Gasser is required by Law in Maryland...
We heat a 2200 sft house built in 1908 with virtually no insulation and original windows which have storm windows in place. There are 10 rooms with 10 large tube style radiators from about when the house was first built. Our heat source before OWF was a newer oil boiler, burning just over 1100 gal in a heating season.
The GX10 is CERTAINLY INADEQUATE TO HEAT OUR HOUSE. Hawken calculated it to be good. After research, I really did find that sft alone is really not the way to calculate a load... duh! should have known that, but we trusted the experts... well Hawken is NOT an EXPERT, nor do they stand behind their guarantees..
We are now considering replacing the Hawken (only a few months old) with a Central Boiler E Classic 2400. Looks like the correct BTU and sizing... the bummer is that we now have to redo it all. and in the middle of winter...
Your feedback on this is appreciated.
Don't make any rash decisions yet, it seems like if you were only using 1100 gallons of fuel oil before, the gx 10 should work. I am no expert by any means but I will share what I think I know. A gallon of fuel oil is 140,000 btu's. A newer fuel oil boiler is probably 80% effecient. 1100*140,000=154,000,000. 154,000,000*0.80=123,200,000 per heating season. 180 days in the heating season 123,200,000/180=684,444btu's per day. 684,444/24=28,518 btu's/hour. EPA burnwise table has the gx10 rated at 78,000btu's/hour for 8 hours.
On paper, that gx10 should work.....all that said, this winter has been very cold so far. With temps below 0 along with a stiff breeze I would guess your homes btu requirements could very well be 4-5 times its average requirements, which would get you down to that 6-7 hour burn time.
Has the hawken been keeping up this past week or so during more "normal" temps? Are you 100% sure your wood is seasoned? Do you plan on improving the insulation and windows in your home?