Help Ranco temp reading E2 (Wont stay running)
« on: January 30, 2013, 03:59:25 PM »

 We lost power today while I was out working. I am not sure when, or how the furnace was at the time.  A hour after I got home the power was restored. But the furnace wont stay on.  I reset breakers and temp settings...but nothing works.

The display reads e2. When I power it off and on (or reset temp settings) it clanks on and blows for about 30-60 secs that clanks off.

Water level seems ok, as in it didnt boil over.
Logged
Climb High Tree Service
Lebanon PA

Certified Arborist

"Kiss My Axe"

birchbark

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 45
  • OWF Brand: Heatmaster
  • OWF Model: 10000e
    • View Profile
Re: Help Ranco temp reading E2 (Wont stay running)
« Reply #1 on: January 30, 2013, 05:39:46 PM »

This is what is says in my manual


E2 - Appears if the control settings are not properly stored
in memory.
To correct: Re-set all settings. If the display continues
to show E2, replace the control.
Logged

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: Help Ranco temp reading E2 (Wont stay running)
« Reply #2 on: January 30, 2013, 07:27:02 PM »

Normally when a Ranco starts reading e2 its time to replace it. Sometimes you can make it last a little longer by turning of power for a few minutes but they never recover completely. Its easy to change one, just pull the cover and rewire the same way you found it. I imagine you had some sort of power surge that damaged the Ranco. At least I have had several that were damaged by either power outages or lightning.
« Last Edit: January 30, 2013, 07:28:49 PM by yoderheating »
Logged
Southwest Virginia
WF4000 Heat Master

Tree_Killer

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 38
  • OWF Brand: Heatmaster
  • OWF Model: MF5000SS
    • View Profile
Re: Help Ranco temp reading E2 (Wont stay running)
« Reply #3 on: January 30, 2013, 09:04:36 PM »

Ya i am pretty sure that is waht happen. I got it running for now. But going to get another one, and replace it.  Tomorrow I will open it up to gt model number etc.