I see that Marty was able to post a picture this morning so I'm going to try and post the diagram this morning for those of you who are interested, Darn it won't go, I have had several requests for it so I'll try to get Marty to post it on this thread, Guys if you want it Please send me an E-Mail request and I'll send it right back, my E-Mail is mainlycustomsawing@yahoo.com
The whole Idea is to interrupt the power wire to the blower/actuator and pass it through a Strap on Aqua Stat( I use a honeywell 6006C 1018 ) this gets placed on the supply line off the back of the boiler, use the R+W terminals (they make connection on temp rise) set the Aqua Stat at 160 degrees, this kills the blower below set point, now where you interrupted the power wire, attach 2 more wires to run over to a 60 minute timer ( I use the TORK A560MW ) this allows you to bypass the Aqua-Stat for 60 minutes while the fire is rekindling itself