All-Purpose OWF Discussions => Electronics => Topic started by: wonderwhy? on October 31, 2019, 07:00:38 PM
-
I have my OWB installed, Everything works just as it should with the exception of the fan in my oil furnace wont come on with the second thermostat. I have read 30+ posts from all different OWB websites. Lots of info out there, I have tried many different things to get it to run the fan. Right now the only way i can turn on the fan with the second thermostat is to take the face off the thermostat and jump a wire from W to RC. I ran a jumper back up to G on first thermostat and fan only works on first thermostat. Is this because I have a delay on the fan for the oil furnace? is it waiting for heat build up? I am currently burning a Hardy H4 i picked up used, aquastat controls the furnace and i run my pump all the time to keep hot water flowing. Any help would be great. Thanks Paul :bash:
-
Does the 2nd thermostat run on batteries? If not, do you have a C wire hooked to it?
What terminals do you have the wires on. You should have the wire that used to be on the G terminal in the original thermostat connected to the W in the new thermostat.
You also need a wire added from the RH on the original thermostat(or R if no RH) to the RH in the new thermostat.
-
If RC to W works than you have power to RC. You need a jumper to RH to RC and it should work, battery or otherwise powered. But as RSI said you need C to common if t-stat is powered by 24v from furnace.
-
I have batteries, that took care of my problem. I just didn't understand. The way that i read how to hook the second thermostat up was jumper wire for both R (blue wire) and RC (red wire, 24vac) from thermostat 1 to thermostat 2. Green wire removed from thermostat one and put in W hole in thermostat 2. this was a no go for me, no fan. After taking jumper off of R and using supplied little metal jumper from R to RC i have a fan when second thermostat calls for heat. So thankful for the quick replies. I have two identical honeywell thermostats model number RTH111B1016 they do not have the option C some refer too. Hopefully this will help some poor sucker like me one day. Thanks again to those that replied over night to help me.
So this is how i understand my second thermostat now, power comes in on RC is jumped to R using supplied metal jumper that came with honeywell thermostat. When heat is called for power goes from R to W, done by thermostat automatically controlling the fan in my oil furnace that i hope doesn't burn any more oil.
-
you got it!