OK Larry, I was actually waiting for other ideas but here goes. outside wood boiler circ and inside primary circ both get wired to seperate toggle/light swithces, inside oil/gas boiler circ gets wired to the C-1 terminal on your boiler aqua-stat ( this circ only operates when your oil/gas boiler is up to temperture and there is a call for heat) and is not used when heating with wood. The remaining 7 loop circs would be wired through the circulator relays to control the zones, my choice for relays would be 2 Taco SR 504 EXP circulator switching relays with the capability to expand for future use, I would use 2- 4 zone instead of a 6 and 2 as they will look better and I'm not sure if they make an 8 zone.