo

  • Full Member
  • ***
  • Offline Offline
  • Posts: 149
  • OWF Brand: P & M
  • OWF Model: Optimizer 250
    • View Profile
Pressurized vs. Non Pressurized
« on: March 17, 2014, 03:27:10 PM »

I was on the jobsite today discussing OWB set ups and a guy with a Central Boiler told me this past fall he had removed the plate exchanger from his set up and the thing has been running better then ever.  I questioned him about tying the 2 systems together since the house boiler is pressurized and he said that the OWB is at about the same elevation as the house boiler thus they balance out.  I continued questioning him and he said that occasionally his 2nd floor baseboards would not circulate if OWB water level wasn't kept topped off.  This whole set up seems very strange to me from what I have read on here.  Maybe I'm not understanding the situation but it seems to be working for him.
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Pressurized vs. Non Pressurized
« Reply #1 on: March 17, 2014, 04:35:17 PM »

Well....if the closed system is now hooked to a open system, it's no longer closed. Might be working great, might work great for number of years, wonder what's going to happen to the closed boiler though?

Sounds to me like he had a flow problem or should have had a larger HX.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #2 on: March 17, 2014, 05:31:07 PM »

Increased indoor boiler corrosion and he will have air problems. If not always, then occasionally. Which he has already learned from topping off the central. If there was a warranty on the indoor boiler, there isn't anymore, so instead of lasting 30-40 years, it could be as bad as just a few more seasons. Hard to judge. Taco and grundfos circulators also require a minimum psi to keep the cartridge from failing according to their manual. It's not much.
Logged
Michigan Thumber

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #3 on: March 17, 2014, 09:54:42 PM »

 With no heat exchange between the two it will work better. But there are changes that have to be done to make it work. I have one customer who wanted it done that way and has had great success for many years.
Logged
Southwest Virginia
WF4000 Heat Master

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Pressurized vs. Non Pressurized
« Reply #4 on: March 18, 2014, 03:47:30 AM »

I WILL NOT install an open system boiler into a closed system without the use of a plate exchanger for the reasons already mentioned, it WILL lead to more expensive problems down the road.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #5 on: March 21, 2014, 09:50:24 AM »

Also of note, is that once the system is all tied together and "OPEN" you should really begin to run SS or bronze pumps - the whole ozidation of pump valoute comes to mind

**yeah warrenty of gad boiler is shot once system is open

I personally went from open to closed system (OWB seperated by water to water HE) so that I could add Antifreeze to closed side and not spend $$$$ on the good glycol to add some level of freeze protection.  Also so I could install on 2nd floor, with less issues
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #6 on: March 21, 2014, 02:28:08 PM »

Also of note, is that once the system is all tied together and "OPEN" you should really begin to run SS or bronze pumps - the whole ozidation of pump valoute comes to mind

**yeah warrenty of gad boiler is shot once system is open

I personally went from open to closed system (OWB seperated by water to water HE) so that I could add Antifreeze to closed side and not spend $$$$ on the good glycol to add some level of freeze protection.  Also so I could install on 2nd floor, with less issues

If you open a system up to where it's all one, I don't like that but it you do the water treatment will be in the entire system.   Why would you need to run bronze pumps in treated water then? 
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #7 on: March 23, 2014, 07:56:11 PM »

I WILL NOT install an open system boiler into a closed system without the use of a plate exchanger for the reasons already mentioned, it WILL lead to more expensive problems down the road.
Agreed!!..I will have to say though CB does says it can be directly hooked up by depressurizing the oil boiler…. I don't dont agree with it at all with a open system
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #8 on: March 24, 2014, 07:23:03 AM »

Theres no warranty on taco and grundfos circulators when used on open or chemical treated systems unless they are bronze or stainless. I have seen Taco warranty tho when it was a real obvious manufacturer fault regardless.
Logged
Michigan Thumber

idahohay

  • Guest
Re: Pressurized vs. Non Pressurized
« Reply #9 on: March 24, 2014, 11:24:16 AM »

Side question: does it make sense to go with a stainless circulator in a stainless OWB?
Logged

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #10 on: March 24, 2014, 12:16:55 PM »

Side question: does it make sense to go with a stainless circulator in a stainless OWB?

If its an open system (ss and bronze should be your only two thoughts)  8) - If its closed loop, you will be ok with a cast iron

Oxygen is sneaky it will eat out the hardest to replace Non-ferrous components in your system.
Logged

idahohay

  • Guest
Re: Pressurized vs. Non Pressurized
« Reply #11 on: March 24, 2014, 01:34:17 PM »

LittleJohn, thats what I was thinking.  My boiler is a Heatmor and not pressurized. It has a ball on a rod in the top overflow but to me it is open and currently have a ss pump (007) but may need to upgrade and not looking forward to the cost.
Logged

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #12 on: March 24, 2014, 02:53:30 PM »

Sorry to help in the HIJACK of a thread, but idahohay - could you not just get the replacement cartridge for the pump, instead of replacing the whole pump or pump head.

How about this one - pricing between the cheapest 3-speed SS Grundfos and SS Grundfos Alpha - is typically less than $10; which is still about 3x what you pay for a cast iron pump.
Logged

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: Pressurized vs. Non Pressurized
« Reply #13 on: March 24, 2014, 04:07:45 PM »

Should always use stainless or bronze in any open system. It eliminates any corrosion lock up or failure related possibilities. And it will never add corrosion debris to the system. 007 SSF5 is under $200, a cartridge will also do but only a little cheaper than whole unit.
Logged
Michigan Thumber

idahohay

  • Guest
Re: Pressurized vs. Non Pressurized
« Reply #14 on: March 24, 2014, 05:24:46 PM »

Sorry I wasn't clear. I'm adding my in floor primary/secondary loops via fphe and the 007 will be facing more head, especially if I use 30% or more glycol so maybe higher head circulator. Sorry to get off topic.
Logged