so, lets say i really am losing close to 20 degrees in a hundred ft. at 5gpm what can i do to remedy that situation?
dig em up and replace them
or if you can live with losing all that heat" speed up your gpm to deliver more heat to the house
if you upsize the pump to deliver say 8 gpm teh heat loss will be the same (or slightly more) but because you have increased teh gpm you have also increased the delivery of btu's
lets say at 5 gpm and 180 degree water you are sending 50,000 btu per hour to the home and you are losing (not actual just a figure) 25,000. so that leaves 25,000 to the home as well. if you increase the delivery to 8gpm that would be close to 80,000 btu per hour to the home and maybe only increase the loss marginally. lets say it increased the loss to 30,000 that would now still leave 50,000 for the home.
this method would work, but your wood consuption would be huge.
1 degree heat loss would be the same as 1 degree in rise for figuring...1 btu raises 1 pound of water 1 degree F Works in the opposite direction the same. 1 gal ==(for easy figures) 8 pounds, 5 gpm = 40 pounds a min going through the lines so for every degree of loss = 40 btu x 20 degree loss = 800 btu per min...48,000 btu per hour...1,152,000 per day...x 150 heating days=172,800,000 btu per season...that is more than the average home uses. so you would be using over twice the wood as a normal year with good underground lines (if my math is correct?)