I question the 9 foot head estimate. Does that take into account elevation, pipe length and every possible flow obstruction?
I did screw up the head calc. I have a 370' loop of 1 1/4" pex with 10 elbows, 4 ball valves, 2-5x12 plate Hx with 1 1/4" ports, and a 6' elevation difference. Disregarding the Hx the 'correct' head number is 15.6' (unless I screwed up again).
With the Taco 009 this should mean I have a flow of about 7 gpm. (
http://s3.supplyhouse.com/manuals/1350986824086/84486_PROD_FILE.pdf)
So, I had supply temps of 180 and return temps of 127 for a difference of 53 degrees, lets take away the 4 degree drop I see with no load and that's a difference of 49 degrees. Assuming I am getting a flow of 7gpm that means by turning all three thermostats up from 70 degrees to 75 degrees at the same time on a warm day, my system required 171,500 BTU?
Am I missing something or doing something wrong? These numbers just don't make sense based on what I know (or think I know).
Am I over thinking it? We had temps in the 30's this weekend and when I fixed the fire I never saw return temps below 165.