Author Topic: air conditioning using the same heat exchanger  (Read 8186 times)

bruey

  • Full Member
  • ***
  • Offline Offline
  • Posts: 105
    • View Profile
air conditioning using the same heat exchanger
« on: October 12, 2009, 08:06:13 PM »

was wondering if anyone has tried or heard of anyone doing this.  was thinking of runing 2 new pex lines to my pond and spooling about 1000 feet , sinking it to the bottom where it is about 55 . put a pump inside the house on intake line , shutoff valves on the wood stove pipe, and the air pipe.  summer pump the cold , winter switch and pump the hot.  somewhat worried about the condensation but i put the air handler at the bottom with a drain plug just in case.  i cant see why it wont work, but hate to spend the time and money for nothing.  any help out their?????
Logged
Newrichmond, Ohio

piper

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 10
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #1 on: October 12, 2009, 08:17:03 PM »

i don't think you would have to go to the pond, just bury the pipe in the ground around the house some where the ground temp. is around 55 , also deep enough not to freeze.  it seems you could use non insulated line's for this.
Logged
piper   kevil ky.  the western part of the state

bruey

  • Full Member
  • ***
  • Offline Offline
  • Posts: 105
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #2 on: October 12, 2009, 08:34:11 PM »

for sure on the non-insolated lines, but still am worried about the humidity, and if it will work.
Logged
Newrichmond, Ohio

Acecooper

  • Newbie
  • *
  • Offline Offline
  • Posts: 2
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #3 on: August 28, 2010, 12:43:45 AM »

Your wonderful idea will surely work! But if I were you I will just spend my time and money with someone who is really capable to do all the electrical aspects. You are bound to ruin a lot if it will fail to work properly. 
« Last Edit: September 07, 2010, 12:19:46 AM by Acecooper »
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #4 on: August 28, 2010, 10:02:26 PM »

I've often threatened to do this. 

It will work, and depending on how well your insulation is in your house is how well it work.  For example if your house is insualted fair, it might keep the ac from kicking on until it was 75 or so outside, if it was really tight it might extend those numbers up to 80-85. 

Yea the coil will sweat of course.  It will drain the same as a regular a coil will though. 

I've often threatened to run a small pump with about 60 feet of black pex across my roof line and come back to my plate exchanger for my hot water.  It does work.  we have tried that on a larger scale by placing a spool of black water line on a flat roof in the summer.  Water from that system was entering a swimming pool at 190 degrees on hot sunny days.
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

HandyMark

  • Full Member
  • ***
  • Offline Offline
  • Posts: 124
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #5 on: October 21, 2011, 12:50:27 PM »

Hey Bruey, It's been a good while since this was discussed. Did you ever try out this system? I have set my new system up for this type of cooling but it will likely be a while before I put in a ground loop.
Logged

beeman

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 251
  • OWF Brand: homemade
  • OWF Model: her name is HOT CHICK
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #6 on: November 13, 2011, 09:42:46 AM »

i hope to add the lines to try this , i have a sistern in front of my house that i would use
Logged
work like a bee  1970 mgb stihl 029

oldchenowth

  • Guest
Re: air conditioning using the same heat exchanger
« Reply #7 on: November 13, 2011, 05:07:55 PM »

If you do try this, please post some pics and details.  My wife would be happy as all get out to figure an air system from the boiler.  I was told $3000 + for air hook up to my forced air,  aint gonna happen anytime soon.
Logged

beeman

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 251
  • OWF Brand: homemade
  • OWF Model: her name is HOT CHICK
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #8 on: November 20, 2011, 08:06:52 AM »

i got some old baseboard heaters that ill modif for the coil that will go into the sistern
Logged
work like a bee  1970 mgb stihl 029

PatrickfromPA

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 13
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #9 on: December 12, 2011, 08:10:13 PM »

I actually did this. I have had a OWB for 2 years and year number one i was sitting outside phila sweating my proverbial you know what off and thought, hmmm i wonder if it would work.  So i took out my calculator and figured that using cast iron radiator off of craigs list for free. I needed for my 3900 square foot house I would need 2000 inches of 1/2" pipe for the water entering at 100 degrees F to be reduced to 58dg F ( I have a fresh water spring that moves 3 gallons per minute. it is about 18inches wide and 6 inches deep.
So I dug a little pit in the brook, then I went and got rubber in a can spray (as seen on tv). Then used swimming pool paint. (that didn't work) So then i went with roofing tar from home depot. I put it everywhere then put the spray rubber on top of that to contain anything from messing with the water quality of my spring.  So far It works. 

Since I installed my pump close to my Forced air exchanger. I use that set up but I installed inside the house several just in case ball valves in case i wanted to add some extra hot water radiator baseboard heat in my basement. So, it cuts off the water from the stove and connects to my 3/4" pex which runs to my stream for the stove. I just placed some black 3/4"inch next to it, hooked it up with the extra valve that I had installed originally and there is a shut off valve in front of the extra valves. 

OKAY got that... now here is the tricky part. IT FREAKIN WORKED. however, a small problem arose. It does not get rid of the humidity.  Living outside philadelphia/wilmington, DE area it gets sticky here.  so, i used my calculator to figure out with my size house that you need to run a 150 qt per 24 hour dehumidifier all the time. Since to buy one of those was about 3500 bucks i said no thanks. however i used 2-72 qt dehumidifiers in the house. Well, i got it to work by august 30th of this past year and bam... cold sept no real heat wave... so it worked and my humidity was around 48 percent for the house which acutally keep the house cool without running the central Air on days more than 80 but never really had bad humidity after that. So, all i know is the first test i did was that I let the OWB run at 90-95 dg F for a week and my house was 75 degrees with 82 percent humidity... That's what spurred on my next set of tests that i reveled here.  So, I hope the calculations help you guys. oh copper was better than cast iron you needed less that 2000 inches. But i was looking for a cheap test, so i went craigs list FREE way and used cast iron. So i would show a picture but thing is buried in my stream. it is 2ft tall and 9 loops stacked on top of one another x 2 radiators. So imagine 2 radiators against a wall that are connected by a small nipple then dropped "laying down" into a 3 foot hole in a stream. The water flows on average 3-4 GPM across the fins showing. Above the radiator it is 58 degrees (water temp) and 50 ft down stream the temp is 70. So it does work
Logged
OWB-wood doctor XL champion series
installed 1-16-2010
uses for my OWB-
heat house/garage- Air condition house/garage-
working on using the seebeck/thompson effect to generate electricity

Bull

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 662
  • OWF Brand: Hardy
  • OWF Model: Rebuilt H2
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #10 on: December 13, 2011, 07:21:37 AM »

Very cool, Thanks Patrick and welcome to the site.
Logged
Southern Indiana
Just outside of the "Small Town"

abarton

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 33
  • OWF Brand: taylor
  • OWF Model: 450
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #11 on: January 11, 2012, 06:05:00 PM »

For most chill water air conditioning to obtain good moisture removal a good chill water temp is about 45 degF. A 15degF drop across your coil is going to be borderline for good moisture removal (air entering-air leaving).  A 55degF coil mite work better for sensible cooling if you tried reducing your air flow to let that air really hang out longer with the coil.  It will lower the air temp as well as extracting a little bit more moisture.  Just remember to speed it back up again before turning that AC unit back on.  I have built two residential water chillers based on the same idea of if your using water why not stick with it.  First one was a flop.  Second one worked well for a while and began to freeze up,  evaporator was too small.  Building third one now and hopefully will have all the bugs worked out of this one.
Logged
"I could have saved a fortune when I built my house if only I had not installed any light switches but instead straight wired all the lights. I'm the only one that realizes they also turn off"

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: air conditioning using the same heat exchanger
« Reply #12 on: January 11, 2012, 07:58:24 PM »

I was just thinking about this a couple days ago. I am thinking a coil of pipe in the return side of the furnace would work to condense the water. It should be pretty simple to make a coil similar to what is in a dehumidifier. It should work much better without the fins as the metal surface will be a lot cooler.

Then put it in series with the existing heat exchanger.
Logged

PatrickfromPA

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 13
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #13 on: September 02, 2012, 06:55:17 PM »

UPDATE:

after more tests this summer (kind of a hot one huh?) I have concluded that the system described above works, sort of.  We were able to get the water temp. down that was going through the heat exchanger in the air ducts. We discovered using old cast iron radiators was not a good idea. the "flow" of water just doesn't cooperate with my theory. So we changed it to round coils of copper from amazon home brewing beer kit. 3800 square foot house needs 1600 inches of copper or 160 ft or so.  great results. it worked hooking up the dehumidifer that is already connected to the system with some simple rewiring to work when the fan is working. I need to create a "manifold" for a summer and winter configurations. it turns out we were trying to cool the water in the wood boiler... man i am an idiot.
Logged
OWB-wood doctor XL champion series
installed 1-16-2010
uses for my OWB-
heat house/garage- Air condition house/garage-
working on using the seebeck/thompson effect to generate electricity

HandyMark

  • Full Member
  • ***
  • Offline Offline
  • Posts: 124
    • View Profile
Re: air conditioning using the same heat exchanger
« Reply #14 on: September 02, 2012, 08:36:26 PM »

UPDATE:

after more tests this summer (kind of a hot one huh?) I have concluded that the system described above works, sort of.  We were able to get the water temp. down that was going through the heat exchanger in the air ducts. We discovered using old cast iron radiators was not a good idea. the "flow" of water just doesn't cooperate with my theory. So we changed it to round coils of copper from amazon home brewing beer kit. 3800 square foot house needs 1600 inches of copper or 160 ft or so.  great results. it worked hooking up the dehumidifer that is already connected to the system with some simple rewiring to work when the fan is working. I need to create a "manifold" for a summer and winter configurations. it turns out we were trying to cool the water in the wood boiler... man i am an idiot.
Have you put in a thermometer to see what temps you are getting before the water enters the heat exchanger? I am confident I can keep the house cool enough but I am wondering how low the temps need to be to dehumidify.
Logged