I used a second heat only thermostat wired to the fan only side of your existing thermostat.
You have a lot of options here, depending on what you want to spend. A second thermostat wired direct to the blower fan or jumped to the original Thermostat is one option. If the AC unit fires when the fan runs, you can either throw the breaker off on the AC unit during the winter heating season, or you can use a fan relay. Another option would be to purchase a multi-stage thermostat and run all 3 systems through it. This works the best but costs a few bucks more.
If you just want the LP burner disabled completely just take the wire off the W terminal on thermostat and move the wire that is on the G over to the W.If you want to add a second thermostat and keep the LP furnace operational just run a jumper wire from the RH in the original thermostat to the RH in the new thermostat and remove the wire from the G terminal and run it to the W on the new thermostat. (do not leave on the G in the original tstat or the AC may run) If the new thermostat doesn't use batteries you will need to run a jumper between the C terminals too.Another option is a strap on aquastat on the line from the OWB. If can be wired to switch the existing thermostat from LP gas to fan only when the pipe is hot. To wire it you would connect the RH wire going to the furnace to the NC connection, the G to the furnace to the NO connection and the RH to the thermostat to the common connection.