Author Topic: why can't I just connect to my boiler without a heater exchanger  (Read 5618 times)

sergeant721

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 30
  • OWF Brand: Shaver
  • OWF Model: 250
    • View Profile

Dose anyone know why I have to use a heat exchanger I know the house is pressurized but if I turn the water off to the boiler in the house the system is then non pressurized all I would have to do is add a check valve on the return line to stop the water from draining out right this would eleminat alot of heat loss  I'd like everyone input  thanks
Logged

Trint

  • Full Member
  • ***
  • Offline Offline
  • Posts: 124
  • OWF Brand: Portage and Main
  • OWF Model: ml 30
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #1 on: January 13, 2012, 06:44:16 AM »

Not sure about shaver but it was an option in my instalation manual to depressurise and direct plumb, I know central boiler shows this as well in their literature.  I have my installed directly into my oil burner, hot feed tee in with the relief valve and tee out with the drain as these were the only ports available to me.  I have check valves installed to prevent gost flow also note that all my zones are below my boiler, have not connected the one on the second floor yet.   No problems so far excep I think I have a leak some where in the old system inside.

One thing I forgot earlier, bigest thing is to maintain some pressure to your circulator inside. 
« Last Edit: January 13, 2012, 03:48:54 PM by Trint »
Logged
North Central Ohio

lugnut

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 306
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #2 on: January 13, 2012, 09:18:26 AM »

Sergeant,

Did you ever contact Shaver OR your friend for an owner's manual?

Lugnut
Logged
Jerry
Greenleaf, Wisconsin
Shaver Pro series 250 - Installed 10/28/2011
Cub Cadet / Yanmar 2450  sub-compact tractor
Husquvarna 455 Rancher
1999 Ford F-150 4x4 w/207k miles

johnybcold

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 376
  • OWF Brand: Central Boiler
  • OWF Model: Classic E1400
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #3 on: January 13, 2012, 03:13:28 PM »

My cb is connected directly to my boiler the cb is higher then my boiler, the boiler is in the basement the only thing between the owb and the indoor boiler is a ball valve
Logged
old truck
old craftsman chain saw
Polaris Sportsman 500HO

MattyNH

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1284
  • OWF Brand: Crown Royal former Aqua-Therm
  • OWF Model: 7300E ; S-275
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #4 on: January 13, 2012, 03:59:11 PM »

You can hook your wood boiler without a heat exchanger..Just make sure its not below grade.. You will drain your heating plumbing...Also the problem is since the wood boiler is a "open system"..All your heating plumbing in your house is now exposed to the atmosphere (oxygen).. Thats the reason why you should/ have to use a heat exchanger..Keep the household  heating water separate from the  wood boiler water..  Just make sure your boiler water chemical specs are what the manual says..If you take that route by not using a heat exchanger....
Logged
Crown Royal 7300E (2021)
Aqua-Therm S-275 (2006)
Jonsered 2188
Jonsered 2165
Jonsered 2050
Timberwolf- TWP1 5.5 Honda 25in wood splitter
American CLS- AM48HH 8 Honda 48in wood splitter
Kubota L3800DT
Lake Winnipesaukee New Hampshire

sergeant721

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 30
  • OWF Brand: Shaver
  • OWF Model: 250
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #5 on: January 16, 2012, 09:24:14 AM »

What if I use back flow preventers so the senond floor water dose not drain out I would hook it up to the return back to the OWF
Logged

sergeant721

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 30
  • OWF Brand: Shaver
  • OWF Model: 250
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #6 on: January 17, 2012, 05:47:24 PM »

Thanks for everyones info, dont know what I should do
Logged

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #7 on: January 17, 2012, 06:58:31 PM »

I have a 40 plate ex and iam on the fence on takeing it out! my dealer said i should !
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #8 on: January 17, 2012, 07:09:41 PM »

I have a 40 plate ex and iam on the fence on takeing it out! my dealer said i should !

did your dealer give a reason to take it out fireboss? this interests me because i feel it best to keep the systems seperate.

i think that if you use the heat exchanger you only have to worry about introducing air or crud into one exchanger. And  why you would want to change the design of a heating system to run under no pressure when it was designe to run under pressure is beyond me.  why mess with something that works. i can think of no reason to make the two systems one? i would like to hear the reasoning for doing it, i know we all have our own reasons for doing things and i would like to hear some thoughts on why joining the systems would be better? if we all hear the pros and cons from a bunch of people then we all have more info to go on in future decisions
Logged
home made OWB (2012)
Ontario Canada

Trint

  • Full Member
  • ***
  • Offline Offline
  • Posts: 124
  • OWF Brand: Portage and Main
  • OWF Model: ml 30
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #9 on: January 17, 2012, 07:50:04 PM »

I have a 40 plate ex and iam on the fence on takeing it out! my dealer said i should !

did your dealer give a reason to take it out fireboss? this interests me because i feel it best to keep the systems seperate.

i think that if you use the heat exchanger you only have to worry about introducing air or crud into one exchanger. And  why you would want to change the design of a heating system to run under no pressure when it was designe to run under pressure is beyond me.  why mess with something that works. i can think of no reason to make the two systems one? i would like to hear the reasoning for doing it, i know we all have our own reasons for doing things and i would like to hear some thoughts on why joining the systems would be better? if we all hear the pros and cons from a bunch of people then we all have more info to go on in future decisions


My biggest reasons for going the direct conection root was cost and simplicity.  I renovated a house that had been vacant for several years and the exsisting pressurised system would need additional work to be able to run pressurised beyond the large amount of work already put into it.  Additionaly it saved me the cost of a large heat exchanger and the possibility of having to run 3 pumps apposed to the 2 I curently run.  Plus since both systems are combined all the water is treated and constantly being filtered.
Logged
North Central Ohio

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #10 on: January 17, 2012, 08:01:52 PM »



My biggest reasons for going the direct conection root was cost and simplicity.  I renovated a house that had been vacant for several years and the exsisting pressurised system would need additional work to be able to run pressurised beyond the large amount of work already put into it.  Additionaly it saved me the cost of a large heat exchanger and the possibility of having to run 3 pumps apposed to the 2 I curently run.  Plus since both systems are combined all the water is treated and constantly being filtered.
[/quote]
sounds like cost drove your reasoning mostly..and cost is a big factor in many of our decisons. and it sounds like your old system may allready be corroded so the depressurizing and letting air into the system that may cause mor corrosion would not be a concern likley.
Logged
home made OWB (2012)
Ontario Canada

lugnut

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 306
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #11 on: January 17, 2012, 08:17:46 PM »

Sergeant,

Did you ever contact Shaver OR your friend for an owner's manual?

Lugnut

I suppose since I've not gotten a response to this question several times...that you have not received an owner's manual either from the friend who sold you the furnace and you've not contacted Shaver.  In my humble opinion, you NEED to have this owner's manual....it MIGHT help you in many ways, though not certain regarding the situation you're having now, BUT...you might want to c all Shaver and inquire there about this issue.  Do NOT talk to Don Burge...Discuss this issue with HIS supervisor.  Just an FYI.

Lugnut
Logged
Jerry
Greenleaf, Wisconsin
Shaver Pro series 250 - Installed 10/28/2011
Cub Cadet / Yanmar 2450  sub-compact tractor
Husquvarna 455 Rancher
1999 Ford F-150 4x4 w/207k miles

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #12 on: January 18, 2012, 07:32:49 PM »

yes the ex works, but am i geting the most out of my wb? and like willieg said iam running 3 pumps and chaseing ghosts.
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

sergeant721

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 30
  • OWF Brand: Shaver
  • OWF Model: 250
    • View Profile
Re: why can't I just connect to my boiler without a heater exchanger
« Reply #13 on: January 24, 2012, 07:45:21 PM »

Hi lugnut, I got the manuel a few weeks ago thanks Im going to keep it a two system
Logged