Has anybody ever successfully changed their pipe by having whatever you used inside another pipe?
Just wondering as we install our own drain tile here at the farm and with the corrugations used on the pipe trying to slide it thru another piece of corrugated tile might be a joke at best. Maybe if the inner one was slid thru a 6" smooth bore plastic sewer pipe?
I also know the stuff my cousin installed (from Central Boiler perhaps) is stiff enough that again you'd play holy hell trying to get it to slide around any corners.
Yeah I don't think so , or worse yet when the outer shell gets full of water and holds it on the pipe your trying to protect. Those dead air spaces always fill with water if there not filled with something to keep it out. It's only a matter of time.
Rehau, logstor , Uponor Wirsbo insulated lines don't fail ever, the installers lack of a proper bed/backfill or lack of extra protection did. Anything can be made to fail in the wrong hands. Regardless of the recklace btu numbers thrown around , there is nothing better than these brands readily available on the market.
So a 1/2 degree loss in 100' at 5gpm & 180' = 1250 btu/hr x 24hr = 30kbtu/day x 182 days = 5.46mbtu/6 months
Compared to magic bubble or loose closed cell foam wrap with same flow specs but a 10 degree loss/100'
= 25kbtu/hr x 24hr = 600kbtu x 182 days = 109.2mbtu/6 months
I've seen anywhere from 6 degree loss to 18 degree loss per 100' at more than 5 GPM flow. If your snow is melting even a little bit you have more than a 6 degree loss.
If in anyway shape or form one of those fancy wrapped lines truly did perform as good or even a tiny bit better than the high dollar brands. Those multimillion dollar companies would be buying the rights to manufacturer or at least copying. AND if any of those fancy wrapped homemade pipes did perform even as good or close, they would show full detailed side by side tests, and or at least a claim on their website, ......" Ours tests as good or within 1 degree of logstor, central pex, rehau, Uponor". But they don't cuz they can't. Best you get is some claim where a few numbers are posted that look good, without the rest of the test data.
If fact one of those pipes does show >1 degree loss at 16 GPM. More than triple the speed.