Author Topic: hydraulic seperator  (Read 4621 times)

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
hydraulic seperator
« on: January 05, 2013, 07:06:47 AM »

I am planning to install gasification OWB and plumb to my wall hung boiler for radiant heat and DHW.  I want to have it so I can still the run the wall hung boiler in the summer for DHW.  Is a hydraulic seperator the best way to go?
Logged
Gilford NH

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: hydraulic seperator
« Reply #1 on: January 05, 2013, 07:53:16 AM »

Are you talking about a plate exchanger?  Often times when hooking to exsisting boilers we'll install anywhere from a 50-100 plate heat exchanger depending on heat load and such
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: hydraulic seperator
« Reply #2 on: January 05, 2013, 02:01:45 PM »

Do you just put the plate heat exhanger on the supply side of the loop off the boiler?
Logged
Gilford NH

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: hydraulic seperator
« Reply #3 on: January 06, 2013, 07:49:59 AM »

intheoaks would you mind taking a picture of your hx and piping setup and post.  That would be very helpful for me.  Thanks
Logged
Gilford NH

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: hydraulic seperator
« Reply #4 on: January 06, 2013, 08:47:55 AM »

How do you get the air out of the plate exchanger with it mounted upside down?
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: hydraulic seperator
« Reply #5 on: January 06, 2013, 09:19:25 AM »

I saw that, there not supposed to be mounted upside down, but he may have got lucky and had its bleed out. 
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: hydraulic seperator
« Reply #6 on: January 06, 2013, 11:38:35 AM »

Bleeders higher arent going to get the air out of the plate.

I wouldnt be surprised if there is only water in half of the plates.
Logged

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: hydraulic seperator
« Reply #7 on: January 06, 2013, 11:53:22 AM »

The pump will push some of it out but once it is full to the point where the water is not obstructed by the air it wont push anymore out.
Logged

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: hydraulic seperator
« Reply #8 on: January 06, 2013, 12:06:03 PM »

The pump will push some of it out but once it is full to the point where the water is not obstructed by the air it wont push anymore out.

I bet your right, I made that mistake once.  It worked but water wasn't as hot as i thought it should be, remounted it and worked fine
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: hydraulic seperator
« Reply #9 on: January 06, 2013, 12:38:03 PM »

Thanks for the pictures.  It is always nice to see how other people do things.

What size HZ is that?  Do you size them according to the size of the boiler that is currently heating the load?  My boiler in my basement that I heat the house with is 115,000 BTU and the wall hung in my barn is 165,000 BTU.

I was thiking about using 1" for the house and 1 1/4" for the barn.  Does that seem right?

Thanks in advance for all the great information.
Logged
Gilford NH

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: hydraulic seperator
« Reply #10 on: January 06, 2013, 01:34:47 PM »

Depends on how far your going and such.  Pex al pex is an option as well, it's 1.04 vs pex 1" which is .875.  When tying to exsisting boilers I think keeping the flow up is very important, and big plate heat exchangers are needed.  Even if your exsisting boiler is just 115,000 btu, You should want a playe exchanger capable of much more than that, probably at least a 50 plate

Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: hydraulic seperator
« Reply #11 on: January 06, 2013, 01:53:16 PM »

The OWB is going to be around 100 feet from where it enters the barn.  Then to get through the barn and into the house is another 100 feet.

Also with a system like this I am assuming I would just run the pumps on the OWB 24/7.
Logged
Gilford NH

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: hydraulic seperator
« Reply #12 on: January 06, 2013, 02:04:51 PM »

The OWB is going to be around 100 feet from where it enters the barn.  Then to get through the barn and into the house is another 100 feet.

Also with a system like this I am assuming I would just run the pumps on the OWB 24/7.

Yes the pumps would run 24/7... 

You would have to run 2 line sets, one for your barm and one for your home.  You couldn't heat that much space in series. 

The barn would pull off heat, then the home, and it would likely have your return water temps far to low to protect your boiler. That's why central boiler and empyre have boiler protection systems, is to eliminate water returning to cold and making the stove sweat inside
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

Belknap

  • Full Member
  • ***
  • Offline Offline
  • Posts: 107
    • View Profile
Re: hydraulic seperator
« Reply #13 on: January 06, 2013, 02:53:30 PM »

Yes.  I was going to run 2 lines one for house and one for barn.  I was just wondering on if I should go 1" for house and 1 1/4" for barn.
Logged
Gilford NH

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: hydraulic seperator
« Reply #14 on: January 06, 2013, 03:04:32 PM »

You have to use the proper pump and line combinations, so there isn't one right answer. 

If you use 1 1/4" you could get by with a smaller pump, with 1" it might work for both, but of course your pump would have to be sized larger to make up with the restriction in flow. 

If I went with 1" pex to the house, I'd def go with pex al pex for the increased flow.

Funny this all came about today, had a customer call today who I had worked with before on a very similar distance/application as you.  His dealer sold him regular 1" and his flow is so low it's 40-50 degree difference in supply/return temps.  He will either have to get a substantially larger pump or use 2 pumps in series because his line is simply to small for the application. 
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697