All-Purpose OWF Discussions => General Outdoor Furnace Discussion => Topic started by: mwoos on January 05, 2014, 09:48:26 PM

Title: Water pushing pass my circulator pump
Post by: mwoos on January 05, 2014, 09:48:26 PM
I have a mahoning 300 running two zones and domestic hot water my problem is when my zone for upstairs is not calling for heat the pump from the OWB had enough force to push water pass my pump and flow check valve any help would be great.
Title: Re: Water pushing pass my circulator pump
Post by: Sprinter on January 06, 2014, 09:01:52 AM
 Then the primary pump is too big or their is a problem in the piping layout. Since both pumps can see each other, you must have it pipe primary /secondary.  What is your flow rate? And circ models? Post a few pics, will help much easier