Author Topic: The water hammer, maybe  (Read 3029 times)

ST98

  • Full Member
  • ***
  • Offline Offline
  • Posts: 115
    • View Profile
The water hammer, maybe
« on: February 16, 2015, 04:00:21 PM »

This is the second year with the OWB.  Couldn't be happier. I noticed about a month ago what seems to be a water hammer when one of the zone valve closes.  I don't remember it happening any other time.

Here is the lowdown.  The oil burner has one pump and two zone valves. I have a second pump on my furnace that runs 24/7 from my water to water heat exchanger.

When one zone calls for heat the furnace pump comes on and off with no incident. When two zones are open with pump running and one zone valve closes while the other is still open I get the bang.  I've got two air eliminators on the pressurized side.  I don't really have any thoughts on why because it just started doing it or I just don't have any thought.

Thanks
Logged

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: The water hammer, maybe
« Reply #1 on: February 17, 2015, 06:31:20 AM »

You are not pump against one of the zone valves are you??  Forcing it shut or creating a vaccuum, causing it to close loudly
Logged

ST98

  • Full Member
  • ***
  • Offline Offline
  • Posts: 115
    • View Profile
Re: The water hammer, maybe
« Reply #2 on: February 17, 2015, 02:25:58 PM »

I'm not sure what that means?  Nothing has changed since they put the oil boiler in 19 years ago, other than adding the OWF.  I just never heard the problem before. I did secure one pipe better and it has seemed to be less of a bang but still there.
Logged

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: The water hammer, maybe
« Reply #3 on: March 04, 2015, 06:26:47 AM »

...do you have an expansion tank in the system, on the pressurized side, as it may have gone out and that is causing your noise.
Logged

ST98

  • Full Member
  • ***
  • Offline Offline
  • Posts: 115
    • View Profile
Re: The water hammer, maybe
« Reply #4 on: April 08, 2015, 06:38:58 PM »

I do have an expansion tank on it. Is there away to check it? 

Thanks
Logged

fireman69lfd

  • Training Wheels
  • *
  • Offline Offline
  • Posts: 30
  • OWF Brand: Portage and Main
  • OWF Model: Optimizer 250
    • View Profile
Re: The water hammer, maybe
« Reply #5 on: April 08, 2015, 07:48:36 PM »

If your owb is plumbed straight into your oil boiler without a heat exchanger, that is your problem. Zone valves can only stand so much slam from the volume and pressure from the owb. I had the same thing happen to me after 2 years from the dealer installed startup. Dealer said I would not need an expencive heat exchanger for my install to work with a 2 story. He was right, it worked great for a couple of years then I ended up replacing 5 zone valves and adding  a plate exchanger. Hope this helps.
Just another point, I had a 007 on my oil boiler and an 0011 on my owb
Logged
Russ
Near Okemo Mtn. Ski area Vermont

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: The water hammer, maybe
« Reply #6 on: April 08, 2015, 09:55:31 PM »

FPHE's are not that expensive compared to not doing it right the first time.
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: The water hammer, maybe
« Reply #7 on: April 09, 2015, 03:12:49 AM »

 :post:Exactly Marty!
Logged
Wood boiler sales, service and installation for the Northeastern USA.

ST98

  • Full Member
  • ***
  • Offline Offline
  • Posts: 115
    • View Profile
Re: The water hammer, maybe
« Reply #8 on: April 09, 2015, 02:50:31 PM »

The knowledgable people on this site steered me to the correct install so I have an exchanger.

I have oo7 on the oil furnace and then a grundfos circulator pumping water through the oil furnace 24/7 back to the heat exchanger.  Oil burner circ only comes on when there is a call for heat.  If only one zone is open with oil burner circ running it doesn't do it. It only happens when both zones are open and one closes,  then bang.
Logged