All-Purpose OWF Discussions => Plumbing => Topic started by: hoardac on April 16, 2018, 09:55:56 AM
I have a pump question, right now I am running 2 Taco 007-F5 in series to push water through my in floor heating Would like to change to a single pump. Would a single Grundfos UPS15-58FC replace those. That is what my boiler internal circulator pump is so a spare would work for either one.
I think a 15-58 maxes out at around 18' of head, a single 007 maxes at 10'. So together two 007's would have a 20' of head available compared to a single 15-58 with 18'. But you may not need that tiny bit extra and it would be fine.
How many loops of what size and length are you pushing? A B&G NRF-25 has a bit more flow with the same head and runs about the same price. It's a 3 speed also so is very versatile.
I got 10 loops 1/2 pex 300ft loops but usually only 6 on at once the others are there but not usually needed.
Checking return water temps after it's been running several days to level out would tell you if you're lacking on flow. Anything over 20F delta T would indicate dropping down to one 15-58 probably wouldn't be good.
I'd bet you'd be fine though, but I don't do radiant on an everyday basis down here in forced air land. I know there's others on here who do it all the time.
Is this in a slab? Mixed down temps?
Unless you have a very low flow rate, a single 15-58 will not flow as much as two 007 in series. Take a look at the flow curves for each pump and double the head pressure for the 007 and you can directly compare them.
If you need the same flow rate, I would probably use a 26-99 if you want to go with a single pump. Low or medium speed would probably be pretty close to the two 007 pumps.
I second the 26-99. 10 loops is too much for proper flow with a 15-58, although it will likely still work if you're determined to go that route. I have seen quite a few 10-12 loop systems fed with a 15-58, but the delta T is pretty huge- like 40-50 degrees. Anything over 8 loops I go to a 26-99 to keep the delta T tight. At 10 loops I go to speed 2, and at 13 loops speed 3. Did one last fall with an 8, 10, and 11 loop manifold on 3 zones. Each got their own 26-99, with the little guy on speed 1 and the others on speed 2. They balanced out to ~.70 GPM per loop and settled to a 24 degree delta T. I also run my loops 250ft max. In your case you'd be maxing out speed 2
Thanks for all the info I will pull the 15 off the boiler and try it see if I can get same or very similar flow rates if not then I will go to the bigger pump. Never had a problem with Delta T most it ever was 13-15 degrees and that is on the coldest windiest nights. I thought 300 feet was ok to run with a 10% overage max on 1/2 inch pex. I have never had a house is to cold issue but I spaced the pex very close and extra around perimeters.