side arm exchanger sucks heat out of water heater in the summer
« on: December 25, 2014, 03:55:20 PM »

When I was getting the OWB with side arm on the water heater up and running this fall (fresh install) I was circulating the water through it before a fire was going, to check for leeks, during this time the water heater was still being heated with propane. I noticed that within probably 5 mintues of turning on the OWB circulating pump the propane would turn on for the water heater. It was probably working the opposite way as its designed, it sucked the heat out of water in the water heater. The dealer for the OWB said to let the circulating pump run all summer long, there won't be a fire going in the summer, so if i do this it will suck all the heat out of the water heater. Should a bypass loop before the side arm with valves be installed so it won't circulate through the side arm, or will shut offs on the domestic side of the side arm stop the thermo siphon action? I'd guess the second way there would still be heat loss through the steel of the valves though.

I know summer is a long way off, but I believe the water heater sprung a leek, if i was going to add shut off valves now would be the time to do it.
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #1 on: December 25, 2014, 04:21:25 PM »

Definately use the ball valves
Logged
Wood boiler sales, service and installation for the Northeastern USA.

CornFarmer416

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 21
  • OWF Brand: Portage and maine
  • OWF Model: BL 3444
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #2 on: December 25, 2014, 06:34:42 PM »

I didn't relize we have to run the water pumps year round? I just figured you shut them off after winter and just let them circulate one day in the month?
Logged
Stihl 461
Homemade Skid Steer Log Splitter turned upside down
Ohio
If it aint Red, keep it in the Shed

juddspaintballs

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 640
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #3 on: December 25, 2014, 07:52:54 PM »

First of all, every zone or circuit should be on brass ball valves so you can isolate it for repairs or shut it down if you don't want to use it.  Keep the water heater isolated out all summer regardless of whether you're running the circulator so it doesn't thermosiphon backwards. 

Secondly, I only ran the circulator for my system about once a month during the summer and never had any issues. 
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #4 on: December 26, 2014, 02:53:11 AM »

Agreed, and in the past I have always shut my circs off in the warmer months, however after cutting open the tank on the 9 year old Wood Doctor that I am repairing and seeing the settled sludge and corrosion in the bottom of the tank, I think I will now let my Wood boiler loop circulate constantly all year.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

ijon

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 263
  • OWF Brand: Portage and main
  • OWF Model: 28-40
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #5 on: December 26, 2014, 05:21:43 AM »

Would that  make condensation ?
Logged
installed in 2014

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #6 on: December 26, 2014, 05:31:26 AM »

I have gate valves in the bottom and top of my sidearm, come spring when I let the boiler go out and I turn the water heater back on those valves get shut.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

yotehunter66

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 271
  • OWF Brand: Woodmaster
  • OWF Model: 4400
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #7 on: December 26, 2014, 06:14:09 AM »

Agreed, and in the past I have always shut my circs off in the warmer months, however after cutting open the tank on the 9 year old Wood Doctor that I am repairing and seeing the settled sludge and corrosion in the bottom of the tank, I think I will now let my Wood boiler loop circulate constantly all year.
I completely drain and flush my system every year. I would think that would keep the build up down and fresh boiler treatment in the system.
Logged
Husky 372xp 24"
Makita DCS520i 20"
Poulan 2300 18"
Macullough Eager Beaver 2.3 18"
Troybilt 27 ton log splitter

aries9245

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1091
  • OWF Brand: Central Boiler
  • OWF Model: Cl6048
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #8 on: December 26, 2014, 06:27:36 AM »

So just by continuously circulating the pump it will not sludge up? Is it because the water moves and doesn't give it a chance to settle or does it just build up inside the tank by not moving .. I would think being an open system that Oxegen is the key killer regardless..
Logged
Joe
Dodge 5500 dump
Ford f450 dump
Cat 303cr excavator
Cat 246 skid steer
Kubota l4610 tractor
2 sthil farm boss saws
Homemade 4way splitter w/log lift ( the terminator)

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #9 on: December 26, 2014, 06:37:23 AM »

Well the moving water certainly would keep the crap in suspension better and that particular boiler has about 1/3 of the bottom as dead space that water does not circulate in at the moment but when I put it back together it will as I will be putting a return port at the lowest point.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

aries9245

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1091
  • OWF Brand: Central Boiler
  • OWF Model: Cl6048
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #10 on: December 26, 2014, 11:52:33 AM »

Ok Slim what do you feel is the cause of most sludge is impurities in the water breaking down when heating or the steel realesing impurities as part of its breaking down be the cause ?
Logged
Joe
Dodge 5500 dump
Ford f450 dump
Cat 303cr excavator
Cat 246 skid steer
Kubota l4610 tractor
2 sthil farm boss saws
Homemade 4way splitter w/log lift ( the terminator)

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #11 on: December 26, 2014, 01:11:08 PM »

Ok Slim what do you feel is the cause of most sludge is impurities in the water breaking down when heating or the steel realesing impurities as part of its breaking down be the cause ?

Even "soft" water still has crud in it, just let a faucet drip here and you'll still have rust stains even though the "Culligan" man has been out to test our water and said they can't get it any softer than the 3rd party softener we have is.

Can also be dust, mill scale, oil, etc on the steel when the boiler is built. Add in any residue from your fittings, pump, HX, lines, etc and you end up with crud in your water.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

juddspaintballs

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 640
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #12 on: December 26, 2014, 02:25:38 PM »

What about a coolant filter like on big trucks?
Logged

Jwood

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1065
  • OWF Brand: P&M Ultimizer
  • OWF Model: Bl 28-40
    • View Profile
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #13 on: December 26, 2014, 02:29:34 PM »

Now for us Bl owners that have piped our returns to the top as suggested by this site I now feel that may have been the wrong move and should have the return on the bottom?
Logged
North Central Minnesota
Stihl MS 270c
Stihl MS 461
Blacked out Fiskars X27
06' Silverado 2500HD Duramax

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: side arm exchanger sucks heat out of water heater in the summer
« Reply #14 on: December 27, 2014, 03:34:58 AM »

I'm not sure why you would think that Jwood?  As long as the water is moving, it should keep any sediment in the boiler suspended and allow a filter to remove it regardless of which direction it is moving, this particular unit that I am working on had no ports on the bottom 1/3 of the unit so all the debris settled to the bottom of the tank, your boiler is a dry base boiler, it has ports at the top as well as the very bottom of the tank.
Logged
Wood boiler sales, service and installation for the Northeastern USA.