Outdoor Wood Furnace Info

Outdoor Furnaces - Manufacturers WITH EPA-Certified Models => Central Boiler => Topic started by: MTJAG on November 14, 2017, 09:39:46 AM

Title: CB CL5036 display
Post by: MTJAG on November 14, 2017, 09:39:46 AM
I have a Central Boiler 5036 that has a dot in the display.  So, last night I loaded it up and there were coals in there before I closed the door.  The temp reading at the time was 177.  This morning I go out and the solenoid is open and drafting, but when I open the door, there was never a fire from last night.  I looked at the display and it is reading 1.12 (except the dot is at the top of the display).  I turned everything off and restarted and the dot is still in the display and the solenoid opened again.  I started a fire in it and it is currently burning with the display now showing 1.49 or 149 degrees.  Wondering if anyone else has had this problem and what is the issue with the dot in the display.
Thanks,
Title: Re: CB CL5036 display
Post by: boilerman on November 17, 2017, 06:21:06 PM
The dot in the temperature is not a problem, it is simply the way it works. You will see it illuminated in the water temperature readout any time the controller is sending power to the solenoid, that opens the damper in the door allowing air into the firebox to create a burn cycle. If your water set point is 185F it will open the damper at 175F and stay open until water temp reaches 185F and will then close until water temp drops to 175F again.