Author Topic: Major temp loss with new install  (Read 5360 times)

Wi woodburner

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 16
  • OWF Brand: Woodmaster
  • OWF Model: 5500
    • View Profile
Major temp loss with new install
« on: March 09, 2014, 02:51:34 PM »

I am very new to heating with my new woodmaster 5500.  I have the owb 150 feet from the house.  I have the insulated pex running on top of the snow for now as I installed in January.  I have about 75 foot run once inside to my forced air furnace.  Installed at the furnace is a Ranco temperature controll.  The temp probe is installed on the supply line going into the 18 x 20 hx.  The temp reading at the ranco is at 120 degrees when the stove is 160.  The supply line is warm but not hot to the touch.  I am using the supply line to heat my hot water as well. 
The air blowing out of my ducts have never been warm.  The house does heat up but takes a while to raise the temp 1 degree.  I increased the blower speed but that just let more cool/warm blow through ducts.  I am very green when it comes to any of this and would appreciate all the help.  from what I have read, could I have a pump issue?
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: Major temp loss with new install
« Reply #1 on: March 09, 2014, 04:36:32 PM »

There are many things to check, pump size, restriction in loop, to small piping, poorly insulated lines, air in the loop, all these are problems, your water losing 40 degrees is crazy!
Logged
Wood boiler sales, service and installation for the Northeastern USA.

NaturallyAspirated

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 443
  • OWF Brand: Central Boiler
  • OWF Model: M250
  • Golfing, snowmobiling fool!
    • View Profile
    • http://www.nealmastel.com
Re: Major temp loss with new install
« Reply #2 on: March 09, 2014, 04:40:27 PM »

What model of pump do you have?

Neal
Logged
Miss Farad was pretty and sensual, and charged to a reckless potential; but a rascal named Ohm conducted her home - Her decline was, alas, exponential
Send me your bitcoins!  1GEsGKzP5xK9e45YDjmRzGYpnhwT3oNbvj

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: Major temp loss with new install
« Reply #3 on: March 09, 2014, 04:51:50 PM »

Yeap, major issue somewhere. You should have the same temp outside as you do inside or within a degree or two. First off most of us run our stoves at 180 +. This ensures that return water back to the boiler is not below 150 which can cause condensation to form in the fire box and early failure of your owb. Next we need to make sure that the water leaving your owb is actually 160. Do you have a IR thermometer you can use to get an idea of the line temp? I believe the Ranco in the house is reading true if you do not have warm air coming from the vents. My water goes into my HX at 180 and comes out of my vents at 135-150. Snow melt ontop of your insulated pex lines? Won't be a pump issue if between your boiler and your supply side of the hx are a 40 degree difference.
Logged

willieG

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1852
  • owbinfo.com
    • View Profile
Re: Major temp loss with new install
« Reply #4 on: March 09, 2014, 05:16:02 PM »

if your aquastat at the stove is right and you have 160 at the stove and you have only 120 where it enters into the house...you have one of 2 problems...pump is too small or junk....or ...you have air in the system and the pump is not moving enough water.

if you were only moving 5gpm and the water was leaving the stove at 160...in a 75 foot run in unisulated pipe i doubt if you would lose more than 10 or 12 degrees

to be leaving the stove at 160 and losing 40 degrees in that 75 foot run....there is barely any water .

when my water lines were comprimised  years ago..i was moving about 7 gpm and my underground lines were 250 feet  from stove to house, i had a 3 foot wide melted (no snow or frost) for the whole 250 feet and i was still getting enough hot water to heat the house and my hot water...i can only assume you are not (for what ever reason...bad pump..wrong pump...or air lock) moving enough water
Logged
home made OWB (2012)
Ontario Canada

Wi woodburner

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 16
  • OWF Brand: Woodmaster
  • OWF Model: 5500
    • View Profile
Re: Major temp loss with new install
« Reply #5 on: March 09, 2014, 06:41:46 PM »

Just checked again and owb is 170 and inside temp before hx is 150.  No demand for heat in the house.  The pump is a taco 011 with 1.00 lines in the house. I am going to check the temp tomorrow at various spots on the run...where it enters the house, leaves the owb, enters hx at dhw and where it leaves the hx at the furnace. 
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Major temp loss with new install
« Reply #6 on: March 09, 2014, 06:45:08 PM »

What brand of insulated pipe?

Sounds like a air lock.

May sound a little silly, but check the obvious like that the pump is installed in the right direction.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

Wi woodburner

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 16
  • OWF Brand: Woodmaster
  • OWF Model: 5500
    • View Profile
Re: Major temp loss with new install
« Reply #7 on: March 09, 2014, 06:53:09 PM »

Outdoor lines are thermoplex at 10.00/ft.  The supply line does run through the dhw first.  Could this be taking the heat first before the hx at the furance?  If there is air in the lines what can be done?
Logged

ITO

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 254
  • OWF Brand: HS1
  • OWF Model: 555
    • View Profile
Re: Major temp loss with new install
« Reply #8 on: March 09, 2014, 07:13:52 PM »

Interesting, how is the DHW run before your HX? Do you have a sidearm or a tank or? Sometimes opening and closing a valve in the supply line slowly and repeatedly will move air out of a line.
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Major temp loss with new install
« Reply #9 on: March 09, 2014, 07:17:28 PM »

sidearm or plate type for DHW? It would take a huge DHW draw with a pretty big plate type exchanger to eat up 40 degrees.

I'm betting on a airlock. I have a auto vent installed at the highest point in the basement, also have another installed at the highest point of my sidearm.

http://www.pexsupply.com/Watts-0590716-1-4-FV-4M1-Auto-Air-Vent?gclid=CObUsdHjhr0CFbQWMgoddUEAjg

Can you crack a fitting in the basement somewhere? Is the pump at the stove or in the basement?
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

Wi woodburner

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 16
  • OWF Brand: Woodmaster
  • OWF Model: 5500
    • View Profile
Re: Major temp loss with new install
« Reply #10 on: March 09, 2014, 07:27:32 PM »

 It is a gea plate heat exchanger.  I have an inline valve that I can use to fill up the stove from this location.  This is right at the hot water heater. The pump is at the owb.  With no need. For heat, I feel the temp difference is around 20 degrees.  I am send a pic of the setup if that would help.
Logged

yoderheating

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 833
    • View Profile
Re: Major temp loss with new install
« Reply #11 on: March 09, 2014, 07:46:50 PM »

 If you have the ranco probe taped to pex pipe you are going to be off as much as 20 degrees. If that is the way its installed retape it to the copper inlet of the coil and then insulate it well. It still will not be accurate but should get within 10 degrees of actual temps.
 If you are checking the supply pipe by hand always check before the dhw. If the outdoor furnace is showing 170 you shouldn't be able to hold the supply line where it comes into the house. Compare temps where it comes out of the back of the furnace and where it comes into the house.
 An 011 with one inch pipe should be sufficient. When you filled the furnace did you work all the air out of the system by closing the return valve at the furnace and then reversing and closing the supply valve? This is very important, all air must be out of the system.
 If the supply line in the home is showing 150 with the ranco probe taped to the outside i=of the pipe you should be getting hot heat out of the vents with a 18x20 coil. Any chance air can flow around the coil?
Logged
Southwest Virginia
WF4000 Heat Master

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: Major temp loss with new install
« Reply #12 on: March 09, 2014, 10:01:38 PM »

Not sure what's going on for sure but all yoder said was spot on, test methods of temps on here are wrong 90% of the time

But don't worry about going to plate exchanger first,  I do all of mine that way, never a problem
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Major temp loss with new install
« Reply #13 on: March 09, 2014, 11:00:51 PM »

From your name I am guessing you are from Wisconsin. If you are in the southern part of the state I may be able to take a look at your system if you are interested.
Logged

hondaracer2oo4

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1471
  • OWF Brand: Heatmaster. Past Hardy
  • OWF Model: G200. Past H4
    • View Profile
Re: Major temp loss with new install
« Reply #14 on: March 10, 2014, 07:06:06 AM »

My mistake I guess not thinking that a bad pump could move water so slowly that you could possibly lose 40 degrees from the stove to the house on a 75 foot run. I can't imagine how slow the water would actually have to move to lose that much?
Logged