I have an e 1450 running thru 140' of thermopex one way to an oil fired boiler core and back. There are 2 1" copper 90s and 2 3/4 blackiron 90s also 4 ball valves 2 1" and 2 3/4" full port. Also have the CB thermostatic valve piped in. My taco 009 is on the WB and I wood like to get a better pump with more flow.
Does any one have some suggestions or would another circ in series work also. I have a spare up 15 42
Thanks
Jon
-
It looks like the 0011 would be more in line with your target flow rate and head loss.
-
I would go with a Grundfos UPS26-99
-
Is the grundfos a variable speed? It would be nice to dial the flow to weather requirements. Also where would you mount indoors in basement or on the stove where it is now.
-
It is 3 speed. At the stove is better.
-
Take a look at taco 2400 - 20 wb made for outside wood boilers look it up on line
-
This thread got me thinking and gave me the kick in the butt I needed to do something I've been thinking about for a while. I've got about 100' of 1" pex between my owb and my hx with an Alpha 15-55 showing 6 gpm in high. I wanted to bump it up a bit so yesterday ordered another 15-55 and just installed it in series with the existing, one on either side of the hx. The first pump is showing 11 gpm now and new one is at 8 gpm and both are at 43 watt. I don't know how these pumps calculate gpm, but they are both doing the same even though they read different.
Anyways, happy camper, I've got more flow and now have a backup already installed in case one fails. I will just run one on low speed during the summer to keep some circulation going. I'll also start playing with pump speeds to see what happens.
-
Update. Now both pumps are reading 9 gpm. Perfect.
-
It is 3 speed. At the stove is better.
RSI, why does the fact that the pump is a 3 speed affect why it should be at the burner or not?
Thanks!
Nick
-
Being 3 speed has nothing to do with being at the stove. I was answering 2 separate questions.
-
Generally a lot easier to get the air out of your system if the pump is at the boiler, less chances of it air locking.