Author Topic: Actual btus per hour used  (Read 3069 times)

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Actual btus per hour used
« on: December 10, 2016, 06:20:35 PM »

So I am interested in trying to figure what exactly I am using for real btus to heat my house. So I think I have the calculations right, someone please correct me if I am wrong. So I have a g200 which holds 200 gallons. If I am correct to find out how many btus are available at 180 degrees the calc is 200x8.33x180=299,880 btus. So I have timed how long my blower in the house runs for. It runs for typically 7.5 minutes at a shot. After the blower runs the boiler loses approx 3 degrees. So if my calc is correct that means that 200x8.33x177=294882. If we deduct 299880 from 294882 we get 4998 btus used every time the furnace runs. If we break it down further to btus used per minute we would divide 4998 by 7.5=666.4 btus per minute. Right now it's 15 degrees out and the fan is running 7.5 minutes on and 11.5 minutes off. So that means more or less the blower is running 22.5 minutes per hour. So 22.5x666.4=14,827 btus used per hour. Now that seems awful little btus used per hour to me??? My house is 2800 sqft and is 220 years old. I have I insulate apps and air sealed well but it still seems awful low on the btus per hour. I know my Woodstock fireview wood stove which should be putting out around 30k btus per hour at least can no way handle heating the house at these temps we have right now. I know that air isn't moving like the forced hot air is but still??
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Actual btus per hour used
« Reply #1 on: December 10, 2016, 07:02:40 PM »

You can skip the 180 from your equation and just multiply by the temp drop instead. You should get the same numbers.

The problem with trying to calculate by water btu capacity is that the boiler itself (steel, refractory, ashes, etc) is storing heat and there is most likely some amount of heat being generated even while the stove is idling.
Logged

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: Actual btus per hour used
« Reply #2 on: December 10, 2016, 07:16:40 PM »

Good point on just multiplying the temp drop. Are you saying that the btus used are actually greater than the 3 degree drop I see because the temp of the boiler itself radiates some and keeps the final temp of the water higher than it actually should be?
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Actual btus per hour used
« Reply #3 on: December 10, 2016, 07:30:20 PM »

Yes, at least some.
Logged

Pointblank

  • Full Member
  • ***
  • Offline Offline
  • Posts: 177
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550
    • View Profile
Re: Actual btus per hour used
« Reply #4 on: December 10, 2016, 09:03:43 PM »

Ya, i think some heat gets radiated from the boiler between cycles. My Central Boiler has a thermocouple in the secondary burn chamber. If you have a good coal bed it can still be 400-500 degrees in there 1\2 hour after it reached its set point and shut off.
Plus, if your pump runs continuous, then the heat exchanger and pex lines in the home are still radiating heat into the home between furnace cycles. I know in my house, if its above 40 degrees, the furnace rarely comes on. Just having the hot water circulating through the lines and heat exchanger dumps enough heat into the home to keep it warm.
Logged
Central Boiler Classic Edge 550
Previous- Central Boiler 5648- 13 years

Minnesota

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: Actual btus per hour used
« Reply #5 on: December 11, 2016, 05:36:07 AM »

I think my numbers may be closer to correct than I initially thought. I looked at equivalent for oil. Oil has 138k btu per gallon. At 75% efficiency that brings it down to 103k btu per gallon. If I needed 18 k btu per hour x 24 hours= 432000 per day. 432000/103000= 4.1 gallons of oil per day x 1.89 = $7.88 per day x 30 days=$245 per month. Appears somewhat low still but maybe not.
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Actual btus per hour used
« Reply #6 on: December 11, 2016, 09:02:12 AM »

It could be close. The heat loss from the boiler and underground pipe would offset some of the thermal storage of the boiler itself.
I think fuel oil has lower BTU content since they switched over to ULSD. I have heard 125k BTU but not sure if that is correct.
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Actual btus per hour used
« Reply #7 on: December 11, 2016, 02:46:16 PM »


I think fuel oil has lower BTU content since they switched over to ULSD. I have heard 125k BTU but not sure if that is correct.

Thats odd, supposedly waste oil has roughly 160,000 BTU per gallon.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Actual btus per hour used
« Reply #8 on: December 12, 2016, 02:42:33 AM »

I was taught that heating oil has 144,000 BTU's per gallon.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

schoppy

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 377
  • OWF Brand: Heatmaster
  • OWF Model: G200
    • View Profile
Re: Actual btus per hour used
« Reply #9 on: December 13, 2016, 12:30:17 AM »

Not sure about the calculations you used hondaracer but it is very hard to calculate in all the variables associated with wood burning. The fire box is continually radiating heat unless it goes out. Heat loss in the lines and boiler itself and is your home heating the only load on the boiler, no water heating or other buildings?   

A house your size would normally be sized for an 80 to 100 BTU rated high efficiency furnace with an approximate 50% cycle time. That would be for a well insulated home and the rating is normally worse case scenario(-15 to -20 temps).

Slim you are correct about fuel oil, normally 144,000 is number we used for a conversion factor when we used to convert fuel oil furnaces or boilers to natural gas. Different # oils have different BTU content as does regular diesel fuel and ULSD.

Logged
Husqvarna 562XP
Echo CS-361P
Echo CS-310
31 ton splitter

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Actual btus per hour used
« Reply #10 on: December 13, 2016, 08:37:10 AM »



Slim you are correct about fuel oil, normally 144,000 is number we used for a conversion factor when we used to convert fuel oil furnaces or boilers to natural gas. Different # oils have different BTU content as does regular diesel fuel and ULSD.

How much the difference you suppose between old school premium diesel and this new ultra low sulfur crap? Never had algae problems until they took the sulfur out, now we treat it all rather than deal with that happy crap again.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Actual btus per hour used
« Reply #11 on: December 13, 2016, 10:03:40 AM »

Yea but sulfer AND wood smoke odor are offensive to some people so the government deems it necesary to take our LIBERTY away AGAIN! Of course I bet there was not a cent exchanged?
Logged
Wood boiler sales, service and installation for the Northeastern USA.

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Actual btus per hour used
« Reply #12 on: December 13, 2016, 08:54:11 PM »

I was taught that heating oil has 144,000 BTU's per gallon.
I think it used to be 144K, then when it went to low sulfur it dropped to 139K, then when it went to ultra low sulfur it went to somewhere around 125-129k.

I may be off a bit on the numbers but I think they are around there somewhere.
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Actual btus per hour used
« Reply #13 on: December 14, 2016, 01:52:36 AM »

Another beautiful thing about burning wood, our fearless leaders can't legislate/ dictate the BTU's out of it.
Logged
Wood boiler sales, service and installation for the Northeastern USA.