Re: Radiant walls
« Reply #30 on: September 30, 2018, 08:08:06 AM »

175? Small. That size space with average insulation in my neck of the woods would only take about 2000 BTU, so a 6 foot section of 3/4" with 180 degree water would be plenty
Logged

sceptre74

  • Full Member
  • ***
  • Offline Offline
  • Posts: 192
  • OWF Brand: Portage and Main
  • OWF Model: BL 28-40
    • View Profile
Re: Radiant walls
« Reply #31 on: September 30, 2018, 12:45:03 PM »

Good. Thanks for the help.
Logged

mlappin

  • Fabricator Extraordinaire
  • Global Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4140
  • OWF Brand: homebuilt, now HeatmasterSS
  • OWF Model: Martin Steel Works Gen 1 then, now a G200.
  • North Liberty, Indiana
    • View Profile
    • Altheatsolutions
Re: Radiant walls
« Reply #32 on: July 16, 2019, 11:22:45 AM »

Gotcha! I really don't think you would like running 180 through there. The linear expansion and noise is enough to drive a guy batty. Pex-Al-Pex will help considerably with that, but it'll still be noticeable if you're trying to keep them straight and/or sandwiched. How long are these walls? The BTU output is pretty minimal and takes a whole lot of tubing. I took a course with Uponor this summer and was trained in their Quik-Trak system, and must say I was very surprised with how little the output really is. And sheetrock cannot withstand anything over 130* water without warping and cracking, so that limits a lot of output also. As for knocking your temp down, if you'd be adding a pump for this loop anyway, why not just pipe a mixing valve in between the primary and circulator? Then you have whatever temp water you need

So if I read this correctly, even using the quik-trak on a wall the temp will need to be mixed down to 130 or less?
Logged
Stihl 023
Stihl 362
Stihl 460
Sachs Dolmar 112 and 120
Homemade skid steer mounted splitter, 30" throat, 5" cylinder
Wood-Eze model 8100 firewood processor

HeatmasterSS dealer for Northern Indiana

wreckit87

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 659
  • OWF Brand: Heatmaster
  • OWF Model: C375
    • View Profile
Re: Radiant walls
« Reply #33 on: July 16, 2019, 03:19:48 PM »

Depending on finish, maybe. I'd have to look in the paperwork but I want to say the max temp for Quik-Trak was 140
Logged