Author Topic: now that its getting warmer ?  (Read 11066 times)

newmanab

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 22
  • OWF Brand: Central boiler
  • OWF Model: CB6048
    • View Profile
Re: now that its getting warmer ?
« Reply #15 on: March 12, 2012, 08:35:48 PM »

What hapens when you shut down for the summer the? :o
Logged

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: now that its getting warmer ?
« Reply #16 on: March 12, 2012, 08:44:56 PM »

mg/l of oxygen solubility...
20 degrees C 9 mg/l
40 degrees C 6mg/l
60 degrees C 5mg/l
80 degrees C 3 mg/l
100 degrees C 0mg/l

20= 68  degrees
40 =104
60 =140
80 =176
100=212
Logged
home made OWB (2012)
Ontario Canada

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: now that its getting warmer ?
« Reply #17 on: March 12, 2012, 09:55:29 PM »

This is such a touchy topic and not one I am really confident in.  I will however share my current thoughts.

I beleive we should keep our water as close to 180 as we can, even thought I'm 155 on 165 off.  I still think it would be better for the stove to be hotter, next winter with a gasser I'm going to 180-185 or so..

As far as 140 the magic number.....   I say you don't want your return coming back at under 140, if your pulling a lot of heat and the return water is coming back to a roaring firebox at 130, the stove will sweet inside the firebox and cause condensation that will put your furnace to an early grave regardless of brand. 

As far as the o2 in the water itself, the hotter the water up to 180 the less o2 you'll have present.
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

lugnut

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 306
    • View Profile
Re: now that its getting warmer ?
« Reply #18 on: March 13, 2012, 09:35:09 AM »

Okay, now I'm getting confused.  I have the Shaver 250 and it has the corrosion inhibitor in.  Do I need to keep that thing heated up now or can I shut it down?  Granted we are going to get "some" cool nights, like last night it dipped down to the 40s.  If I top the tank off and the inhibitor is in the water, it should be fine correct?

Lugnut
Logged
Jerry
Greenleaf, Wisconsin
Shaver Pro series 250 - Installed 10/28/2011
Cub Cadet / Yanmar 2450  sub-compact tractor
Husquvarna 455 Rancher
1999 Ford F-150 4x4 w/207k miles

tbone

  • Full Member
  • ***
  • Offline Offline
  • Posts: 111
  • OWF Brand: Heatmor
    • View Profile
Re: now that its getting warmer ?
« Reply #19 on: March 13, 2012, 11:12:10 AM »

My guess would be as long as your not moving the water you will not accumulate DO2.
« Last Edit: March 13, 2012, 11:14:12 AM by tbone »
Logged
Stihl 460
Stihl pro 360
Honda 27 ton splitter
Ford 350 with hoist

boilerman

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 270
  • OWF Brand: Central Boiler
  • OWF Model: E2400 Currently CL5648 Previously
    • View Profile
Re: now that its getting warmer ?
« Reply #20 on: March 13, 2012, 05:38:09 PM »

A good corrosion inhibitors purpose is to protect the water jacket. Does not matter if the water is 33 degrees or 210 degrees.
The problem with sending colder water back to the OWF below 150 degrees is that it shocks the furnace, causing condensation in the firebox, which is what can create wet acidic ash.
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: now that its getting warmer ?
« Reply #21 on: March 13, 2012, 07:20:13 PM »

Is that why they put the thermostatic valve in the supply and return???  So you don't shock it

Yes that's the theory behind it, it causes the firebox to sweat if return water is to cold. 
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: now that its getting warmer ?
« Reply #22 on: March 13, 2012, 07:27:15 PM »

A good corrosion inhibitors purpose is to protect the water jacket. Does not matter if the water is 33 degrees or 210 degrees.
The problem with sending colder water back to the OWF below 150 degrees is that it shocks the furnace, causing condensation in the firebox, which is what can create wet acidic ash.

I don't see how sending colder water back to the OWB "shocks" it and then causes condensation in the fire box.. After all you have a live fire in the box.. If anything burning wet green wood would cause the condensation
« Last Edit: March 13, 2012, 07:33:49 PM by MattyNH »
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: now that its getting warmer ?
« Reply #23 on: March 13, 2012, 07:37:39 PM »

Matty, what happens when you first fire the stove?  Water runs down the inside walls from condensation because it's surrounded by cold water, every Customer I have met freaks out on there first fire, I have to stand there and calm each one down and explain why it's sweating

The same thing happens in operation if your return water is to cold, empyre had a customer with a pro400 who had a huge pool exchanger which was sending his water back at like 100, the stove sweated internally until it failed, the customer was taken care of and empyre started installing a feature that shuts the pump off if the return gets to cold.  This guy had likes 500kbtu pool exchanger on his, so it wasn't a normal application
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: now that its getting warmer ?
« Reply #24 on: March 13, 2012, 08:01:47 PM »

Scott, I can see that at the very start of OWB for the season..Everything is cold..The water, the unit itself, pipes etc....I don't see it happening when the OWB has been running for a season/ got a nice fire in the box..Then you decided to turn the temp a bit. Shouldn't have any problem with water in the fire box unless you burn wet/green wood..a low temps.... Far as  the Pool exchanger sounds like the unit wasn't even big enough..So ya not a normal application
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: now that its getting warmer ?
« Reply #25 on: March 13, 2012, 08:08:00 PM »

No....  I don't see how u think it makes a difference..  I mean the stove don't know if it's the first fire or the 400th!  If there is cold water being introduced to the stove it's going to sweat, I domt care if it's October 1st or january first, cold water is cold water.

The unit was not the problem as it heated the pool fine, if anything was to big it was the pool exchanger, pulling to much heat off....   Another way of having that problem if the pool exchanger and stove are sized right is a pump not flowing fast enough.  If it is in the pool exchanger to long it pulls off to much heat...

Return water temp is very important, the first fire example is as goodas I can get, if you think cold water being introduced at a different time would make that different I'm not sure what you mean
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: now that its getting warmer ?
« Reply #26 on: March 13, 2012, 08:08:39 PM »

there is evaporation and condensating going on all the time..the heat in the fire boils the water from  teh wood and the air that is feeding the fire... this moisture hits teh walls of the water jacket and instantly starts to turn back to liquid. i thin this happens no matter what the temp unless the steel jacket is boiling

one of the reasons there is so much on first start up is everything is cold and until everything is warmed up(including the chimney where there will be a lot of condensate) there will be more condensing than at normal operating temps.

im not so sure on this shocking thing but i can't disprove it either so i am neutral

the only reason to turn down your temps i can see (there will be some small savings in wood consumption but i dont think any thing much) would be if your underground lines were bad (if you used lower water temp your loss to the earth would be slower due to the temp. spread)  or if your boiler leaked air and  because the heat draw would be less in warmer weather it may boil over if left at the higher setting (lets say your shut off was 180 adn air leaked in it may (if the hosue was not drawing for an extended peiod of time) slowly crawl up to boiling. by setting the shut off temp lower you would by your self some more time between 'calls for heat" and you would  use some heat before boile over occured
Logged
home made OWB (2012)
Ontario Canada

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: now that its getting warmer ?
« Reply #27 on: March 13, 2012, 08:14:13 PM »

Well....   I don't know what to say...  All I know is what I've saw and that companies like empyre and central now require folks to run a system that shuts the pump off or something similar if return water is to cold..  Central does it different...   Empyre has a system that goes right on the back of the stove. There doin this because of problems they've had and trying to prevent it from happening again. 
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: now that its getting warmer ?
« Reply #28 on: March 13, 2012, 08:23:51 PM »

im not doubting you scott i am jsut saying that condensation and evaporation go on all the time..heck if there is a pool of water outside in the winter (as long as it is not freezing) that water gets evaporated into the air.

and i also know that some boilers have a thermostat that measures the outside air temp and adjusts the water temp inside the boiler  to accomodate for lower temps to save on fuel as they say less btu's are required per hour on warm days. how much this saves i have no idea but it is done..and how low these settings are i have no info but i have heard that return temps can be as low as 145?

the guys building these stoves that you and i use, (hopefully) know a lot more than you and i about all this thermodynamic stuff..we are paying them big bucks to get it right but some times i wonder if some of these things they add on are just sales gimmics.
Logged
home made OWB (2012)
Ontario Canada

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: now that its getting warmer ?
« Reply #29 on: March 13, 2012, 08:41:06 PM »

Scott, So your saying when my house dumps the cold water back into my boiler theres water dripping in my fire box?..Im assuming you know Hydronic's...
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188