I installed a unit heater in my garage. My house has three zones of hot water heat. I was not using my basement zone. So I hook into that zone for the unit heater in my garage.
My problem is that the T stat in the garage tells the pump to circulate and to open the zone. So that leaves the motor on the unit heater. I bought a snap disc, thinking that would do the trick strap to the cooper line. It will not close it unless I take a torch to the snap disc.
Is there any simple relays I can use to operator the fan?
-
A Honeywell strap on Aqua Stat is the simplest way I know of to control the fan motor!
-
So when the copper line heats ups, it will tell the fan to run.
That would work, just looking for something cheaper.
-
The ones I use are just over $100
-
How about this: Grundfos 595656 1/2-Inch Clip-On Aquastat Control. Just found it on amazon.
-
Never mine that is backwards from what i need
-
Just run the power to the unit heater off the same source as the pump. Then they will come on together.
-
I can not do that, because when a different zone would energize the fan would run.
-
my snap dick work the same ...they want 100% contact ...I just got one with a "lower come on temp"...i'll see this weekend.
-
The lowest I could find was 110 turn on temp. Where did you mount yours?
-
Never got to it yet :(
-
I talk to a hvac person and they said to use a 24 volt relay off the thermostat.
-
Well slim, I ended up putting a aquastat on the unit heater. Set it @ 120. Working good. Thanks
-
Awesome, glad I could help!