Clueless, I hope you are getting some heat out of your slab by now. I was thinking you have additional radiant heat capabilities in your house but are just concentrating on the basement first? You have an 007 for your basement slab, a ?? at your boiler? and what other pumps if any and what size? Is there insulation under your floor slab, or basement walls? Also, can the installer you mentioned tell you anything more about your installation? This information can help the pro's advise you, I'm no pro, just trying to learn here.
Willie, I'm math challenged so having been forcing myself to figure some of this stuff out.
The only clues from Clueless were 5 loops at .25 gpm, a supply temp of 110, return temp 60. Thats a Dt of 60. So 1.25 gpm x 500 x 60Dt= 31,250 btu/hr. (assuming 5 loops at 1/4 gpm) You said output would not be 10,000btu because water was not 180. Nobody would send 180 into a slab, but if so, btu output would still be gpm x 500 x Dt=btu/hr. As the slab temp. approaches the air temp, the Dt would narrow, then at some point, you would only need to supply enough btu to cover the heat loss and maintain the desired room temperature.
Also,I still don't understand the statement "a .1 gpm increase=5 btu per sq. ft." Is that some sort of rule of thumb? To me it seems like something that could occur but other factors like how many square feet, spacing of pex in slab, slab insulation, would all influence btu/sq ft. In your own basement, (2 gpm, Dt 10 deg) you would be supplying btu's at the rate of 10,000 btu/hr. If you increased you gpm to 2.1( and your Dt remained the same) your out put went up to 10,500. If there was a 5 btu/sq.ft increase, your basement is 100 sq.ft.Any thoughts? I know I'm missing something here. Please help, my wife just gives me a blank stare when I bounce this stuff off her.