fitting leaking lok at this
« on: November 28, 2013, 05:02:38 PM »

Inside of the one end is all pitted and the other end looks fine. This is only two years old going on third season. Bad fitting otr something else causing this?
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: fitting leaking lok at this
« Reply #1 on: November 29, 2013, 05:00:28 AM »

I'm going to bet there was a pocket of air at that fitting that never got removed.
Logged
Wood boiler sales, service and installation for the Northeastern USA.

Scott7m

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3740
  • OWF Brand: Heatmaster
  • OWF Model: E Series
    • View Profile
Re: fitting leaking lok at this
« Reply #2 on: November 29, 2013, 08:28:52 AM »

Are you using a broeder 3 speed?  What is length of run

Ive heard to much flow can pit and wear fittings but never seen it first hand
Logged
Dealer for:  Heatmaster, Empyre, Earth, Ridgewood, and Woodmaster outdoor furnaces
Furnace Parts Dealer
Pelican water treatment systems
606-316-9697

allis48

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 87
  • OWF Brand: natures comfort
  • OWF Model: ncb250
    • View Profile
Re: fitting leaking lok at this
« Reply #3 on: November 29, 2013, 02:38:07 PM »

I was running the broeder 3 speed for the first two pumps i was running them on middle speed but now it has a  bell and gossett pl36. Its is a 30 foot run but its about 10 feet above ground cause it a hanging wall heater.
Logged

allis48

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 87
  • OWF Brand: natures comfort
  • OWF Model: ncb250
    • View Profile
Re: fitting leaking lok at this
« Reply #4 on: March 02, 2014, 05:55:58 AM »

Hey Guys I still need help here with these fittings. I had to change 3 of them this season and this one was already changed around thanksgiving. What is the problem/s? Is there anyother fitting that I can use that will hold up better?
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: fitting leaking lok at this
« Reply #5 on: March 02, 2014, 06:04:37 AM »

I think you will find that air elimination is going to be the key, I would bet the deteriorated portion of the fitting is on the outbound side am I right?
Logged
Wood boiler sales, service and installation for the Northeastern USA.

allis48

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 87
  • OWF Brand: natures comfort
  • OWF Model: ncb250
    • View Profile
Re: fitting leaking lok at this
« Reply #6 on: March 02, 2014, 06:24:52 AM »

I can't remember which way it was this is the other end of same fitting not as bad but still started. This one (changed twice this season) is on inlet side of heat exchanger the other one I chnged this year was on outlet side of same exchanger.Do you think I should replace it with a tee ans short peice of pex and ball valve to bleed off air?
Logged

slimjim

  • Full Member
  • ***
  • Offline Offline
  • Posts: 158
  • OWF Brand: Wood Doctor / HeatMaster
  • OWF Model: 14,000. / G 200 and G 400
  • Southern Maine
    • View Profile
    • www.mainlycustom.com
Re: fitting leaking lok at this
« Reply #7 on: March 02, 2014, 06:56:54 AM »

When you say heat exchanger, water to water or water to air? what I'm looking for,  is that fitting in the pressurized or non pressurized side of the system, it will be impossible to eliminate air in the non pressurized side but air elimination on the pressurized side is easy, resistance in those 90's are way up there can you eliminate some of them or use long radius 90's
Logged
Wood boiler sales, service and installation for the Northeastern USA.

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: fitting leaking lok at this
« Reply #8 on: March 02, 2014, 08:47:15 AM »

How does air erode brass?  There is a known problem called zinc depletion from chloride levels in some brass pex fittings, but I don't think this is the case in a boiler.  The zinc problem usually has lots of crusty build up that's blue ish white. That brass surface looks like erosion? Any  copper in the system other than Air handler.
Logged
Michigan Thumber

allis48

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 87
  • OWF Brand: natures comfort
  • OWF Model: ncb250
    • View Profile
Re: fitting leaking lok at this
« Reply #9 on: March 02, 2014, 09:54:19 AM »

This is what I m working on the red line I changed twice this season the blue once. It is none pressurized. I have a total of two elbows on this loop both in this picture. I have a total of 6 on house loop haven't changed any of them yet.
Logged

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: fitting leaking lok at this
« Reply #10 on: March 03, 2014, 08:28:53 AM »

So you've gone thru 2 pumps and on a third?  Does the pl36 only serve the 30' pex and air handler? If that's all it is in the loop, there's probably no temp diff in S&R lines with water flowing 50mph.
Can you hear the water flowing in the pipe
Logged
Michigan Thumber

LittleJohn

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 494
  • OWF Brand: Central Boiler
  • OWF Model: E-Classic 2400
  • Lonsdale, MN
    • View Profile
Re: fitting leaking lok at this
« Reply #11 on: March 03, 2014, 10:38:46 AM »

What kind of GPM you running thru the fittings, cause you should try and keep water velocities below 8ft/s ( or you get this little thing called erosion)  :o which maybe what you are seeing.  It woudl be very interesting if you also knew which way the water was flowing thru the fitting might lead you down the path to an answer.
Logged

allis48

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 87
  • OWF Brand: natures comfort
  • OWF Model: ncb250
    • View Profile
Re: fitting leaking lok at this
« Reply #12 on: March 03, 2014, 04:57:30 PM »

By looking back out some of my other pics from before it it the outlet side of the fittings that is the worse. I have about 15 degree drop from one side to the other
Logged

CRJR

  • Full Member
  • ***
  • Offline Offline
  • Posts: 105
    • View Profile
Re: fitting leaking lok at this
« Reply #13 on: May 13, 2014, 11:23:46 AM »

Do a Google search for "dezincification"
Logged

Sprinter

  • Do it right the first time, its cheaper In the long run
  • Global Moderator
  • Sr. Member
  • *****
  • Offline Offline
  • Posts: 474
  • OWF Brand: Indoor Boiler
  • OWF Model: Menominee
  • In the long run
    • View Profile
Re: fitting leaking lok at this
« Reply #14 on: May 13, 2014, 02:50:18 PM »

I think that was an older problem, even the lawsuits are over. But its possible he has some very old stock. The zinc problem was more of a pitting and lots of whitish blueish calcium looking buildup. You'd find it mostly on the ribs where the crimp seals. You would have a nice size pin hole in the elbow or leaks at the ribs.
Logged