Outdoor Furnaces - Manufacturers WITH EPA-Certified Models => Central Boiler => Topic started by: sumptersmoker on October 15, 2012, 07:04:34 AM
-
I just fired up the stove for the first time :thumbup: I have yet to add another thermostat to control the fan (using the orginal for now) I have a quick question to ask.
I dont have a manual for my stove, I've ordered one but waiting. How do you chenge the settings on the stove ? I pressed the set button on the display and pu came up I changed the temp to 180 deg then pressed st again. does this mean the damper will close when the water gets to that temp ? if so at what point does the damper open once the temp starts to fall off. and how is this set ?
Sumptersmoker
-
My 5036 came from the factory set to a ten degree swing. If I am set at 170 it will open at 160 and off at 170.
-
I called CB, the setting on the inside of the pump panel is a max only setting. the defult is 10 degrees lower from that setting... for the air dampner to open and close.. I thought you had to program the low setting as well.
Now I know...