5036 Hot water Plate exchanger
« on: December 12, 2013, 04:29:51 AM »

I know Ive mentioned this before in another post somewhere but my hot water return line to the boiler was cool this morning Ive checked inline strainer and found no pluggeg there, I had to shut off the water going to my heat exchager to force as much as I could the the plate exchager this worked i guess Im going to try to reverse the line's going to the plate exchager and see if this helps. :'(
Logged
I use a Stihl MS361 saw & MS250 & MS170
New Holland TC30 tractor
powerdiver6000@aol.com

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: 5036 Hot water Plate exchanger
« Reply #1 on: December 12, 2013, 07:07:37 AM »

Maybe plugged up and only letting a small amount of gpm through causing all of the heat to have been extracted from the water by the time it makes it out the other side?
Logged

pwdiver

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Central Boiler since 2009
  • OWF Model: CL5036
  • No matter where you go there you are
    • View Profile
    • narronseggstra's
Re: 5036 Hot water Plate exchanger
« Reply #2 on: February 05, 2014, 02:10:11 PM »

What calculation would you use to size a new hot water plate exchanger mine is fouled and I think Im going to get another so I can just change the current one out and get it soaking in white vinegar per my dealer my current exchanger is 5inx13in 1in thick with 1in water in and water out, I dont know if going to a 20 plate or 30 plate is better. :-\
Logged
I use a Stihl MS361 saw & MS250 & MS170
New Holland TC30 tractor
powerdiver6000@aol.com

fireboss

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 491
  • OWF Brand: central boiler
  • OWF Model: 6048
    • View Profile
Re: 5036 Hot water Plate exchanger
« Reply #3 on: February 05, 2014, 11:02:41 PM »

I say 30 plate,  bigger the better, I have a 40 plate and wish I had a 60 
Logged
Sussex county new jersey                                                                   cb 6048 instald may 2010, heating 3000 sq and 15,000 gal pool,sure track dump trailer,35ton splitter,029,ms200,homlite xl

CountryBoyJohn

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 686
  • OWF Brand: Heatmaster
  • OWF Model: MF 10,000 E
    • View Profile
Re: 5036 Hot water Plate exchanger
« Reply #4 on: February 06, 2014, 05:20:10 AM »

A 20 plate is definitely all that's needed for hot water.  When you get into plate exchangers for your boilers and pressurized heating systems, that's when you get into 50 or 60 plate exchangers.  A 20 plate is all that's needed for domestic water.
Logged
2013 F250 6.2L Lariat
Stihl MS290
DHT 27 Ton Log Splitter
Woodchuck Log Jack
56, 57, 58 Ferguson TO-35
Knox County, IN

pwdiver

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Central Boiler since 2009
  • OWF Model: CL5036
  • No matter where you go there you are
    • View Profile
    • narronseggstra's
Re: 5036 Hot water Plate exchanger
« Reply #5 on: February 06, 2014, 05:45:15 AM »

Thanks for the info i will be getting a spare plate exchanger soon :thumbup:
Logged
I use a Stihl MS361 saw & MS250 & MS170
New Holland TC30 tractor
powerdiver6000@aol.com

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: 5036 Hot water Plate exchanger
« Reply #6 on: February 06, 2014, 10:40:11 AM »

It sounds like you have a 10 plate now. 20 is the minimum that should be used in series in a primary loop.
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 5036 Hot water Plate exchanger
« Reply #7 on: February 06, 2014, 06:22:18 PM »

It sounds like you have a 10 plate now. 20 is the minimum that should be used in series in a primary loop.

Would a thirty offer more flow with the same fitting sizes as a 20 plate?
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

CountryBoyJohn

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 686
  • OWF Brand: Heatmaster
  • OWF Model: MF 10,000 E
    • View Profile
Re: 5036 Hot water Plate exchanger
« Reply #8 on: February 06, 2014, 06:34:56 PM »

Yes, but it isn't necessary. I believe the 20 plate is enough not to cause restrictions. More plates are a waste of BTUs. You'll get your water temp much higher than is necessary and just cool it back down with a mixing valve. A 20 plate gets my temp up to 130 or so. That's all you need.
Logged
2013 F250 6.2L Lariat
Stihl MS290
DHT 27 Ton Log Splitter
Woodchuck Log Jack
56, 57, 58 Ferguson TO-35
Knox County, IN

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 5036 Hot water Plate exchanger
« Reply #9 on: February 06, 2014, 06:50:49 PM »

Yes, but it isn't necessary. I believe the 20 plate is enough not to cause restrictions. More plates are a waste of BTUs. You'll get your water temp much higher than is necessary and just cool it back down with a mixing valve. A 20 plate gets my temp up to 130 or so. That's all you need.

Good to know, but I was referring more to restricting flow from the OWB. Or if it came with say 1 1/4 fittings for the OWB, it will flow as much as 1 1/4 pipe regardless of the number of plates?
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

CountryBoyJohn

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 686
  • OWF Brand: Heatmaster
  • OWF Model: MF 10,000 E
    • View Profile
Re: 5036 Hot water Plate exchanger
« Reply #10 on: February 06, 2014, 06:54:38 PM »

I'm not positive, but I think the plates are the restriction. I believe a 20 plate with 1" fittings well have the same restriction as a 20 plate with 1-1/4" fittings.

Is that what you mean?
Logged
2013 F250 6.2L Lariat
Stihl MS290
DHT 27 Ton Log Splitter
Woodchuck Log Jack
56, 57, 58 Ferguson TO-35
Knox County, IN

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: 5036 Hot water Plate exchanger
« Reply #11 on: February 06, 2014, 07:02:05 PM »

I'm not positive, but I think the plates are the restriction. I believe a 20 plate with 1" fittings well have the same restriction as a 20 plate with 1-1/4" fittings.

Is that what you mean?

yup.

I was just wondering what the minimum number of plates that could be used with 1 1/4" pex or 1" pex-al-pex and not add considerably to the total head in the system on the boiler side.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

pwdiver

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Central Boiler since 2009
  • OWF Model: CL5036
  • No matter where you go there you are
    • View Profile
    • narronseggstra's
Re: 5036 Hot water Plate exchanger
« Reply #12 on: February 07, 2014, 05:28:03 AM »

I measured mine the other day its 5x13x1in thick I thought it had 1in fittings but its 3/4 fitting's I remembered after seeing the red Pex that I had to reduce it to make it fit. My main run from and back to the boiler is 1in as this is what size my main heating coil take's, I cant complain but so much Ive been running boiler constant since Feb of 2009 because I heat my hot water in the summer months also. :thumbup:
Logged
I use a Stihl MS361 saw & MS250 & MS170
New Holland TC30 tractor
powerdiver6000@aol.com

pwdiver

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Central Boiler since 2009
  • OWF Model: CL5036
  • No matter where you go there you are
    • View Profile
    • narronseggstra's
Re: 5036 Hot water Plate exchanger
« Reply #13 on: February 09, 2014, 06:47:30 AM »

I have found several Plate exchangers on ebay a 20 plate for 130.00 or a 30 plate for 150.00 :thumbup:
Logged
I use a Stihl MS361 saw & MS250 & MS170
New Holland TC30 tractor
powerdiver6000@aol.com

pwdiver

  • Full Member
  • ***
  • Offline Offline
  • Posts: 117
  • OWF Brand: Central Boiler since 2009
  • OWF Model: CL5036
  • No matter where you go there you are
    • View Profile
    • narronseggstra's
Re: 5036 Hot water Plate exchanger
« Reply #14 on: February 22, 2014, 06:58:27 AM »

Im getting ready to install my 30 plate exchanger do you think i would give up much heating value to leave the 3/4 in lines I currently have or up it to 1in I currently have it reduced to 3/4 because that is what size the current fittings are on the old exchanger :-[
Logged
I use a Stihl MS361 saw & MS250 & MS170
New Holland TC30 tractor
powerdiver6000@aol.com