Central Boiler / Central Boiler E Classic 1450 will not start
« on: October 21, 2015, 03:55:29 PM »
When I powered my CB EC 1450 for the season two weeks ago the Firestar II booted normally but displayed the following:
HI then 1.43 ( this continues to repeat ) All three stage led were alternately flashing on and off

The fan will not start, however, when I put the Firestar into the diagnostic mode (menu item #7) the fan started and ran as well as each solenoid energized and the diagnostic completed.

I thought it may have been one of the two hi temp alarms and replaced the water sensor first, then the reaction chamber temp sensor but still have the same issue. I've contacted my dealer and CB Both were helpful but neither were technical enough to help.

Has anyone seen this issue and if so what is the resolution?

Any idea's would be much appreciated..