Brass or Galvanized At Boiler
« on: September 17, 2019, 04:49:19 PM »

Just wondering what everyone's thoughts are on the type of fittings to use.
I have brass or copper fittings everywhere else but I was thinking on using galvanized 1" barbed to 1" barbed to join the Logstor to the flex pipe at the boiler. These seem be be more ready available and I was wondering if it was advisable to use them.
Dave
Logged
Polar G2
580 Case
Kubota F2100
Stihl 028
Stihl MS261

Living the dream...
Near Novar Ontario Canada

wreckit87

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 659
  • OWF Brand: Heatmaster
  • OWF Model: C375
    • View Profile
Re: Brass or Galvanized At Boiler
« Reply #1 on: September 17, 2019, 05:40:58 PM »

Do NOT use galvanized fitting in a hot water heating system. That's just asking for galvanic corrosion and a lifetime of leak chasing. Do yourself a favor and use either black malleable or brass fittings
Logged

DBeleskey

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 95
  • OWF Brand: Polar
  • OWF Model: G2
  • Novar ON
    • View Profile
Re: Brass or Galvanized At Boiler
« Reply #2 on: September 18, 2019, 07:11:04 AM »

Glad I asked...thanks for your feedback, much appreciated as always .