Author Topic: Return Temps  (Read 4213 times)

GCTerpfan

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 83
  • OWF Brand: Central Boiler
  • OWF Model: Classic
    • View Profile
Return Temps
« on: October 30, 2014, 07:29:45 PM »

I installed my first OWB about two months ago and have been heating my DHW with it since.  Just last weekend I hooked up temp gauges on my supply and return lines at my furnace.  I have a 370' loop of 1 1/4" pex  and with no load I was seeing a consistent 4 degree temp difference between supply and return.  Tonight I turned on all three zones in my house just to check my return temps, and it was 129.  I understand it should not get below 150, so do I need a bigger pump?  I currently have a Taco 009.
Logged
Garrett County, MD

cando attitude

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 72
  • OWF Brand: Portage & Main
  • OWF Model: BL 28-40
    • View Profile
Re: Return Temps
« Reply #1 on: October 30, 2014, 07:39:48 PM »

Terpfan, it certainly sounds like you need a bigger pump.  370' loop is not a small loop by any means and when you mention that you have 3 independent zones, it brings to mind valves, T's and 90's, all of which create pressure drop and thus a drop in flowrate.  There are two items that you did not mention that are important here and that's supply temp and whether or not you have much of a load on your system right now.
Logged
Producing a little smoke, here in  South Central Ohio....
Echo CS 400
Jonsered 2255
Case 35B
Dirty hands splitter
2013 3500 Duramax

victor6deep

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 393
  • OWF Brand: Burnrite
  • OWF Model: 228
    • View Profile
Re: Return Temps
« Reply #2 on: October 30, 2014, 08:20:35 PM »

I don't buy into the return temp theory. I'm waiting for mine to spring a leak but I know too many that run less than 180 and have had zero issues.
Logged

GCTerpfan

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 83
  • OWF Brand: Central Boiler
  • OWF Model: Classic
    • View Profile
Re: Return Temps
« Reply #3 on: October 31, 2014, 07:04:52 AM »

Okay, here is some more info on my system.  My supply temp is 180. The 370' of 1 1/4" pex runs through two 5x12 plate heat exchangers, a 50 plate that heats my indoor boiler and a 30 plate that heats my DHW.  I ran through the Taco worksheet and calculated my head loss at 8.9' (not including the heat exchangers because I don't know how to account for them). 

When I tried this experiment it was fairly warm out, the house was at about 68 deg. which is where we keep it.  I simply turned all three thermostats up to about 75, so that they would call for heat and walked out to the boiler.  The return temp dropped quickly and seemed to hold at about 127 to 129.  There was no call for heat from DHW at this time.  Does that seem right?  The return temp was a lot lower than I expected. 
Logged
Garrett County, MD

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Return Temps
« Reply #4 on: October 31, 2014, 07:49:54 AM »

Yes 370' is quite a loop, and 4 degrees with no load is pretty respectable.  Most boilers are recommended to NOT have regular return temps below 140f, as it reduces the possibility of creosote/rust forming. However, if you have a temperary drop of return temps below 140f you should be OK, since I only turn my pump on between OWB and FPHE when there is a call for heat (I get short 5-10 minute windows where return temps to boiler are below 140)

Question, you do have a CB so do you have the thermostatic bypass installed?  Because if the supply temps from boiler drop low enough (the by-pass) will simply divert water back to boiler to be heated up to temp, before sending it out to radiant application. 

**Good luck, if you do decide to go with a bigger pump (based on a quick check of a pump curve chart from TACO) it looks like a 0011 would be the next step up, from a 009.  Just be careful you are not OVER-PUMPING the system, which causes noise and eventually erosion of metal fittings

EDIT: Added word NOT & below
« Last Edit: October 31, 2014, 12:15:51 PM by LittleJohn »
Logged

GCTerpfan

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 83
  • OWF Brand: Central Boiler
  • OWF Model: Classic
    • View Profile
Re: Return Temps
« Reply #5 on: October 31, 2014, 08:21:01 AM »

Yes, I have a CB classic and no I do not have a thermostatic bypass installed. I wasn't aware of them until after I installed my system.  I inherited the boiler, so I did the install myself.  There are lots of things I would have done differently if I was to do it again.

How does a thermostatic bypass actually work?  If it diverts hot water from the supply to the return, wouldn't that just reduce the flow to your heating system, thereby compounding the problem?
Logged
Garrett County, MD

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Return Temps
« Reply #6 on: October 31, 2014, 09:26:25 AM »

The Thermostatic by-pass works in 3 stages;  (all water temps stated are coming off the HOT side of the boiler)
 1: Water temps below 140f get returned to be reheated
 2: Water temps between 140-165ish, a portion of the water is returned to OWB and some is let out into Radiant application
 3: Water temps above 165sh, valve is FULL open and all water from OWB is going to radiant application

Basically if water temps coming off the OWB drops to low, it diverts flow from heating loops back to OWB, so it has a chance to catch up.  The thermostatic bypass does NOT take into account the return temperatures being too low, it only tries to keep the supply temperatures above 140F
Logged

GCTerpfan

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 83
  • OWF Brand: Central Boiler
  • OWF Model: Classic
    • View Profile
Re: Return Temps
« Reply #7 on: October 31, 2014, 10:47:32 AM »

Got it. That makes sense.

Any other opinions on whether I should be concerned with the return temps I saw?  I just don't want to find out there is a problem the first week the temps hit 20 degrees and have to deal with it then.
Logged
Garrett County, MD

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Return Temps
« Reply #8 on: October 31, 2014, 12:17:05 PM »

Sorry reread an earlier post and made corrections...  :bag: :bag:

...typical return temps shoudl be above 140f, with temporary dips below 140
Logged

oaky

  • Full Member
  • ***
  • Offline Offline
  • Posts: 217
  • OWF Brand: Portage & Main
  • OWF Model: BL-2840
    • View Profile
Re: Return Temps
« Reply #9 on: November 01, 2014, 06:46:10 AM »

Sorry reread an earlier post and made corrections...  :bag: :bag:

...typical return temps shoudl be above 140f, with temporary dips below 140

What's the maximum length of time would be acceptable for a temporary dip below 140? Boiler temp set @175 on/180 off. Thanks
« Last Edit: November 01, 2014, 06:49:58 AM by oaky »
Logged
Husqvarna 272
Husqvarna 55
27 Ton Cub Cadet Log Splitter
John Deere 826D Walk-Behind Snowblower
Always A Good Pile Of Oak Firewood
Home is: West Central Wisconsin

BoilerHouse

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 368
  • OWF Brand: Home Built
  • OWF Model: Fire Tube/Water Tube
    • View Profile
Re: Return Temps
« Reply #10 on: November 01, 2014, 08:04:58 AM »

To GCT

I don't know if low return temps will hurt your boiler.  It hasn't for me.  This is now year 6 and my system has spent a good part of it's life running at lower than recommended temps.  Anyways...to me, your 50 degree temp difference sounds awfully high.  I question the 9 foot head estimate.  Does that take into account elevation, pipe length and every possible flow obstruction?   What I do to confirm flows is pull the return line off at the boiler and measure with a pail and a stop watch.  Crude but effective and it eliminates guess work.
Logged
Muskoka, Ont

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Return Temps
« Reply #11 on: November 03, 2014, 06:58:55 AM »

Oaky, I can not say a definately what kind of time frames are acceptable or not; but it is generally accepted that return temperature should be above 140f.  As temps below that are more likely to create condesation on interior of reaction chamber, create creosote, which leads to rust, which leads to LEAKS. 

**I am not saying, that you can't run with return temps below 140F, but IMO I woudl try to chance some stuff so my return temperatures where a bit higher.
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Return Temps
« Reply #12 on: November 03, 2014, 07:01:03 AM »

I would agree with you as well LittleJohn
Logged
Wood boiler sales, service and installation for the Northeastern USA.

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: Return Temps
« Reply #13 on: November 03, 2014, 07:13:45 AM »

I would agree with you as well LittleJohn
Hey Slim want to tell that to my WIFE, that I am somewhat knowledgable  ;D
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Return Temps
« Reply #14 on: November 03, 2014, 07:21:11 AM »

 If she's anything like mine, she won't listen anyway!
Logged