I also learned the hard way. I put in 3 wrap and ended up having groundwater getting to my pex, went through a ton of wood. Dug it up and put in Thermopex from Central Boiler, what a difference!
I have about 200 feet to run, how much did you spend?
Thermopex is good pipe from what I’ve heard, however it’s not true 1” pipe and is nominally specced at 7/8” ID, and is the same OD as the OD of 1” copper. Thats how they get away with calling it 1”.
Logstor is actually 32mm ID which is close enough to call 1” ID.
Depending on your load, with the smaller pipe you may not be able to force enough water thru it to avoid having a rather large delta T.
With my previous setup I was seeing a temperature drop of 35-40 degrees with the house calling for heat, the domestic hot water calling for heat and the snow melt on.
Installing Logstor helped some, replacing all the PEX in the basement with copper 1” pipe solved the rest.
Can have everything calling for heat now and have a Delta T of 20 now running the same pump on the OWB.