Bigger Pump?
« on: October 15, 2014, 03:18:54 PM »

I've had my 5000e up and running for 15 days now.  Everything is going great so far.  I recently purchased a wireless meat thermometer and due to nast weather outside I decided that I would just go into my basement and attach it as apposed to hooking it up outside at the stove.  I taped it to my water to air HX connections (supply and return).  I let it sit for a few minutes, got the reading from the thermometer and then went and checked my stove temp.  They were within 1-2 degrees which tells me that I am getting a fairly accurate reading from the thermometer. 

Anyway, the other night I was doing the dishes and I happened to look at my thermometer unit that I have sitting on my counter.  The air HX is hooked up after the plate exchanger and the supply line on the HX was reading 140's.  My stove is set on 185 with a 14 deg differential. 

I have about a 125 ft run with 1" pex, 20 plate HX to my air HX and then back to the stove.  I have a Grundfos 15-58 running on HI.  From what I hear, return temps of more than a 20 degree difference is hard on a stove.  Do I need a bigger pump or maybe a mixing valve at the stove?  Thanks!
Logged
Athens, Illinois
Dealer for HeatMaster SS
Stihl MS 290
Troy Bilt 27 ton splitter

sceptre74

  • Full Member
  • ***
  • Offline Offline
  • Posts: 192
  • OWF Brand: Portage and Main
  • OWF Model: BL 28-40
    • View Profile
Re: Bigger Pump?
« Reply #1 on: October 15, 2014, 03:42:28 PM »

I was recommended to use a 26-99 and I have 150 ft return trip to the furnace and only running through a 50 plate. Haven't got it up and running yet so I can't tell you what speed I'll be running at yet
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Bigger Pump?
« Reply #2 on: October 15, 2014, 05:12:10 PM »

That is a lot of distance for a 15-58, are your pipes nominal sizing or inside diameter?
Logged
Wood boiler sales, service and installation for the Northeastern USA.

CountryBoyJohn

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 686
  • OWF Brand: Heatmaster
  • OWF Model: MF 10,000 E
    • View Profile
Re: Bigger Pump?
« Reply #3 on: October 15, 2014, 05:28:33 PM »

How much vertical elevation change do you have? The 15-58 does seen to have a low gpm rating. The 26-96 gives you 26gpm with 30' of head loss and costs almost $300. I'm running Badger  25-10 pumps that give me 34 gpm at 30' of loss for only $110. 2 year warranty.

For $110 it would be with a try. I'm sure you could sell that grundfos if the badger out the bigger grundfos works out. Your dealer may even buy it back.
Logged
2013 F250 6.2L Lariat
Stihl MS290
DHT 27 Ton Log Splitter
Woodchuck Log Jack
56, 57, 58 Ferguson TO-35
Knox County, IN

AirForcePOL

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 864
  • OWF Brand: HeatMaster
  • OWF Model: G400
    • View Profile
Re: Bigger Pump?
« Reply #4 on: October 15, 2014, 08:42:09 PM »

It's just standard 1" pex. I used rehau insulated pex.  My line goes into the house then drops down about 6 ft then back up 6 ft and back to the boiler.  Are most pumps the same length?  As in, if I used a badger pump, would I need to add or remove pipe at my stove to make it work?  $300 seems like a lot for a pump to me.  I think I paid $72 for the 15-58.  I have another one that I am going to use for the garage.  I could keep the other one as a back up. 
Logged
Athens, Illinois
Dealer for HeatMaster SS
Stihl MS 290
Troy Bilt 27 ton splitter

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Bigger Pump?
« Reply #5 on: October 15, 2014, 09:44:28 PM »

It's just standard 1" pex. I used rehau insulated pex.  My line goes into the house then drops down about 6 ft then back up 6 ft and back to the boiler.  Are most pumps the same length?  As in, if I used a badger pump, would I need to add or remove pipe at my stove to make it work?  $300 seems like a lot for a pump to me.  I think I paid $72 for the 15-58.  I have another one that I am going to use for the garage.  I could keep the other one as a back up.

On my short runs in the shop I went with $80 dollar pumps but 1 1/4" line, with 1" line I'd be looking at around lets say a $300 pump. I did buy two Grundfos 26-99FC's though, one for the shop boiler to the FPHX and one from the wood boiler to the FPHX. Around $240 bucks a piece at Supplyhouse.

Seems to be a big jump from a mid head 5-8 GPM pump and a higher head, high GPM pump.

Thats what it sounds like though if your delta T is that high, need more GPM if you want to keep it around the 20-25 degree range.

I think for the most part pumps will interchange with one another until you start to get into the ones that look like a pump attached to a separate motor.
« Last Edit: October 15, 2014, 09:52:13 PM by mlappin »
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

Big Wood

  • Full Member
  • ***
  • Offline Offline
  • Posts: 182
  • OWF Brand: Central Boiler Heatsource 1
  • OWF Model: E-2300 Model 2000
    • View Profile
Re: Bigger Pump?
« Reply #6 on: October 16, 2014, 03:13:07 AM »

Try bring up the differential up even though it is 14 degrees check the boiler temp after it fires at 171 and see how much lower it goes before it starts climbing up in temp just something else to check
Logged
Outdoor wood boiler repair and help

CountryBoyJohn

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 686
  • OWF Brand: Heatmaster
  • OWF Model: MF 10,000 E
    • View Profile
Re: Bigger Pump?
« Reply #7 on: October 16, 2014, 05:24:52 AM »

My understanding is that the Badger pumps are just the generic version of the Grundfos.  They may even come out of the same factory.  So, I'd say they are very similar in dimensions.  I will add that I had one of my 2 Badgers go out last winter after only a few months of usage.  They sent me a new one right away and it was relatively painless.  I'm going to order a backup pump to keep on the shelf.  I can buy a new Badger 3 times before equaling the cost of an equivalent Grundfos. 

http://www.badgerinsulatedpipe.com/Circulating-Pumps_c14.htm

Logged
2013 F250 6.2L Lariat
Stihl MS290
DHT 27 Ton Log Splitter
Woodchuck Log Jack
56, 57, 58 Ferguson TO-35
Knox County, IN

AirForcePOL

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 864
  • OWF Brand: HeatMaster
  • OWF Model: G400
    • View Profile
Re: Bigger Pump?
« Reply #8 on: October 16, 2014, 08:06:49 AM »

Try bring up the differential up even though it is 14 degrees check the boiler temp after it fires at 171 and see how much lower it goes before it starts climbing up in temp just something else to check

I have noticed the stove go down to around 168 when it first starts to cycle.  Will moving more water increase my efficiency at all?  I think I remeber reading a thread on here and it was a sensitive subject for some....

I think I'm going to order one of those badgers Countryboy, thanks.  I wanted to buy at least one extra pump to have on hand just in case, anyway.  My 15-58 should work on my garage.  10 ft elevation and only about a 60-70 ft run (one way).  I only have a water to air HX in there.
Logged
Athens, Illinois
Dealer for HeatMaster SS
Stihl MS 290
Troy Bilt 27 ton splitter

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Bigger Pump?
« Reply #9 on: October 16, 2014, 09:22:14 AM »

That short term drop you are seeing is probably just all the water between OWB and FPHX, happens to me all the time; cause I only system the pump on when there is a call for heat in the house.  In less than 5 minutes, the lines (50' run each way of 1" PEX) are up to temperature and I can begin pulling heat off of stove.

How about this for a setup (MINE  ;)):
Water comes off of OWB (pumped by SS Alpha, set to AutoAdapt and happily pumps at 3 GPM), thru thermostatic bypass (sends water back to OWB if below 140) then to 60 plate FPHX
*On other side of FPHE, mechanical mixing valve (with outdoor reset, max temp into slab is 110f), thru a different Cast Iron Alpha (in AutoAdapt) and out to 2-zone (6 & 8 loops, heating 4000sf)

**ONLY COMPLAINT, was from wife the week it was -40f and the house kept losing a degree a day (til it was about 65, in the house) at which point kicked pump up to HIGH between FPHX and slab and everyone was happy again, after a few hours