Central boiler solenoid problems
« on: November 22, 2015, 07:12:18 AM »

So I wake up this morning to a cold house. Went outside and the water temperature was down to 148. Opened the door and the stove was full. Noticed the damper wasn't open so no air was getting to the firebox.  Took the front panel off and looked at the fuse. It had a burnt spot in the middle. I'm assuming that means it's blown?  So, how can I fix this?  Where can I order parts and get them shipped asap?  Thanks.
Logged

BoilerHouse

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 368
  • OWF Brand: Home Built
  • OWF Model: Fire Tube/Water Tube
    • View Profile
Re: Central boiler solenoid problems
« Reply #1 on: November 22, 2015, 07:49:29 AM »

Do you have an electrical supply near by?  They should have different styles, just make sure the voltage and amperage are correct.  They may even do an ohm check (using a multi-tester) on the old fuse.  Zero resistance = good fuse and Infinite resistance = blown fuse.
Logged
Muskoka, Ont

tinfoilhat2020

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 634
  • OWF Brand: POS
    • View Profile
Re: Central boiler solenoid problems
« Reply #2 on: November 22, 2015, 07:50:49 AM »

i would get a few~!~~ solenoids can go often, always nice to have a few on the shelf for situations like this!
Logged

Roger2561

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1780
  • OWF Brand: Central Boiler
  • OWF Model: Classic Edge 550 HD
    • View Profile
Re: Central boiler solenoid problems
« Reply #3 on: November 22, 2015, 07:53:04 AM »

Make sure the fuse is blown first.  If you have a volt meter, check for continuity.  If you have an analog meter; if the fuse is good the needle should move to infinity, if it's bad the needle won't move at all.  If it is bad, take the blown fuse to any auto supply store (Advance Auto, Auto Zone, Senals, etc...) they may have what you're looking for.  If not, try Radio Shack.  There is nothing special about them.  Oh, make sure you get the same type, amp rating, etc...  DO NOT get something with a larger amp rating, it could fry something else or worse, start a fire.  Report back.  Good luck.  Roger
Logged
CB Classic Edge 550 HD
JD Tractor 4500 4X4 with front-end loader
JD LX277AWS
Stihl 021
Stihl MS 311
Cud Cadet 27 Ton Wood splitter
2012 Honda Goldwing GL1800
New Hampshire

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: Central boiler solenoid problems
« Reply #4 on: November 22, 2015, 08:05:45 AM »

You can leave the door open or the flap and get the temp back up to get your house warm ! Then mess with it!
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

concordprof

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 43
  • OWF Brand: Central Boiler
  • OWF Model: 4030
    • View Profile
Re: Central boiler solenoid problems
« Reply #5 on: November 22, 2015, 08:11:51 AM »

Thanks for the feedback. The fuse was blown. Replaced it and it is back to working. I will be ordering a solenoid today for a backup. Any reputable online dealers recommended?  Anything I can do to prevent blowing a fuse in the future?
Logged

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: Central boiler solenoid problems
« Reply #6 on: November 22, 2015, 08:44:01 AM »

You want the fuse to blow! It's a safety to protect controller
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: Central boiler solenoid problems
« Reply #7 on: November 22, 2015, 08:46:03 AM »

Concord prof, you were the one having problems with your boiler size being to small before right? Did you upgrade the size or did you figure out your issues?
Logged

concordprof

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 43
  • OWF Brand: Central Boiler
  • OWF Model: 4030
    • View Profile
Re: Central boiler solenoid problems
« Reply #8 on: November 22, 2015, 09:53:26 AM »

Good memory Honda.

I upgraded from the 4030 to the 5036 last winter. I have also insulated all lines and used a piece of r19 on the door of the stove to insulate the pump. When both fans are blowing, my delta t is -20. I've given some thought to adding a plate exchanger but I think that would add too much of a load. I'm still waiting to see results when it gets really cold.
Logged

silver star

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 79
  • OWF Brand: Central Boiler
  • OWF Model: 6048
    • View Profile
Re: Central boiler solenoid problems
« Reply #9 on: November 22, 2015, 11:53:36 AM »

Man, i had the exact issue todat and posted about it is under the central boiler section.  Had a blown fuse.
Logged
Husbands must learn to forget their mistakes. No reason two people should remember them forever.

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: Central boiler solenoid problems
« Reply #10 on: November 22, 2015, 05:09:34 PM »

Good deal. Glad your on track.
Logged