Author Topic: Generator interlock  (Read 5141 times)

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Generator interlock
« on: December 21, 2017, 06:53:58 AM »

Just wanted to let everyone know there is a simple and safe way to run your home with a generator and not be too expensive to hookup. I mounted a inlet box outside on brick wall and run #10 /3 wire to my panel boxes inside. I have 2 side by side. I installed a blank double pole single lever breaker in the top right hand slot and run my 10-3 wire to these two breakers. Both have an interlock mounted on face of panel that prevent both the main breaker and the 30 amp breakers from being on at same time. I know this has been talked about but just wanted to let you know this is the way to go for safety if you don't want to go the transfer switch route. This year I will be more ready for outage if it comes.
So in summary when power goes out:
1. Turn both main breakers off.
2. Hook your generator cord to the inlet box.
3. Start your generator and let warm up.
4. While waiting on generator to heat up turn all breakers off.
5. Flip the 30 amp breakers on at top you installed for generator wire.(if your interlock won't let you turn it on, that means you don't have the main broker off)
6. Go out to generator and flip its breaker on. The one that's is factory installed on generator.
7. Go back to panel and start flipping breakers on that you need.
8. I have red dots beside everything I'm gonna run in each box.
Power comes back on do all this in reverse.
Very safe
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Generator interlock
« Reply #1 on: December 21, 2017, 08:57:35 AM »

Siemens has something very similar, I’m still waiting to hear form an electrician friend if I have the proper one to do an interlock main on or not. A lot cheaper than a dedicated transfer switch.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

NaturallyAspirated

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 443
  • OWF Brand: Central Boiler
  • OWF Model: M250
  • Golfing, snowmobiling fool!
    • View Profile
    • http://www.nealmastel.com
Re: Generator interlock
« Reply #2 on: December 21, 2017, 04:31:01 PM »

Interlocks? Pshh!  I just have mine backfeed through a 30A 240V breaker from my feed on the corner of the deck...

I guess I did buy the female connector to act as a cap so that if someone turns the breaker on it won't zap ya!   :bag:


Used it once so far, 12-26-16:
Logged
Miss Farad was pretty and sensual, and charged to a reckless potential; but a rascal named Ohm conducted her home - Her decline was, alas, exponential
Send me your bitcoins!  1GEsGKzP5xK9e45YDjmRzGYpnhwT3oNbvj

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Generator interlock
« Reply #3 on: December 21, 2017, 04:32:40 PM »

What about putting a sub panel in for everything that you want the generator to run and then just put an outlet that it plugs into. Then put another outlet next to it from the generator.
Then all you have to do is move the plug. There is zero chance of backfeeding that way and when the power comes back on you will know because the rest of the power won't be off.
Logged

NaturallyAspirated

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 443
  • OWF Brand: Central Boiler
  • OWF Model: M250
  • Golfing, snowmobiling fool!
    • View Profile
    • http://www.nealmastel.com
Re: Generator interlock
« Reply #4 on: December 21, 2017, 04:37:40 PM »

Would feeding a sub panel with a receptacle be up on code?
Logged
Miss Farad was pretty and sensual, and charged to a reckless potential; but a rascal named Ohm conducted her home - Her decline was, alas, exponential
Send me your bitcoins!  1GEsGKzP5xK9e45YDjmRzGYpnhwT3oNbvj

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Generator interlock
« Reply #5 on: December 21, 2017, 07:20:22 PM »

If some line technician died from back feed, I not only would not want it on my conscious but I wouldn't wanna spend 10-20 years in prison for man slaughter. And yes it has and can happen. With either transfer switch or interlock you'll not have either to worry about. It's like insurance I hope I never have to use mine but I'm ready if I do.
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

RSI

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3100
  • OWF Brand: HeatMaster
  • OWF Model: G200 and B250
    • View Profile
    • RSI
Re: Generator interlock
« Reply #6 on: December 21, 2017, 09:17:51 PM »

Would feeding a sub panel with a receptacle be up on code?

I have no idea.
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Generator interlock
« Reply #7 on: December 21, 2017, 10:02:37 PM »

Would feeding a sub panel with a receptacle be up on code?

I have no idea.

I kinda doubt it. The whole ideal of an interlock is so its impossible to back feed the line with a generator.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

BoilerHouse

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 368
  • OWF Brand: Home Built
  • OWF Model: Fire Tube/Water Tube
    • View Profile
Re: Generator interlock
« Reply #8 on: December 22, 2017, 09:48:05 AM »

Would feeding a sub panel with a receptacle be up on code?

I have no idea.

I kinda doubt it. The whole ideal of an interlock is so its impossible to back feed the line with a generator.

With this set up it is impossible to back feed. From that regard it is safe.   I believe the issue is running a permanent install (sub panel) from a non permanent wire (heavy extension and plug/receptacle).  The codes in some jurisdictions may frown on it. 
Logged
Muskoka, Ont

NaturallyAspirated

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 443
  • OWF Brand: Central Boiler
  • OWF Model: M250
  • Golfing, snowmobiling fool!
    • View Profile
    • http://www.nealmastel.com
Re: Generator interlock
« Reply #9 on: December 22, 2017, 03:01:41 PM »

Would feeding a sub panel with a receptacle be up on code?

I have no idea.

I kinda doubt it. The whole ideal of an interlock is so its impossible to back feed the line with a generator.

With this set up it is impossible to back feed. From that regard it is safe.   I believe the issue is running a permanent install (sub panel) from a non permanent wire (heavy extension and plug/receptacle).  The codes in some jurisdictions may frown on it.
I agree.  And I understand how my setup is not as safe as it should be. 
Logged
Miss Farad was pretty and sensual, and charged to a reckless potential; but a rascal named Ohm conducted her home - Her decline was, alas, exponential
Send me your bitcoins!  1GEsGKzP5xK9e45YDjmRzGYpnhwT3oNbvj

WoodMOJoe

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 312
  • OWF Brand: Homemade Tank-in-Tank Furnace
  • OWF Model: Ol' Fireball #0002
    • View Profile
Re: Generator interlock
« Reply #10 on: December 23, 2017, 06:46:57 AM »

I feed my main panel through a 220V breaker.

Turn my main breaker off and also throw the main breaker on my meter loop.

Have a pole light on the coop side of the meter loop so I can tell when the power comes back at night, neighbor calls if it comes back in the daytime.

Got by in this fashion for 13 days in 2007, quite the ice storm then.
Logged
Southwest Missouri Ozarks...USA

Bluegrass Wood Burner

  • Full Member
  • ***
  • Offline Offline
  • Posts: 218
  • OWF Brand: Ozzark Biomass
  • OWF Model: Gasconade 500 gallon
    • View Profile
Re: Generator interlock
« Reply #11 on: December 23, 2017, 07:39:47 AM »

These interlocks are very simple little devices. I made the one on the left in my shop. 3 screws on each one and your done.
Logged
South central Kentucky
Ford F-150
16 ft tandem trailer
3000# winch
Husqvarna 142
Husqvarna 460 rancher
6ft spud bar
Poulan 3314
22 ton lowes splitter
Timberline sharpener
"Worn out body"

Rockarosa

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 72
  • OWF Brand: Pro-Fab
  • OWF Model: Cozyburn MS 250
    • View Profile
Re: Generator interlock
« Reply #12 on: December 23, 2017, 08:47:59 AM »

Why not just wire in a transfer switch? I wired one in several years ago and it so simple and safe my wife can start up the electric start generator and plug it in. Go down in the basement and switch the transfer panel to generator.
Logged
New Holland T C 30

E Yoder

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1296
  • OWF Brand: HeatMaster
  • OWF Model: GS 100
    • View Profile
    • www.heatmasterfurnace.com
Re: Generator interlock
« Reply #13 on: December 23, 2017, 01:04:16 PM »

I feed my main panel through a 220V breaker.

Turn my main breaker off and also throw the main breaker on my meter loop.

Have a pole light on the coop side of the meter loop so I can tell when the power comes back at night, neighbor calls if it comes back in the daytime.

Got by in this fashion for 13 days in 2007, quite the ice storm then.

Love those ice storm pics. I live right on the edge of the mountain where the warm air from the east hits the cold air from the north. Nothing like laying in bed when the trees are popping and cracking. ...
I backfeed through a homemade plug on my heat pump outside unit, not code at all..  :)
Logged
HeatMaster dealer serving southwest VA.
www.heatmasterfurnace.com

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Generator interlock
« Reply #14 on: December 23, 2017, 07:59:31 PM »

I need to run the entire farm off my hookup though, well not the entire farm but the electric fences need to be on and in the winter so do the heaters in the waterers need to be on.

One of these days is gonna do it right and have a 200 amp generator wired in. Can’t decide whether to go with nat gas or diesel though. Already have nat gas at the house, and with a diesel cold stacking is always a concern. However I have enough pessimist in me to realize if things ever got bad enough, you may not always have nat gas and you can make your own diesel if we burn thru a thousand gallons or so we always have in storage on the farm.
Logged